Automation Servers

An Automation Server is a Schneider Electric manufactured embedded device that generally serves as the lowest tier SmartStruxure server within the SmartStruxure solution. The Automation Server controls and supervises equipment, typically HVAC equipment. The Automation Server uses I/O modules with connected field devices, such as sensors and actuators, to do that.

Automation Server is based on the patented two-piece design. Each Automation Server consists of an electronics module and a terminal base.

The Automation Server is installed with the I/O modules on DIN rails in cabinets. The Automation Server electronics module uses a W1 enclosure. Power is supplied through the terminal base backplane.

 
action_zoom_plus_stroke Automation Server
Figura: Automation Server

Electronics Modules

The electronics module is the main component of SmartStruxure devices that are based on the patented two-piece design. The electronics module is installed on a terminal base, which constitutes the second component of the device.

Para obtener más información, consulte Electronics Modules .

Terminal Bases

The terminal bases are used for SmartStruxure devices that are based on the patented two-piece design. The terminal base provides the I/O bus to the electronics module installed on the terminal base as well as to the SmartStruxure device installed to the right (next terminal base in the chain).

Para obtener más información, consulte Terminal Bases .

Memory

The Automation Server has two types of memory:

  • 128 MB SDRAM (for program execution)

  • 4 GB flash (for storage)

If a power failure occurs, all important variables are automatically saved to the flash memory before complete shutdown. When power returns, this data retention function ensures that the Automation Server can continue to run with the correct set of values.

Supported Building Standards

The Automation Server natively communicates with three of the most popular communication protocols:

  • BACnet: The Automation Server directly communicates to BACnet/IP and BACnet MS/TP networks, which provides access to b3 devices and BACnet devices.

  • LonWorks: The Automation Server has a built-in FTT-10 port, which enables access to Xenta devices and LonWorks devices.

  • Modbus: The Automation Server natively integrates Modbus RS-485 master and slave configurations, as well as IP client and server. This integration provides access to devices that communicate on the Modbus protocol, such as power meters, circuit breakers, and lighting controllers.

Automation Server Communication Ports

The Automation Server has the following communication ports:

  • 1 Ethernet 10/100 megabit port

  • 2 RS-485 ports

  • 2 LonWorks (TP/FT and RS-485) ports

  • 2 USB host ports

  • 1 USB device port

  • 1 backplane I/O bus port

Para obtener más información, consulte Automation Server Communication Ports .

Automation Server Screw Terminals

There are 12 screw terminals at the top of the Automation Server and 3+4 pluggable screw terminals at the bottom.

Para obtener más información, consulte Automation Server Screw Terminals .

Automation Server LEDs

There are eight LEDs on the front panel of the Automation Server.

Para obtener más información, consulte Automation Server LEDs .

Reset Functions

There are three different types of reset for the SmartStruxure server devices: warm start, cold start, and DFU mode. Depending on the type of reset, the SmartStruxure server device can be reset using the reset button or a command from WorkStation.

Para obtener más información, consulte Reset Functions .

Communication Port Wiring

The wiring recommendations for the SmartStruxure server device communication ports apply to the wires and cables used for RS-485 communications, LonWorks communications, USB connections, and Ethernet connections. Always use the recommended cables and wires.

Para obtener más información, consulte Communication Port Wiring .

SmartStruxure Server Device Replacement Using Restore

Backup and Restore assures that SmartStruxure server devices data can be restored to a replacement SmartStruxure server device in the event of hardware failure, or to the same SmartStruxure server device in the event of data loss. As a precaution, you back up your SmartStruxure server devices regularly so that you can use the most current backup to restore the SmartStruxure server devices data to a replacement SmartStruxure server device. You also configure the new SmartStruxure server device to match the name and the network settings of the replaced SmartStruxure server device so the system can identify this SmartStruxure server device when online.

Para obtener más información, consulte SmartStruxure Server Device Replacement Using Restore .

Especificaciones

Electrical
DC input supply power
7 W
DC input supply voltage
24 VDC
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic rating
UL94-5VB
Enclosure
PC/ABS
Enclosure rating
IP 20
Mechanical
Dimensions including terminal base
90 W x 114 H x 64 D mm (3.6 W x 4.5 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight including terminal base
0.294 kg (0.65 lb)
Weight excluding terminal base
0.194 kg (0.43 lb)
Real-time clock backup
Inaccuracy, at 25 °C (77 °F)
-47 to +73 seconds per month
Backup time
30 days
Communication ports
Ethernet
10/100BASE-TX RJ45
USB
1 device port (type-B) and 2 host ports (type-A)
RS-485
Dual 2-wire ports, bias 3.3 VDC
LonWorks
TP/FT-10
Communications
BACnet
BACnet/IP and MS/TP, port configurable, default 47808
  
BTL B-BC (BACnet Building Controller) a
  
BTL B-OWS (BACnet Operator Workstation) a
a) See the BTL Product Catalog for up-to-date details on BTL listed firmware revisions on BACnet International's home page.
Modbus
Modbus TCP, client and server
  
Serial, RS-485, master or slave
TCP
Binary, port fixed, 4444
HTTP
Non-binary, port configurable, default 80
HTTPS
Encrypted supporting TLS 1.2, 1.1, and 1.0, port configurable default 443
SMTP
Email sending, port configurable, default 25
SNMP
version 3
  
Network supervision using poll and trap
  
Application alarm distribution using trap
LNS
LNS version
OpenLNS
  
Installed on WorkStation PC
LonMark
Resource files version
14.00
CPU
Frequency
160 MHz
Type
AT91RM9200, ARM9 core
SDRAM
128 MB
Flash memory
4 GB

Internal Configuration

All connectors of the Automation Server, except for the Ethernet connector, refer to signal ground as shown in the figure below.

 
action_zoom_plus_stroke Automation Server internal configuration
Figura: Automation Server internal configuration

The I/O bus in the terminal base provides the Automation Server with power and an address.

The address value in the I/O bus is increased by one for each terminal base. The I/O bus also enables RS-485 communication between the I/O module and the SmartStruxure server device.