Log on to rate and give feedback    1 2 3 4 5 Log on to rate
0
Specifications Specifications 7/5/2022
Products: Wireless Adapter - Advanced
Functionalities: Hardware
Product version: 2022

Wireless Adapter - Advanced

Wireless Adapter - Advanced

Wireless Adapter - Advanced

Introduction

SpaceLogic* Wireless Adapter - Advanced is a USB-based wireless adapter that enables Zigbee TM wireless connectivity for your SpaceLogic BACnet/IP controller or automation server, extending its point count and bringing flexibility in your retrofit applications. The adapter can be used with BACnet/IP controllers such as the RP controllers as well as automation servers such as the AS-P and AS-B servers.

An automation server equipped with the adapter can communicate over the Zigbee wireless protocol with up to 164 wireless devices, depending on the type of Zigbee device and the radio bandwidth usage of the device. An RP controller equipped with the adapter can communicate with up to 30 wireless devices.

For information on the supported wireless devices, see section “Supported Wireless Devices”.

The adapter works seamlessly within EcoStruxure Building Management systems so that Zigbee objects become easily available to the user.

The adapter’s compact design allows it to plug in to RP controllers or automation servers in tight spaces and the optional mounting cradle, wall plate, and USB cable extension allow for the choice of a wall, ceiling, or exterior of the enclosure mount to maximize the transmission and reception of signals from distributed Zigbee devices.

In WorkStation, the firmware of the adapter will be automatically updated when you update the RP controller or automation server to which it is connected.

* Formerly known as SmartX.

Features

The adapter has the following features:

  • Zigbee Certified Product (with RP controllers, AS-P and AS-B servers)

  • Zigbee 3.0

  • Compact design and easy to install

  • Multiple mounting options

  • Integrated 2.4 GHz antenna

  • Wireless communication distance:

    • Line-of-sight range: Up to 50 m (164 ft)

  • Configuration and firmware update through EcoStruxure Building Operation software

Part Numbers

Product

Part number

SpaceLogic Wireless Adapter - Advanced
SXWZBAUSB10001

USB Adapter Cradle Kit

Includes plastic mounting cradle and wall plate

SXWUSBCRA10001

USB Extension Cable 1 m (3 ft)

Includes USB extension cable of length 1 m (3 ft)

SXWUSBCBL10001

Plenum Rated USB Extension Cable 3 m (10 ft)

Includes plenum rated USB extension cable of length 3 m (10 ft)

SXWUSBCBL10002
Specifications
Electrical
DC input supply voltage
5 VDC (USB) a
Maximum power consumption
0.3 W
Wireless connectivity
Communication protocol
Zigbee 3.0
Frequency band
2.4 GHz (ISM band), compliant with IEEE Standard 802.15.4
Maximum output power
+10 dBm
Maximum communication distance
Line-of-sight: 50 m (164 ft)
Antenna
Integrated antenna
Maximum total number of hops allowed in the wireless network
5
Wireless device limits for an RP controller
Maximum total number of wireless devices connected to the wireless network
Up to 30 a
Maximum total number of SE8000 and VT8000 room controllers
4
Maximum total number of Zigbee end devices paired with an RP controller
20
Maximum total number of ASSA ABLOY VingCard electronic locks
1
Wireless device limits for an automation server
Maximum total number of wireless devices connected to the wireless network
Up to 164 a
Maximum total number of Zigbee routers and Zigbee end devices
64
Maximum total number of Zigbee Green Power devices
100
Maximum total number of Zigbee end devices paired with an automation server
20
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-40 to +70 °C (-40 to +158 °F)
Humidity
Maximum 95 % RH non-condensing
Material
Plastic flame rating
UL94 HB
Plenum rating
UL 2043
Ingress protection rating
IP 20
Mechanical
Dimensions, adapter
See drawing below
Dimensions, mounting cradle and wall plate
See drawing below
Weight
Adapter: 7.57 g (0.267 oz)
  
Cradle and nut: 21.35 g (0.753 oz)
  
