规格

规格


产品: AS-B
功能: 工程, 硬件
产品版本: 2024
2024/8/15
请点击查看尚未翻译的更新版本

SpaceLogic AS-B

arrow1_rotation简介 arrow1_rotation特点 arrow1_rotation规格 arrow1_rotation端子
 
action_zoom_plus_stroke AS-B 服务器
图: AS-B 服务器

简介

At the core of an EcoStruxure BMS is an automation server, such as the SpaceLogic™ AS-B server. The AS-B server performs key functionality, such as control logic, trend logging, and alarm supervision, provides built-in I/O, and supports communication and connectivity to the field buses. The distributed intelligence of the EcoStruxure BMS helps ensure fault tolerance against detected faults and provides a fully featured user interface through WorkStation and WebStation.

特点

AS-B 服务器是一种功能强大的设备,具有内置电源和 I/O,使其适用于各种大小建筑物中 BMS 的机房级控制应用。AS-B 服务器可以作为使用其内置 I/O 的独立服务器或控制器,还可以监控和管理现场总线设备。在小型安装中,嵌入式 AS-B 服务器充当独立的服务器或控制器,安装在较小的占地面积内。在中型和大型安装中,功能被分配到通过 TCP/IP 通信的多台自动化服务器上。

AS-B 服务器具有以下功能:

  • 通信枢纽

  • 多种 I/O 点组合型号

  • I/O 扩展选项

  • 手动强制功能

  • 内置电源

  • 多种连接选项

  • Zigbee 无线网络支持

  • 通过强大的系统实现的身份验证和权限

  • WorkStation/WebStation 界面

  • 原生 BTL 认证 BACnet 支持

  • BACnet/SC 节点、集线器或路由器

  • 原生 OPC UA Client 支持

  • 原生 Modbus 支持

  • 基于 Web Services 支持的开放标准

  • EcoStruxure Web Services 支持

  • MQTT IoT 协议支持

  • 外部日志存储选项

  • 报告

  • 文本和基于图形的编程工具

  • eMMC 内存用于数据和备份

  • 基于 TCP/IP 通信协议套件的 IT 友好网络

  • TLS 支持

  • 简单的 DIN 导轨安装

  • 可拆卸接线端

  • 高效的端子管理

  • 高压瞬变、过电流和短路保护电路

  • SpaceLogic 操作员显示器支持

Communications hub

Capable of coordinating traffic from above and below its location, the AS-B server can deliver data directly to you or to other servers throughout the site. The AS-B server can run multiple control programs, manage built-in I/O, alarms, and users, handle scheduling and logging, and communicate using a variety of protocols. Because of this, most parts of the system function autonomously and continue to run as a whole even if communication is interrupted or individual EcoStruxure BMS servers or devices go offline.

多种 I/O 点组合型号

The AS-B server comes in eight models that offer two different sets of I/O point count and I/O mix.

Model

I/O Points

AS-B-24

24

AS-B-24H

24

AS-B-24-P

24

AS-B-24H-P

24

AS-B-36

36

AS-B-36H

36

AS-B-36-P

36

AS-B-36H-P

36

AS-B servers with “H” in the product name are equipped with a display for output override.

AS-B servers with “P” in the product name are hardware only. An AS-B software package needs to be purchased separately. For more information, see section “Software bundles”.

AS-B servers with 36 I/O points have the same small footprint as AS-B servers with 24 I/O points.

The AS-B server offers a mix of I/O point types that match a wide variety of HVAC applications. Most of the I/O points are universal inputs/outputs, which are highly flexible and can be configured as either inputs or outputs.

AS-B servers with 24 I/O points have the following types:

  • 12 Universal inputs/outputs, Ua type

  • 4 Universal inputs/outputs, Ub type

  • 4 Digital inputs

  • 4 Relay outputs

AS-B servers with 36 I/O points have the following types:

  • 20 Universal inputs/outputs, Ua type

  • 8 Universal inputs/outputs, Ub type

  • 4 Triac outputs

  • 4 Relay outputs

通用输入/输出

The universal inputs/outputs are ideal for any mix of temperature, pressure, flow, status points, and similar point types in a building control system.

