规格

规格


产品: AS-P Smoke Control, AS-P
功能: 工程, 硬件, 烟气控制
产品版本: 2024
2024/4/18
请点击查看尚未翻译的更新版本

SpaceLogic AS-P

arrow1_rotation简介 arrow1_rotation特点 arrow1_rotation规格
 
action_zoom_plus_stroke AS-P 服务器
图: AS-P 服务器

简介

At the core of an EcoStruxure BMS is an automation server, such as the SpaceLogic™ AS-P server. The AS-P server performs key functionality, such as control logic, trend logging, and alarm supervision, and supports communication and connectivity to the I/O and field buses. The distributed intelligence of the EcoStruxure BMS helps ensure fault tolerance against detected faults and provides a fully featured user interface through WorkStation and WebStation.

特点

AS-P 服务器是一台强大的设备,可充当独立服务器,还可控制中央 IO 模块和监视器并管理现场总线设备。在小型安装中,嵌入式 AS-P 服务器可充当独立服务器,与它的中央 IO 模块一起安装在一个小面积内。在中型和大型安装中,功能被分配到通过 TCP/IP 通信的多台自动化服务器上。

AS-P 服务器具有以下功能:

  • 通信枢纽

  • 多种连接选项

  • Zigbee 无线网络支持

  • 通过强大的系统实现的身份验证和权限

  • WorkStation/WebStation 界面

  • 原生 BTL 认证 BACnet 支持

  • BACnet/SC 节点、集线器或路由器

  • 原生 LonWorks 支持

  • 原生 OPC UA Client 支持

  • 原生 Modbus 支持

  • 补充楼宇协议支持

  • 基于 Web Services 支持的开放标准

  • EcoStruxure Web Services 支持

  • MQTT IoT 协议支持

  • 外部日志存储选项

  • 报告

  • 可扩展的自定义配置

  • I/O 扩展选项

  • 文本和基于图形的编程工具

  • eMMC 内存用于数据和备份

  • 基于 TCP/IP 通信协议套件的 IT 友好网络

  • TLS 支持

  • 专利两片式设计

  • 自动寻址

  • 简单的 DIN 导轨安装

  • 安全启动

Communications hub

Capable of coordinating traffic from above and below its location, the AS-P server can deliver data directly to you or to other servers throughout the site. The AS-P server can run multiple control programs, manage local I/O, alarms, and users, handle scheduling and logging, and communicate using a variety of protocols. Because of this, most parts of the system function autonomously and continue to run as a whole even if communication is interrupted or individual EcoStruxure BMS servers or devices go offline.

多种连接选项

AS-P 服务器有多个端口,它可以与各种协议、设备和服务器通信。

AS-P 服务器有下列端口:

  • 两个 10/100 以太网端口

  • 两个 RS-485 端口

  • 一个 LonWorks TP/FT 端口(在产品名称中带有“NL”的 AS-P 服务器型号上不可用)

  • 一个内置 I/O 总线端口

  • 一个 USB 设备端口

  • 一个 USB 主机端口

The first Ethernet port is dedicated to the site network. The second Ethernet port is fully configurable. The second port can be configured to extend the site network so that various devices and clients can be connected. Another option is to configure the second port as a separate network, which means that the port can host a private network. This port configuration with dual networks requires hardware version 0.62 or higher. If the second port is not used, it can be disabled.

USB 设备端口允许您使用 Device Administrator 升级 AS-P 服务器并与其交互。

借助 USB 以太网适配器,您可将笔记本电脑连接至 USB 主机端口并运行 Device Administrator、WorkStation 和 WebStation 来对 AS-P 服务器进行升级、配置和访问。USB 主机端口也可用于为 Wireless Adapter - Advanced 提供电源和通信。

Zigbee wireless network support

Through Wireless Adapter - Advanced connected to the host USB port, Zigbee TM wireless connectivity can be enabled for the automation server. The automation server can extend its point count through the Zigbee wireless network and bring flexibility in your applications. The automation server equipped with the adapter is together a Zigbee Certified Product that is compliant with Zigbee 3.0. For more information on the adapter and supported wireless devices, see the Wireless Adapter - Advanced Specification Sheet.

