When Modbus is configured on a BACnet/IP controller, you can view the communication status of Modbus devices in the Commission mobile application.
Modbus device status information is not available in the Commission mobile application unless you first configure the BACnet/IP controller to include Modbus. You can do so either directly from WorkStation or from an application image which has been downloaded to the controller.
In the Commission mobile application, connect to the BACnet/IP controller.
On the tab bar, click Commission .
Click I/O Checkout .
On the I/O Resources page the BACnet name of each network interface is listed.
Click Modbus .
On the Modbus page, click Properties.
Click the Back arrow.
Click Devices .
In the list of Modbus devices, check the status of the device:
Offline (red text): The device is not communicating with the BACnet/IP controller. Click on the Info icon for debug suggestions.
Online (gray text): The device is communicating with the BACnet/IP controller.
The Commission mobile application reports the communication status (online or offline) of Modbus devices. I/O Checkout of Modbus devices is limited to Plant Room Sensors.