The universal inputs/outputs can be configured to read several different types of inputs:

  • Digital

  • Counter

  • Supervised

  • Voltage

  • Current (Ub only)

  • Temperature

  • Resistive

  • 2-Wire RTD temperature

  • 2-Wire RTD resistive

As counter inputs, the universal inputs/outputs are commonly used in energy metering applications. As RTD inputs, they are ideal for temperature points in a building control system. As supervised inputs, they are used for security applications where it is critical to know whether or not a wire has been cut or shorted. These events provide a separate indication of alarms and events in the system.

For all analog inputs, maximum and minimum levels can be defined to automatically detect over-range and under-range values.

The universal inputs/outputs are capable of supporting analog outputs of type voltage outputs. Therefore, the universal inputs/outputs support a wide range of devices, such as actuators.

Only devices with safe extra low voltage equipment (SELV/PELV) inputs/outputs should be connected to the AS-B server universal inputs/outputs.

数字量输入

The digital inputs can be used for cost effective sensing of multiple dry contact digital inputs in applications, such as equipment status monitoring or alarm point monitoring. As counter inputs, digital inputs are commonly used in energy metering applications.

继电器输出

The relay outputs support digital Form A point types. The Form A relays are designed for direct load applications.

Triac 输出

The triac outputs can be used in many applications to switch 24 VAC on or off for external loads such as actuators, relays, or indicators. Triacs are silent and do not suffer from relay contact wear.

I/O 扩展

For applications that require more I/O resources, the SpaceLogic IP-IO modules provide a versatile mix of I/O points for any application. For more information, see the SpaceLogic IP-IO Specification Sheet.

手动强制功能

AS-B servers with “H” in the product name are equipped with an LCD display and keys to support manual override control of analog and digital outputs. This function allows you to manually override the outputs for testing, commissioning, and maintenance of equipment.

The override status is readable through EcoStruxure Building Operation WorkStation and WebStation, enabling precise monitoring and more reliable control.

内置电源

The device has a built-in power supply designed to accommodate 24 VAC or 24 VDC input power. The main AC/DC input (L/+ and N/-) is galvanically isolated from the electronics. This removes the risk of damage due to earth currents and permits the input power to be wired without concern for AC polarity matching.

多种连接选项

AS-B 服务器有多个端口,它可以与各种协议、设备和服务器通信。

AS-B 服务器有下列端口:

  • 两个 10/100 以太网端口

  • 一个 RS-485 端口

  • 一个 USB 设备端口

  • 一个 USB 主机端口

The first Ethernet port is dedicated to the site network. The second Ethernet port is fully configurable. The second port can be configured to extend the site network so that various devices and clients can be connected. Another option is to configure the second port as a separate network, which means that the port can host a private network. If the second port is not used, it can be disabled.

USB 设备端口允许您使用 Device Administrator 升级 AS-B 服务器并与其交互。

借助 USB 以太网适配器,您可将笔记本电脑连接至 USB 主机端口并运行 Device Administrator、WorkStation 和 WebStation 来对 AS-B 服务器进行升级、配置和访问。USB 主机端口也可用于为 Wireless Adapter - Advanced 提供电源和通信。

Zigbee wireless network support

Through Wireless Adapter - Advanced connected to the host USB port, Zigbee TM wireless connectivity can be enabled for the automation server. The automation server can extend its point count through the Zigbee wireless network and bring flexibility in your applications. The automation server equipped with the adapter is together a Zigbee Certified Product that is compliant with Zigbee 3.0. For more information on the adapter and supported wireless devices, see the Wireless Adapter - Advanced Specification Sheet.

Authentication and permissions

An EcoStruxure BMS provides a powerful permission system that is easy to manage, flexible, and adapts to all kinds of system sizes. The permission system provides a high standard of authentication. Authentication is done against the built-in user account management system or against Windows Active Directory Domains. The built-in account management system allows an administrator to establish password policies that meet stringent cybersecurity guidelines. When Windows Active Directory is used, the administration costs are lower because users do not have to be managed in multiple directories.

