Products: AO-8, AO-V-8, AS-B, DI-16, DO-FA-12, DO-FC-8, IP-IO , MP-C, MP-V, RP-C, RTD-DI-16, UI-16, UI-8/AO-4, UI-8/AO-V-4, UI-8/DO-FC-4
Functionalities: Hardware
Product version: 3.0
5/13/2019

I/O Wiring

arrow1_rotationShielded Wires arrow1_rotationGrounding and Power arrow1_rotationExternal Device Connections arrow1_rotationWire Sizes and Lengths

The I/O wiring recommendations provide guidance on what type of wires should be used for the different I/O modules, SmartX AS-B server onboard I/O, and SmartX IP Controller device onboard I/O, how to perform grounding, and how to connect different external devices to the inputs and outputs. Always use the recommended cables and wires.

For the I/O modules, most of the wiring is made to the terminal base, and can be done before the electronics module is installed.

For the SmartX AS-B server onboard I/O, MP Series controller onboard I/O, and IP-IO modules, the wiring is made to the removable terminal blocks, and can be done before the SmartX AS-B server, MP Series controller, and IP-IO module are installed on the DIN rail.

For the RP-C controller onboard I/O, the wiring is made to fixed terminal blocks.

Some relay output terminals, I/O modules, or terminal bases may carry lethal voltages. Always disconnect the power supply and other high voltage equipment connected to the device before wiring.

Danger Danger

HAZARD OF ELECTRIC SHOCK, EXPLOSION, OR ARC FLASH

Disconnect the power supply and other high voltage equipment before wiring.

Failure to follow these instructions will result in death or serious injury.

Shielded Wires

For digital inputs and outputs, you can use shielded or unshielded wire. Unshielded wires are usually sufficient.

For analog inputs and outputs, you can use shielded or unshielded wire. Shielded wires are recommended if the wiring is placed in a noisy electrical environment. Connect the shield to ground only at a RET terminal.

If the wiring is placed in a noisy electrical environment, shielded wires are recommended for RTD-DI-16 I/O modules, SmartX AS-B server onboard I/Os, and SmartX IP Controller device onboard I/Os that have the following external connections:

  • RTD temperature input

  • RTD resistive input

  • Resistive input

Grounding and Power

It is important to perform the grounding correctly for the following reasons:

  • To design a system that is not harmed by detected minor connection errors.

  • To design a system that works well and is resistant to EMI.

  • To minimize the effects of ground currents that can cause unstable measurements.

For more information, see Grounding and Power .

External Device Connections

There are many different kinds of external devices from different vendors that can be connected to an EcoStruxure BMS.

For more information, see External Device Connections .

Wire Sizes and Lengths

This section provides recommendations on minimum wire sizes (cross-sectional areas) and maximum wire lengths for the wires connected to the screw terminals of I/O modules, SmartX AS-B servers, and SmartX IP Controller devices. The recommendations are for guidance only. Other wire sizes and lengths may be used, depending on wiring rules and when appropriate.

For more information, see Wire Sizes and Lengths .