Part numbers: SXWRPV4A10001 and SXWRPV5A10001
Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.
Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.
SpaceLogic and EasyLogic - Hardware Installation System Guide, 04-XX001-XX-en
The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet, ecoxpert.se.com. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.
Recommended screw tightening torque: 0.56 to 0.79 Nm (5 to 7 lbf.in)
For information on wiring, see the SpaceLogic and EasyLogic - Hardware Installation System Guide.
Product |
Part number |
RP-V-4A
|
SXWRPV4A10001
|
RP-V-5A
|
SXWRPV5A10001
|
Adapter for damper shaft diameter 9.5 mm (3/8 inch) |
AM-135 |
Isolated RS-485 adapter (cable not included)
|
SXWISORS48510001
|
Non-isolated RS-485 adapter (cable not included)
|
SXWNISORS48510001
|
RS-485 power adapter (cable not included)
|
SXWNISORS485P10001
|
For more information on the RS-485 adapters and the cable required, see the RS-485 Adapter and RS-485 Power Adapter Installation Sheets.
AC input | |
Nominal voltage
|
24 VAC
![]() |
Power consumption
|
18 VA
|
Port types | |
USB host port
|
Type-A, 5 VDC, 0.5 A
|
Ethernet port 1 and 2
|
10/100BASE-TX (RJ45), IEEE 802.3 compliant
|
RS-485 Com A and Com B
|
24 VDC, 3 W, RS-485 (RJ45)
|
Max. 4 W total load
|
|
Wireless connectivity | |
Bluetooth
®
Low Energy (Bluetooth
®
5)
|
2.402 to 2.480 GHz, max. 10 dBm output power, 100 m (328 ft) line-of-sight range
|
Antenna
|
Integrated antenna
|
Approved external antenna (optional)
|
Manufacturer: Linx Technologies, Model: ANT-2.4-WRT-MON-SMA, Gain: 0.8 dBi, Type: Monopole, Impedance: 50 ohm, Connector: SMA
|
Operation environment | |
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
Humidity
|
Maximum 95 % RH non-condensing
|
Mechanical | |
Ingress protection rating
|
IP 20
|
Plastic flame rating
|
UL94 V-0
|
Plenum rating
|
UL 2043 (Approved for plenum installations)
|
IP networking | |
IP address assignment methods
|
Static, DHCP (default), Auto-IP (address range 169.254.0.1 to 169.254.255.254, subnet mask 255.255.0.0)
|
Ub – Universal I/O | |
Input rating
|
24 VDC
![]() |
Voltage output rating
|
0 to 10 VDC
![]() |
Channels
|
RP-V-4A: 4; RP-V-5A: 2
|
DO – Solid-state relay outputs | |
Output rating
|
30 VAC
![]() ![]() |
Max. 3 A total load
|
|
Channels
|