The RP-IO module is available in two models that only support BACnet MS/TP communication. These two models offer two different combinations (sets) of the number and types of I/O points. Both models support 24 VAC/VDC input power.
|
Range |
Model |
BACnet |
I/O–CPU Set |
I/O Points |
CPU Type |
Input Power |
|
EasyLogic RP-IO |
RP-IO-12A-M-24V |
MS/TP |
12A |
12 |
Single-core |
24 VAC or 24-30 VDC |
|
EasyLogic RP-IO |
RP-IO-16E-M-24V |
MS/TP |
16E |
16 |
Single-core |
24 VAC or 24-30 VDC |
For more information, see RP-IO Onboard I/O .
For more information, see RP-IO Module Built-in Power Supply .
All RP-IO models have the same small footprint as most of RP-C controller models.
The EasyLogic range differs significantly from the SpaceLogic range of products not only in terms of the supported BACnet communication protocol (BACnet/IP and/or BACnet MS/TP), but also with regards to several other features.
The EasyLogic models have an “-M” in the product name.
|
Feature |
RP-IO-12A-M-24V, RP-IO-16E-M-24V |
|
Built-in wireless connectivity |
no |
|
Ethernet ports |
0 |
|
USB ports |
0 |
|
RS-485 ports with RJ45 interface |
0 |
|
RS-485 port with screw terminals |
1 a |
|
I/O and power input terminals/connectors |
Fixed screw terminals |
|
MS/TP address configuration |
DIP switch |
|
Room bus support |
no |
|
Sensor bus support |
no |
|
Modbus support |
no |
|
RTD sensor support |
no |
|
LED(s) |
1 b |
|
Real-time clock |
no |
|
Input power |
24 VAC or 24-30 VDC |
|
Power input type |
Isolated |
|
CPU type |
Single-core |
|
Memory (RAM / NOR flash / FRAM) |
6 MB / 32 MB / 128 kB c |