Part number: SXWPS24VX10001
Electrical equipment should be installed, operated, serviced, and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.
Carefully read these instructions and all information relevant for this product before trying to install it. See the list of technical literature.
SpaceLogic and EasyLogic - Hardware Installation System Guide, 04-XX001-XX-en
EcoStruxure Building Management - Smoke Control System Design Guide, 04-16014-XX-en
The technical literature and declarations of conformity can be accessed on the Schneider Electric extranet, ecoxpert.se.com. Contact your local Schneider Electric sales office for a hard copy of the documentation or for additional information.
The input power terminals are power-limited per UL 864 requirements. For more information on the use of the PS-24V power supply for a UL 864 smoke control application, see the latest version of the EcoStruxure Building Management - Smoke Control System Design Guide (04-16014-XX-en).
Device |
Part number |
PS-24V Power Supply |
SXWPS24VX10001 |
TB-PS-W1 Terminal Base |
SXWTBPSW110001 |
AC input | |
Nominal voltage
|
24 VAC
![]() |
Recommended transformer rating
|
≥60 VA
|
DC input | |
Nominal voltage
|
24 VDC
![]() |
Power consumption
|
max. 40 W
|
DC output | |
Output voltage
|
24 V ±1 V
|
Output power
|
max. 30 W
|
Operation environment | |
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
Humidity
|
Maximum 95 % RH non-condensing
|
Mechanical | |
Ingress protection rating
|
IP 20
|
Plastic flame rating
|
UL94-5VB
|
Electrical | |
I/O bus power
|
24 VDC
![]() |
Maximum addresses per I/O bus
|
32
|