Authentication and permissions

An EcoStruxure BMS provides a powerful permission system that is easy to manage, flexible, and adapts to all kinds of system sizes. The permission system provides a high standard of authentication. Authentication is done against the built-in user account management system or against Windows Active Directory Domains. The built-in account management system allows an administrator to establish password policies that meet stringent cybersecurity guidelines. When Windows Active Directory is used, the administration costs are lower because users do not have to be managed in multiple directories.

WorkStation/WebStation 界面

经由任何客户端进入的用户所获得的体验都是相似的,无论用户登录到哪个 EcoStruxure BMS 服务器。用户可以直接登录 AS-P 服务器,以设计、调试、监督和监控 AS-P 服务器及其连接的中央 IO 模块和现场总线设备。更多信息参见 WorkStation 和 WebStation 规格表。

开放楼宇协议支持

EcoStruxure BMS 的基础之一是支持开放标准。AS-P 服务器原生可与三个最流行的楼宇标准进行通信:BACnet(包括 BACnet/SC)、OPC UA Client、LonWorks 和 Modbus。

原生 BTL 认证 BACnet 支持

AS-P 服务器可与 BACnet/IP 和 BACnet MS/TP 网络直接通信。AS-P 服务器是 BTL 认证的 BACnet 楼宇控制器 (B-BC),是最为高级的 BACnet 设备设置文件。该功能提供访问施耐德电气和其他供应商提供的各种 BACnet 设备的能力。在 BACnet International 首页查看 BTL 产品目录了解 BTL 清单固件修订版本的最新详情。AS-P 服务器还可充当 BACnet 广播管理设备 (BBMD) 来促进横跨多个 IP 子网的 BACnet 系统。

BACnet/SC (Secure Connect) support

The Enterprise Server and automation servers support BACnet/SC applications as a BACnet/SC node, hub, and router. This allows the Enterprise Server and automation servers to be in BACnet/SC networks and support applications that connect BACnet/IP or MS/TP networks with BACnet/SC networks. A major benefit of BACnet/SC is that it allows more secure transport of BACnet traffic and information between BACnet/SC devices over private and public networks without the need for BBMDs, VLANs, and VPNs, because the BACnet/SC protocol uses WebSocket technology and TLS 1.3 encryption. In addition, BACnet/SC uses certificate management to help ensure only those devices authorized to be on a BACnet/SC network can operate on that network.

Native OPC UA Client support

OPC UA Client functionality is natively supported in Enterprise Server and automation servers, enabling powerful and high-capacity integration of devices or systems that have OPC UA Server capability. OPC Unified Architecture (OPC UA) is a standard originating from industrial automation and process control that provides methods intended to provide improved security, performance, and engineering efficiency. With OPC UA Client support, the EcoStruxure Building Operation software can monitor and control a wide variety of devices or systems, from Schneider Electric as well as from other companies.

原生 LonWorks 支持

AS-P 服务器拥有一个内置 FTT-10 端口与 TP/FT-10 LonWorks 网络通信。集成 LonWorks 功能使其能够访问来自施耐德电气和其他供应商的 LonWorks 设备。可利用内置 LonWorks 网络管理工具从 AS-P 服务器对 LonWorks 网络进行调试、绑定和配置。无需第三方工具。具有强大的纠错和网络质量监视功能的协议分析仪可利用第三方软件来实现,无需额外的硬件。为增加易用性,还支持 LNS 设备插件。这样可便于管理和维护来自施耐德电气和其他供应商的 LonWorks 网络。关于如何使用 LNS 设备插件有一些限制。

产品名称中带有“NL”的 AS-P 服务器型号,例如 AS-P-NL 和 AS-P-NLS,不支持 LonWorks。

Native Modbus support

The Enterprise Server and automation servers natively integrate Modbus RS-485 client and server configurations, as well as Modbus TCP client and server. This allows full access to third-party products and the range of Schneider Electric products that communicate on the Modbus protocol, such as power meters, UPS, circuit breakers, and lighting controllers.