Cradle, nut, and wall plate: 33.40 g (1.178 oz)
Installation
Connection to USB host port on RP controller or automation server
  
Indoor use only
Installation options
Enclosure exterior
  
Drop ceiling with mounting cradle (optional)
  
Wall with wall plate (optional)
Maximum USB 2.0 cable length
3 m (10 ft)
Software requirements
EcoStruxure Building Operation software
version 3.2 and later
EcoStruxure Building Commission mobile application software 
version 4.0 and later
RP-C controller firmware
version 3.02.xx or higher
AS-P server firmware
EcoStruxure Building Operation software version 3.2 and later
AS-B server firmware
EcoStruxure Building Operation software version 3.3 and later
Agency compliances
EMC
EN 301 489-1 V2.2.3; EN 301 489-17 V3.2.2; BS/EN 55032:2015; BS/EN 55035:2017; FCC Part 15, Sub-part C, Class B; ICES-003, Class B
Radio
EN 300 328 V2.2.2
Safety standards
BS/EN 62368-1:2014; BS/EN 62311:2008; BS/EN 62479:2010
FCC ID
QOQ13
ISED certification number
IC: 5123A-13
Hardware
CPU type
ARM Cortex-M4 with Floating Point Unit (FPU)
Frequency
38.4 MHz
SRAM (embedded)
64 KB
Flash memory (embedded)
512 KB
Connectors
USB 2.0, type-A connector

Supported Wireless Devices

This section provides information on the wireless devices that are supported by the wireless network.

In EcoStruxure Building Operation software version 4.0 and later, additional Zigbee 3.0 wireless devices can be supported using the Zigbee Wireless Device Support Service. For information on how support for Zigbee 3.0 devices can be added in the EcoStruxure Building Operation software through this service, see PA-00842.

SpaceLogic SE8000 and VT8000 controllers

The SE8000 and VT8000 controllers can be used for fan coil, roof top unit, heat pump, indoor air quality, and VAV control applications.

The SE8000 and VT8000 controllers without built-in wireless networking capability require the VCM8000V5045P Zigbee extended profile wireless communication adapter to be installed to enable Zigbee wireless connectivity.

The following conditions apply to the support of SE8000 and VT8000 controllers under an automation server Zigbee wireless network:

  • In EcoStruxure Building Operation software version 3.3, when you connect an SE8000 or VT8000 controller via Zigbee wireless network to the automation server, you are not able to connect Zigbee devices to the SE8000 or VT8000 controller. If you already have Zigbee devices connected to the SE8000 or VT8000 controllers in the Zigbee network, you must either re-connect them to the automation server or upgrade to EcoStruxure Building Operation software version 4.0.

  • When you connect SE8000 and VT8000 controllers via Zigbee wireless network to the automation server, you are not able to use multiple SE8000 or VT8000 controllers as sensors to control a single setpoint in a single zone.

The following conditions apply to the support of SE8000 and VT8000 controllers under an RP controller Zigbee wireless network:

  • In EcoStruxure Building Operation software version 3.3 and version 4.0, when you connect an SE8000 or VT8000 controller via Zigbee wireless network to the RP controller, you are not able to connect Zigbee devices to the SE8000 or VT8000 controller. If you already have Zigbee devices connected to the SE8000 or VT8000 controllers in the Zigbee network, you must re-connect them to the RP controller.

  • Support for SE8000 and VT8000 controllers under the RP controller Zigbee wireless network is limited to display and sensor functionality. Under the RP controller Zigbee network, they are not supported as HVAC controllers.

  • When you connect SE8000 and VT8000 controllers via Zigbee wireless network to the RP controller, you are not able to use multiple SE8000 or VT8000 controllers as sensors to control a single setpoint in a single zone.

