This section outlines the recommended cables and wires, specifying the appropriate wire sizes and lengths for the Central IO modules.
For more information, see I/O Modules .
For more information, see Central IO Modules v2 .
The recommendations are for guidance only. Other wire sizes and lengths may be used, depending on wiring rules and when appropriate.
Terminals | Minimum Cross-sectional Area | Maximum Cable Length |
Digital inputs and universal inputs as digitala inputs | 0.34 mm² (22 AWG) | 200 m (650 ft) |
0.34 mm² (22 AWG) | 100 m (330 ft) | |
Universal inputs as temperature (thermistor) inputs, up to 75 °C (167 °F) | 0.75 mm² (18 AWG) | 75 m (250 ft) |
Universal inputs as temperature (thermistor) inputs, up to 75 °C (167 °F) | 1.5 mm² (15 AWG) | 150 m (500 ft) |
Universal inputs as temperature (thermistor) inputs, up to 150 °C (302 °F) | 1.5 mm² (15 AWG) | 75 m (250 ft) |
Universal inputs, for transmitters powered from the same transformer as the PS-24V power supply | 0.75 mm² (18 AWG) | 20 m (65 ft) |
Universal inputs, for transmitters powered from their own transformer (external or internal) | 0.34 mm² (22 AWG) | 200 m (650 ft) |
Analog outputs as voltage or current outputs, for actuators powered from their own transformer (external or internal) or when the outputs have isolated converters | 0.34 mm² (22 AWG) | 200 m (650 ft) |
Relay outputs | According to local wiring rulesd | According to local wiring rules d |
One Return (RET) terminal from each Central IO module connected to the signal ground rail | 1.3 mm² (16 AWG) | As short as possible within the same panel, maximum 1.5 m (4.8 ft). |