Modbus device types are pre-configured Modbus applications for quick and easy Modbus device integration in EcoStruxure Building Operation solutions. For information on the Modbus devices supported using Modbus device types, see the document EcoStruxure Building - Modbus Device Integration - Supported Device Brochure.

补充楼宇协议支持

AS-P 服务器还支持与施耐德电气提供的 BMS 系统和设备的集成和通信,这些系统和设备使用 Andover Continuum Infinet 建筑标准。

Web 服务支持

AS-P 服务器支持基于开放标准(比如 SOAP 和 REST)的 Web 服务的使用,以消耗数据到 EcoStruxure BMS 中。在 Web 上使用输入的第三方数据(温度预测、能源成本)来确定站点模式、日程安排和编程。

EcoStruxure Web Services support

EcoStruxure Web Services, Schneider Electric’s Web Services standard, is natively supported in the EcoStruxure BMS servers. EcoStruxure Web Services offers extra features between compliant systems whether within Schneider Electric or other authorized systems. These features include system directory browsing, read/write of current values, alarm receipt and acknowledgement, and historical trend log data. EcoStruxure Web Services requires user name and password to log on to the system.

MQTT IoT protocol support

The Enterprise Server and automation servers support MQTT as an option for publishing data to, and receiving updates from, other systems. MQTT is a messaging transport protocol that with its small footprint, light bandwidth utilization, and simplicity, is ideal for M2M and IoT communication. The MQTT capability supports communication with any MQTT broker, for example, Amazon, Microsoft, Google or IBM.

外部日志存储选项

EcoStruxure BMS servers can be configured to automatically store all historical data, trend log data, event log and audit trail data, in an external database. If data needs to be available for longer periods of time, an external log storage can be incorporated into the EcoStruxure BMS without the need for extensive engineering work. The supported databases are TimescaleDB, which is built on PostgreSQL, and Microsoft SQL Server. The data in the external log storage is available natively to the viewers built into the EcoStruxure Building Operation clients and to the built-in reporting functionality.

You can use the powerful Log Processor functionality for custom processing of trend data for viewing in charts, dashboards and for inclusion in reports. The Log Processor enables advanced calculations on one or multiple trend logs and point values.

Examples of advanced calculations:

  • Energy usage normalization

  • Virtual submeters and summaries

  • Calculation of Mean Kinetic Temperature

  • Unit conversions

  • Average, maximum, and mini m um over custom periods

The output of the Log Processor can be saved in the database, including the External Log Storage or calculated automatically on demand.

From EcoStruxure Building Operation version 5.0.3 and later, selected trend logs and the event log can be sent to AVEVA PI System directly without the need for intermediate storage or specialized PI System connectors.

Reporting

The EcoStruxure BMS servers provide built-in functionality for basic reporting that can deliver reports in any text format and XLSX, without any dependencies to other external software. Reports for XLSX can be enriched by using advanced functionality such as formulas, conditional formatting, charts and sparklines.

Reports can be generated on schedule, on an alarm event or other custom conditions, and you can get the output delivered via email or written to file.

可扩展的自定义配置

AS-P 服务器及其中央 IO 模块系列的设计旨在满足每种安装的独特需求。根据配置的不同,每台 AS-P 服务器可控制多达 464 个 I/O 点。由于功率和通信沿用公用总线交付,无需工具即可利用内置连接器以简单的一步式流程将多个模块插在一起。

I/O 扩展

For applications that require remote I/O resources, the SpaceLogic IP-IO modules provide a versatile mix of I/O points for any application. For more information, see the SpaceLogic IP-IO Specification Sheet.