Product

Part number

Low-Voltage Fan Coil Room & Zone Controller, RH sensor & control

SE8350U0Bxx a

Low-Voltage Fan Coil Room & Zone Controller, RH sensor & control, PIR motion sensor

SE8350U5Bxx a

Low-Voltage Fan Coil Room & Zone Controller, ZigBee Embedded, RH sensor, PIR motion sensor

SE8350U5BxxP a

Roof Top Unit, Heat Pump & Indoor Air Quality Controller, RH sensor & control

SE8650U0Bxx a

Roof Top Unit, Heat Pump & Indoor Air Quality Controller, RH sensor & control, PIR motion sensor

SE8650U5Bxx a

Roof Top Unit, Heat Pump & Indoor Air Quality Controller, ZigBee Embedded, RH sensor & control, PIR motion sensor

SE8650U5BxxP a

Line-Voltage Fan Coil Room Controller, RH sensor & control

SER8350A0Bxx a

Line-Voltage Fan Coil Room Controller, RH sensor & control, PIR motion sensor

SER8350A5Bxx a

Line-Voltage Fan Coil Room Controller, ZigBee Embedded, RH sensor & control, PIR motion sensor

SER8350A5BxxP a

Variable Air Volume Controller, PD/PI, RH sensor & control

SEZ8250U0Bxx a

Variable Air Volume Controller, PD/PI, RH sensor & control, PIR motion sensor

SEZ8250U5Bxx a

Variable Air Volume Controller, PD/PI, Embedded ZigBee Pro, RH sensor & control, PIR motion sensor

SEZ8250U5BxxP a

Low-Voltage Fan Coil Room Controller, White Case, White Fascia

VT8350U5x00B b

Low-Voltage Fan Coil Room Controller, Embedded ZigBee Pro, RH sensor & control, PIR motion sensor, White Case, White Fascia

VT8350U5500BP

Roof Top Unit, Heat Pump & Indoor Air Quality Controller, White Case, White Fascia

VT8650U5x00B b

Roof Top Unit, Heat Pump & Indoor Air Quality Controller, Embedded ZigBee Pro, RH sensor & control, PIR Motion Sensor, White Case, White Fascia

VT8650U5500BP

Fan Coil Room Controller, White Case, White Fascia

VTR8350A5x00B b

Fan Coil Room Controller, Embedded ZigBee Pro, RH sensor & control, PIR Motion Sensor, White Case, White Fascia

VTR8350A5500BP

Variable Air Volume Controller, PD/PI, White Case, White Fascia

VZ8250U5x00B b

Variable Air Volume Controller, PD/PI, Embedded ZigBee Pro, RH sensor & control, PIR motion sensor, White Case, White Fascia

VZ8250U5500BP

  1. The two characters “xx” of the part number indicate the color of the case and fascia: 00 (Silver Case, Silver Fascia), 11 (White Case, White Fascia)
  2. The character “x” of the part number indicates the sensor type of the controller: 0 (RH sensor & control), 5 (RH sensor & control, PIR motion sensor)
Wireless sensors

The wireless sensors can be used for indoor air quality, motion and occupancy, window and door status, and water leakage monitoring.

Product

Part number

CO2 with Temperature and Humidity Sensor

SED-CO2-G-5045

Temperature and Humidity Sensor

SED-TRH-G-5045

Window/Door Contact Sensor

SED-WDC-G-5045

Motion with Temperature and Humidity Sensor

SED-MTH-G-5045

Water Leak Sensor

SED-WLS-G-5045

SpaceLogic RP controller expansion Zigbee modules

The RP controller expansion Zigbee modules can be used for lighting control applications.

Product

Part number

RP-C-EXT-ZB-0-10V, Zigbee 0-10V module (230 VAC)

SXWREZB010110001

RP-C-EXT-ZB-DALI, Zigbee DALI module (230 VAC)

SXWREZBDALI110001

SpaceLogic TH900 Series thermostats

The TH900 Series thermostats can be used for packaged terminal air conditioner (PTAC), fan coil, heat pump, and gas and oil furnace control applications. The TH900 Series thermostats are only supported for the automation servers.

