Hardware Installation

Hardware Installation


Products: PS-24V
Functionalities: Hardware, Smoke Control
Product version: 3.3, 2022, 2023, 2024, 7.0
7/7/2025

SpaceLogic™ TB-PS-W1

Part number: SXWTBPSW110001

Safety Information

Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.

Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.

Technical Literature

  • SpaceLogic and EasyLogic - Hardware Installation System Guide, 04-XX001-XX-en

  • EcoStruxure Building Management - Smoke Control System Design Guide, 04-16014-XX-en

The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet, ecoxpert.se.com. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.

Dimensions

 
action_zoom_plus_stroke

Overview

 
action_zoom_plus_stroke

Installing the Terminal Base

Notice

REDUCED LIFE SPAN OF ELECTRONICS MODULE

Always install the terminal base on a horizontal DIN rail to provide sufficient cooling air flow through the electronics module.

Failure to follow these instructions can result in reduced life span of the electronics module.

 
action_zoom_plus_stroke

Connecting the Next Terminal Base

Warning Warning

HAZARD OF ELECTRIC SHOCK OR EQUIPMENT DAMAGE

Ensure that the module type and the terminal base type match.

Failure to follow these instructions can result in death, serious injury, or equipment damage.

 
action_zoom_plus_stroke

I/O Bus Addressing, Power Limits, and Cables

 
action_zoom_plus_stroke

Connections

 
action_zoom_plus_stroke

Wiring

Recommended screw tightening torque: 0.56 Nm (5 lbf.in)

Terminal Base and Electronics Module

Device

Part number

TB-PS-W1 Terminal Base

SXWTBPSW110001

PS-24V Power Supply

SXWPS24VX10001

S-Cables

Device

Part number

S-Cable, 1.5 m, angle

SXWSCABLE10002

S-Cable, 0.75 m, angle

SXWSCABLE10003

Smoke Control Application Note

The input power terminals are power-limited per UL 864 requirements. For more information on the use of the PS-24V power supply for a UL 864 smoke control application, see the latest version of the EcoStruxure Building Management - Smoke Control System Design Guide (04-16014-XX-en).

Specifications

AC input
Nominal voltage
24 VAC
 
action_zoom_plus_stroke
50/60 Hz
Recommended transformer rating
≥60 VA
DC input
Nominal voltage
24 VDC
 
action_zoom_plus_stroke
Power consumption
max. 40 W
DC output
Output voltage
24 V ±1 V
Output power
max. 30 W
Operation environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Humidity
Maximum 95 % RH non-condensing
Mechanical
Ingress protection rating
IP 20
Plastic flame rating
UL94-5VB
Electrical
I/O bus power
24 VDC
 
action_zoom_plus_stroke
max. 30 W per I/O bus power supply, Class 2
Maximum addresses per I/O bus
32

Addendum - California Proposition 65 Warning Statement for California Residents

 
action_zoom_plus_stroke
WARNING: This product can expose you to chemicals including lead which is known to the State of California to cause cancer and which is known to the State of California to cause birth defects or other reproductive harm. For more information go to www.P65Warnings.ca.gov

 
action_zoom_plus_stroke