Text and graphics-based programming tools

Unique to the industry, the EcoStruxure BMS servers have both Script and Function Block programming options. This flexibility helps assure that a suitable programming method can be selected for the application.

eMMC memory for data and backup

The automation server has a 4 GB eMMC memory, which is used, for example, for the application, historical data, and backup storage. Users can also manually back up or restore the automation server to a storage location on a PC or network. Through the Enterprise Server, users have the ability to perform scheduled backups of associated automation servers to network storage for even greater levels of protection.

IT friendly

The EcoStruxure BMS servers communicate using the networking standards. This makes installations easy, management simple, and transactions more secure.

支持的协议
  • IP 寻址

  • TCP 通信

  • DHCP,用于轻松地配置网络

  • DNS,用于简捷地查找地址

  • HTTP/HTTPS,用于通过防火墙接入互联网,实现远程监控

  • NTP(网络时间协议),用于整个系统的时间同步

  • SMTP/SMTPS 支持基于 SSL/TLS 的身份验证,可发送时间表或报警触发的电子邮件讯息

  • SNMP,用于网络监测和指定网络管理工具中的应用程序报警接收

  • WebSocket Secure (WSS) 和 TLS 1.3 加密(BACnet/SC 应用程序)

TLS support

Communication between clients and the EcoStruxure BMS servers , and between EcoStruxure BMS servers, can be encrypted using Transport Layer Security (TLS ). The servers are delivered with a default self-signed certificate. Commercial Certification Authority (CA) server certificates are supported to lower the risk of malicious information technology attacks. Use of encrypted communication can be enforced for both WorkStation and WebStation access.

Patented two-piece design

Each module can be separated from its terminal base to allow the site to be wired prior to the installation of the electronics. The patented locking mechanism serves as handles for removing the module from its base. All critical components have a protective cover that permits convection cooling to occur.

 
action_zoom_plus_stroke 两片式设计
图: 两片式设计
Auto-addressing

The auto-addressing feature helps eliminating the need for setting DIP switches or pressing commission buttons. Each module automatically knows its order in the chain and assigns itself accordingly – significantly reducing engineering and maintenance time.

Simple DIN-rail installation

Fasteners easily snap into a locked position for panel installation. The fastener has a quick-release feature for easy DIN-rail removal.

Secure boot

Secure boot is a security standard to help ensure that a device boots using only software that is trusted by Schneider Electric.

Secure boot is supported by AS-P server models with “S” in the product name, for example AS-P-S and AS-P-NLS.

规格

Electrical
DC input supply power
10 W
DC input supply voltage
24 VDC
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94-5VB
Enclosure
PC/ABS
Ingress protection rating
IP 20
Mechanical
Dimensions including terminal base
90 W x 114 H x 64 D mm (3.6 W x 4.5 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight including terminal base
0.321 kg (0.71 lb)
Weight excluding terminal base
0.245 kg (0.54 lb)
Agency compliances
Emission
RCM; BS/EN 61000-6-3; BS/EN IEC 63044-5-2; FCC Part 15, Sub-part B, Class B
Immunity
BS/EN 61000-6-2; BS/EN IEC 63044-5-3
Safety standards
BS/EN 60730-1; BS/EN 60730-2-11; BS/EN IEC 63044-3; UL 916 C-UL US Listed
Product
BS/EN IEC 63044-1
Smoke control product safety a
UL 864
Real-time clock
Accuracy in runtime mode
NTP server
Accuracy in backup mode, at 25 °C (77 °F)
+/-52 seconds per month
Backup time, at 25 °C (77 °F)
10 days
Communication ports
Ethernet
Dual 10/100BASE-TX (RJ45)
USB
1 USB 2.0 device port (mini-B)
  
1 USB 2.0 host port (type-A), 5 VDC, 2.5 W
RS-485
Dual 2-wire ports, bias 5.0 VDC
LonWorks a
TP/FT-10
Communications
BACnet
BACnet/IP, port configurable, default 47808
  