Product

Part number

TH903 Thermostat, LCD/Buttons, Zigbee, Occupancy Sensor, Auxiliary Input, White

TH903-ZP-W

TH903 Thermostat, LCD/Buttons, Zigbee, Occupancy Sensor, Modbus, Auxiliary Input, White

TH903-ZPM-W

TH907 Thermostat, Touchscreen, Zigbee, Occupancy Sensor, Auxiliary Input, White

TH907-ZP-W

TH907 Thermostat, Touchscreen, Zigbee, Occupancy Sensor, Modbus, Auxiliary Input, White

TH907-ZPM-W

TH907 Thermostat, Touchscreen, Zigbee, Occupancy Sensor, Auxiliary Input, Black

TH907-ZP-B a

TH907 Thermostat, Touchscreen, Zigbee, Occupancy Sensor, Modbus, Auxiliary Input, Black

TH907-ZPM-B a

  1. This model is manufactured on a custom basis only.
PowerLogic™ PowerTag energy sensors

The PowerTag energy sensors can be used for energy metering and monitoring, load monitoring and power availability for products and installations rated up to 2000 A.

PowerTag firmware version 004.000.424 or later is required for support in the EcoStruxure Building Operation software.

Product

Part number

PowerTag Energy M63 1P+Wire

A9MEM1520

PowerTag Energy M63 1P+N TOP

A9MEM1521

PowerTag Energy M63 1P+N BOTTOM

A9MEM1522

PowerTag Energy M63 3P

A9MEM1540

PowerTag Energy M63 3P+N TOP

A9MEM1541

PowerTag Energy M63 3P+N BOTTOM

A9MEM1542

PowerTag Energy M63 3P 230V LL

A9MEM1543

PowerTag Energy P63 1P+N TOP

A9MEM1561

PowerTag Energy P63 1P+N BOTTOM

A9MEM1562

Powertag Energy P63 1P+N BOTTOM RCBO 18mm

A9MEM1563

PowerTag Energy P63 3P+N TOP

A9MEM1571

PowerTag Energy P63 3P+N BOTTOM

A9MEM1572

PowerTag Energy F63 1P+N

A9MEM1560

PowerTag Energy F63 1P+N 110V LL

A9MEM1564

PowerTag Energy F63 3P+N

A9MEM1570

PowerTag Energy F63 3P

A9MEM1573

Powertag Energy F63 3P+N 127V/220V

A9MEM1574

PowerTag Energy F160 3P/3P+N

A9MEM1580

PowerTag Energy M250 3P

LV434020

PowerTag Energy M250 3P+N

LV434021

PowerTag Energy M630 3P

LV434022

PowerTag Energy M630 3P+N

LV434023

PowerTag Energy R200 3P/3P+N

A9MEM1590

PowerTag Energy R600 3P/3P+N

A9MEM1591

PowerTag Energy R1000 3P/3P+N

A9MEM1592

PowerTag Energy R2000 3P/3P+N

A9MEM1593

Easergy wireless sensors

The Easergy wireless sensors can be used for environmental condition monitoring for enclosures and continuous thermal monitoring of critical power connections of indoor installations.

Product

Part number

Easergy CL110 Wireless Environmental Sensor

EMS59443 a

Easergy TH110 Wireless Thermal Sensor

EMS59440 b

  1. Set of two pieces.
  2. Set of three pieces.
Wiser micro module switches and dimmers

The Wiser micro module switches and dimmers can be used for lighting control applications.

Product

Part number

Wiser 1 Gang Micro Module Switch

CCT5011-0001_AS

Wiser Micro Module Light Switch

CCT5011-0002

Wiser 1 Gang Micro Module Dimmer

CCT5010-0001_AS

Wiser Micro Module Dimmer

CCT5010-0002

ASSA ABLOY electronic locks

The ASSA ABLOY electronic locks can be used for hotel applications with electronic door locks.

Product

Part number

Electronic Locks - VingCard Allure

See the ASSA ABLOY web site

Electronic Locks - VingCard Essence

See the ASSA ABLOY web site

Electronic Locks - VingCard Signature

See the ASSA ABLOY web site

Electronic Locks - VingCard Classic

See the ASSA ABLOY web site

Electronic Locks - VingCard Flex

See the ASSA ABLOY web site

Community Content

Product version

Language