Communication Port Wiring

arrow1_rotationRS-485 Communications arrow1_rotationLonWorks Communications arrow1_rotationUSB Connections arrow1_rotationEthernet Connections

The wiring recommendations for the SmartStruxure server device communication ports apply to the wires and cables used for RS-485 communications, LonWorks communications, USB connections, and Ethernet connections. Always use the recommended cables and wires.

For Automation Server, the LonWorks wiring is made to the terminal base and can be done before the electronics module is fitted. The connections for RS-485 are made to the removable terminal blocks, and the connections for Ethernet and USB are made to the electronics module.

For AS-P, the LonWorks wiring is made to the removable terminal blocks. The connections for RS-485 are made to the removable terminal blocks, and the connections for Ethernet and USB are made to the electronics module.

For AS-B, the connections for RS-485 are made to the removable terminal blocks and can be done before AS-B is installed on the DIN rail. The connections for Ethernet and USB are made directly to the device.

RS-485 Communications

The information in this section provides recommendations for the RS-485 interface port configuration between the SmartStruxure server device and RS-485 network devices. This information is intended to supplement existing guides for the SmartStruxure server device and for the various RS-485 network devices.

Para obtener más información, consulte RS-485 Communications .

LonWorks Communications

Twisted pair cables should be used between the FTT-10 interface on the Automation Server or AS-P terminal base and the TP/FT-10 LonWorks network. The cables should conform to the standard EN 50173-1.

USB Connections

Standard USB cables should be used for connection to the USB host and device ports on the SmartStruxure server device. The recommended maximum cable length is 3 m (10 ft).

Aviso

LOSS OF COMMUNICATION

Do not use a USB cable that exceeds 3 m (10 ft).

Failure to follow these instructions can result in loss of communication.

Ethernet Connections

Standard Ethernet cables with RJ-45 connector should be used for connection to the Ethernet 10/100 port(s) on the SmartStruxure server device, and other devices included in the SmartStruxure solution.

Unshielded cables

Standard UTP Ethernet cables are recommended for the network connections.

Shielded cables

Shielded network cables can be used on cable sections extending through noisy electrical environments. However, shielded network cables cause ground loops. The grounded RJ45 network connector passes the local ground from a device to the shield of the cable, which in turn passes to the ground of the subsequent device. The devices can be SmartStruxure server devices, network switches or routers, or telecom switch equipment.

Shield-induced ground loops can cause the following problems:

  • Degraded performance on communications network

  • Interruption of communication-dependent process control execution

  • Unstable operation and/or restart of the two devices

  • Damage to one or both devices

Advertencia Advertencia

Unintended equipment operation

Equipment damage or loss of communication

  • Ensure adequate electrical bonding is provided between the grounds serving the two device locations to achieve and maintain equal potentials (0 V) between the two devices.

  • Confirm equal potential is maintained when equipment in both areas has power applied and actively functioning.

Failure to follow these instructions can result in equipment damage or loss of communication.

Failure to follow these instructions can result in death, serious injury, or equipment damage.

The objective is to minimize the potential problems created with ground loops in the facility. The effects and risks with ground loops are reduced when the devices are served from the same AC power distribution panel and the devices are in the same general area of the facilities' metal and grounding structure.

  • Wiring
  • Automation Servers
  • AS-Ps
  • RS-485 Communications