BACnet/SC, port configurable, no default port
BACnet profile
BACnet Building Controller (B-BC), BACnet Secure Connect Hub (B-SCHUB), AMEV AS-B
BACnet certification
BTL Certification (BTL Listing a , WSPCert)
OPC UA Client
Profile group UACore 1.03
Core Client Facet, Base Client Behaviour Facet a , AddressSpace Lookup Client Facet, Attribute Read Client Facet a , Attribute Write Client Facet a , DataChange Subscriber Client Facet a , Method Client Facet, UA-TCP UA-SC UA-Binary, SecurityPolicy – Basic256, SecurityPolicy – Basic256Sha256, User Token – Anonymous Facet, User Token – User Name Password Client Facet, DataAccess Client Facet, Base Event Processing Client Facet, and Historical Access Client Facet.
Modbus a
Modbus TCP, client and server
  
Serial, RS-485, client and server
TCP
Binary, port fixed, 4444
HTTP
Non-binary, port configurable, default 80
HTTPS
Encrypted supporting TLS 1.3, 1.2, 1.1 a , and 1.0 a , port configurable default 443
WSS a
Encrypted supporting TLS 1.3, port configurable
SMTP
Email sending, port configurable, default 25
SMTPS
Email sending, port configurable, default 587
SNMP
version 3
  
Network supervision using poll and trap
  
Application alarm distribution using trap
Terminals
AS-P 和 AS-P-S 型号的接线端如下所示。
 
action_zoom_plus_stroke
AS-P-NL 和 AS-P-NLS 型号的接线端如下所示。
 
action_zoom_plus_stroke
LNS
LNS version
OpenLNS
  
Installed on WorkStation PC
LonMark
Resource files version
14.00
CPU
Frequency
500 MHz
Type
SPEAr1380, ARM Cortex-A9 dual-core
DDR3 SDRAM
512 MB
eMMC memory
4 GB
Memory backup
Yes, battery-free, no maintenance
Part numbers
SpaceLogic AS-P
SXWASPXXX10001
SpaceLogic AS-P-S
SXWASPSBX10001
SpaceLogic AS-P-SBA a
SXWASPSBX10A01
SpaceLogic AS-P-NL
SXWASPXXX10002
SpaceLogic AS-P-NLS
SXWASPSBX10002
SpaceLogic AS-P-SMK a
SXWASPXXX1S001
SpaceLogic AS-P-NLS-SMK a
SXWASPSBX1S002
TB-ASP-W1, Terminal Base for AS-P servers
(Required for each AS-P server)
SXWTBASW110002
TB-ASP-W1-BAA, Terminal Base for AS-P servers a
(Required for each AS-P server)
SXWTBASW110A02
Accessory part numbers
AS-P connector kit
SXWASPCON10001
SpaceLogic Wireless Adapter - Advanced
SXWZBAUSB10001
Software bundles
AS-P-S and AS-P-NLS
In the following description, a Connected Product is a communicating device directly connected to a BACnet, Modbus, Infinet, LonWorks, or Zigbee network driven by the AS-P server. A SpaceLogic Central IO module, a device connected to an RP or MP controller, a non-communicating sensor, valve, or actuator, or a LonWorks local node is not a Connected Product.
AS-P – Standalone SW
Support for 10 Connected Products and 6 Central IO modules.
SXWSWXBU0000SA
AS-P – Standard SW
Support for 25 Connected Products, 30 Central IO modules, and Enterprise Server communication.
SXWSWXBU0000SD
AS-P – Enhanced SW
Support for 100 Connected Products, 30 Central IO modules, and Enterprise Server communication.
SXWSWXBU0000EN
AS-P – Full SW
Support for 300 Connected Products, 30 Central IO modules, and Enterprise Server communication.
SXWSWXBU0000FU
Modbus – SpaceLogic AS-P Server
Modbus software add-on, for AS-P-S and AS-P-NLS bundles.
SXWSWX000MBRTU
AS-P Bundle Upgrade – Standalone to Standard
Upgrades from 10 to 25 Connected Products, from 6 to 30 Central IO modules, and adds Enterprise Server communication.
SXWSWXUP00SASD
AS-P Bundle Upgrade – Standalone to Enhanced
Upgrades from 10 to 100 Connected Products, from 6 to 30 Central IO modules, and adds Enterprise Server communication.
SXWSWXUP00SAEN
AS-P Bundle Upgrade – Standalone to Full
Upgrades from 10 to 300 Connected Products, from 6 to 30 Central IO modules, and adds Enterprise Server communication.
SXWSWXUP00SAFU
AS-P Bundle Upgrade – Standard to Enhanced
Upgrades from 25 to 100 Connected Products.
SXWSWXUP00SDEN
AS-P Bundle Upgrade – Standard to Full
Upgrades from 25 to 300 Connected Products.
SXWSWXUP00SDFU
AS-P Bundle Upgrade – Enhanced to Full
Upgrades from 100 to 300 Connected Products.
SXWSWXUP00ENFU
AS-P Upgrade from software version 4.x or 5.x – Standalone
Standalone AS-P upgrade. Upgrades AS-P, AS-P-NL, AS-P-S, or AS-P-NLS from EcoStruxure Building Operation software version 4.x or 5.x to 6.0.
SXWSWASPUP40SA
AS-P Upgrade from software version 4.x or 5.x – Standard
Standard AS-P upgrade. Upgrades AS-P, AS-P-NL, AS-P-S, or AS-P-NLS from EcoStruxure Building Operation software version 4.x or 5.x to 6.0.
SXWSWASPUP40SD
AS-P Upgrade from software version 4.x or 5.x – Enhanced
Enhanced AS-P upgrade. Upgrades AS-P, AS-P-NL, AS-P-S, or AS-P-NLS from EcoStruxure Building Operation software version 4.x or 5.x to 6.0.
SXWSWASPUP40EN
AS-P Upgrade from software version 4.x or 5.x – Full
Full AS-P upgrade. Upgrades AS-P, AS-P-NL, AS-P-S, or AS-P-NLS from EcoStruxure Building Operation software version 4.x or 5.x to 6.0.
SXWSWASPUP40FU
AS-P and AS-P-NL
AS-P Upgrade Non-Secure Boot – Standalone
Standalone AS-P upgrade. Upgrades AS-P or AS-P-NL from EcoStruxure Building Operation software version 3.x to 6.0. Not compatible with secure boot hardware.
SXWSWASPUP30SA
AS-P Upgrade Non-Secure Boot – Standard
Standard AS-P upgrade. Upgrades AS-P or AS-P-NL from EcoStruxure Building Operation software version 3.x to 6.0. Not compatible with secure boot hardware.
SXWSWASPUP30SD
AS-P Upgrade Non-Secure Boot – Enhanced
Enhanced AS-P upgrade. Upgrades AS-P or AS-P-NL from EcoStruxure Building Operation software version 3.x to 6.0. Not compatible with secure boot hardware.
SXWSWASPUP30EN
AS-P Upgrade Non-Secure Boot – Full
Full AS-P upgrade. Upgrades AS-P or AS-P-NL from EcoStruxure Building Operation software version 3.x to 6.0. Not compatible with secure boot hardware.
SXWSWASPUP30FU
AS-P Upgrade Non-Secure Boot – Full – Bulk Pack 125
Bulk pack for upgrading AS-P or AS-P-NL from EcoStruxure Building Operation software version 3.x to 6.0. Contains 125 pieces of SXWSWASPUP30FU.
SXWSWASPUP30BP
AS-P Upgrade from software version 4.x or 5.x – Standalone
Standalone AS-P upgrade. Upgrades AS-P, AS-P-NL, AS-P-S, or AS-P-NLS from EcoStruxure Building Operation software version 4.x or 5.x to 6.0.
SXWSWASPUP40SA
AS-P Upgrade from software version 4.x or 5.x – Standard
Standard AS-P upgrade. Upgrades AS-P, AS-P-NL, AS-P-S, or AS-P-NLS from EcoStruxure Building Operation software version 4.x or 5.x to 6.0.
SXWSWASPUP40SD
AS-P Upgrade from software version 4.x or 5.x – Enhanced
Enhanced AS-P upgrade. Upgrades AS-P, AS-P-NL, AS-P-S, or AS-P-NLS from EcoStruxure Building Operation software version 4.x or 5.x to 6.0.
SXWSWASPUP40EN
AS-P Upgrade from software version 4.x or 5.x – Full
Full AS-P upgrade. Upgrades AS-P, AS-P-NL, AS-P-S, or AS-P-NLS from EcoStruxure Building Operation software version 4.x or 5.x to 6.0.
SXWSWASPUP40FU
Add-on options
AS-P, AS-P-S, AS-P-NL, and AS-P-NLS
SW-EWS-1, EcoStruxure Web Services (run-time) option
Consume only for one automation server
SXWSWEWSXX0001
SW-EWS-2, EcoStruxure Web Services (run-time) option
Serve & Consume for one automation server
SXWSWEWSXX0002
SW-EWS-3, EcoStruxure Web Services (run-time) option
Serve & Consume, plus Historical trend log data for one automation server
SXWSWEWSXX0003
SW-GWS-1, Web Services (Generic Consume) option
For one automation server
SXWSWGWSXX0001
SW-SNMP-1, Alarm notifications via SNMP option
For one automation server
SXWSWSNMPX0001
EcoStruxure Building Operation SmartDriver option
For one AS-P server
SXWSWSDRVX0001
Building Operation Personal Dashboards option, 1 per server required for users logging on to that server to have Personal Dashboard capabilities
For one automation server
SXWSWDASHX0001
SW-ASDBTS-1, TimescaleDB connection option
For one automation server (not required if the parent Enterprise Server has a license)
SXWSWASDBXS001
EcoStruxure Building Operation, Microsoft SQL Server connection option
For one automation server (not required if the parent Enterprise Server has a license)
SXWSWASDBMS001
EcoStruxure Building Operation, AVEVA PI System connection option
For one automation server (not required if the parent Enterprise Server has a license)
SXWSWASDBPI001
SW-ASMQTT-1, MQTT option
For one automation server (not required if the parent Enterprise Server has a license)
SXWSWMQTTXRW01
Building Operation Zoning option
For one automation server or Edge Server
SXWSWASSDZR001
SAML Authentication option
F or one SpaceLogic automation server
SXWSWASSAML001
Sustainability Pack option
For one automation server or Edge Server
SXWSWASXSUSPK1
OPC UA Client option
For one automation server or Edge Server
SXWSWASXOPCL01
Software requirements
External log storage PostgreSQL option
TimescaleDB 1.2 and later
  
For use of compression: TimescaleDB 2.11 and later
  
PostgreSQL version compatible with the TimescaleDB version
Quality assurance testing has been performed by Schneider Electric with TimescaleDB and PostgreSQL installed natively in Windows 10, Windows Server 2012, 2016, and 2019. Other deployment scenarios have not been tested by Schneider Electric.
External log storage Microsoft SQL option
Microsoft SQL Server 2016 SP1 and later
The following Microsoft SQL Server editions are supported: Enterprise, Standard, and Express.
External log storage AVEVA PI System option
PI Web API 2021 SP3 and database compatible with that version
Quality assurance testing has been performed by Schneider Electric with PI Web API 2021 SP3, and database compatible with that version, installed on Windows Server 2019. Other deployment scenarios have not been tested by Schneider Electric.
  • Enterprise Server
  • PS-24V
  • WorkStation