WorkStation/WebStation 界面

经由任何客户端进入的用户所获得的体验都是相似的,无论用户登录到哪个 EcoStruxure BMS 服务器。用户可直接登录到 AS-B 服务器来设计、调试、管理和监视 AS-B 服务器以及它的内置 I/O 模块和现场总线设备。更多信息参见 WorkStation 和 WebStation 规格表。

开放楼宇协议支持

EcoStruxure BMS 的基础之一是支持开放标准。AS-B 服务器可以与一些最流行的建筑标准进行本地通信:BACnet(包括 BACnet/SC)、OPC UA Client 和 Modbus。

原生 BTL 认证 BACnet 支持

AS-B 服务器可与 BACnet/IP 和 BACnet MS/TP 网络直接通信。AS-B 服务器是 BTL 认证的 BACnet 楼宇控制器 (B-BC),是最为高级的 BACnet 设备设置文件。该功能提供访问施耐德电气和其他供应商提供的各种 BACnet 设备的能力。在 BACnet International 首页查看 BTL 产品目录了解 BTL 清单固件修订版本的最新详情。AS-B 服务器还可充当 BACnet 广播管理设备 (BBMD) 来促进横跨多个 IP 子网的 BACnet 系统。

BACnet/SC (Secure Connect) support

The Enterprise Server and automation servers support BACnet/SC applications as a BACnet/SC node, hub, and router. This allows the Enterprise Server and automation servers to be in BACnet/SC networks and support applications that connect BACnet/IP or MS/TP networks with BACnet/SC networks. A major benefit of BACnet/SC is that it allows more secure transport of BACnet traffic and information between BACnet/SC devices over private and public networks without the need for BBMDs, VLANs, and VPNs, because the BACnet/SC protocol uses WebSocket technology and TLS 1.3 encryption. In addition, BACnet/SC uses certificate management to help ensure only those devices authorized to be on a BACnet/SC network can operate on that network.

Native OPC UA Client support

OPC UA Client functionality is natively supported in Enterprise Server and automation servers, enabling powerful and high-capacity integration of devices or systems that have OPC UA Server capability. OPC Unified Architecture (OPC UA) is a standard originating from industrial automation and process control that provides methods intended to provide improved security, performance, and engineering efficiency. With OPC UA Client support, the EcoStruxure Building Operation software can monitor and control a wide variety of devices or systems, from Schneider Electric as well as from other companies.

Native Modbus support

The Enterprise Server and automation servers natively integrate Modbus RS-485 client and server configurations, as well as Modbus TCP client and server. This allows full access to third-party products and the range of Schneider Electric products that communicate on the Modbus protocol, such as power meters, UPS, circuit breakers, and lighting controllers.

Modbus device types are pre-configured Modbus applications for quick and easy Modbus device integration in EcoStruxure Building Operation solutions. For information on the Modbus devices supported using Modbus device types, see the document EcoStruxure Building - Modbus Device Integration - Supported Device Brochure.

Web 服务支持

AS-B 服务器支持基于开放标准(比如 SOAP 和 REST)的 Web 服务的使用,以消耗数据到 EcoStruxure BMS 中。在 Web 上使用输入的第三方数据(温度预测、能源成本)来确定站点模式、日程安排和编程。

EcoStruxure Web Services support

EcoStruxure Web Services, Schneider Electric’s Web Services standard, is natively supported in the EcoStruxure BMS servers. EcoStruxure Web Services offers extra features between compliant systems whether within Schneider Electric or other authorized systems. These features include system directory browsing, read/write of current values, alarm receipt and acknowledgement, and historical trend log data. EcoStruxure Web Services requires user name and password to log on to the system.

MQTT IoT protocol support

The Enterprise Server and automation servers support MQTT as an option for publishing data to, and receiving updates from, other systems. MQTT is a messaging transport protocol that with its small footprint, light bandwidth utilization, and simplicity, is ideal for M2M and IoT communication. The MQTT capability supports communication with any MQTT broker, for example, Amazon, Microsoft, Google or IBM.

外部日志存储选项

EcoStruxure BMS servers can be configured to automatically store all historical data, trend log data, event log and audit trail data, in an external database. If data needs to be available for longer periods of time, an external log storage can be incorporated into the EcoStruxure BMS without the need for extensive engineering work. The supported databases are TimescaleDB, which is built on PostgreSQL, and Microsoft SQL Server. The data in the external log storage is available natively to the viewers built into the EcoStruxure Building Operation clients and to the built-in reporting functionality.

You can use the powerful Log Processor functionality for custom processing of trend data for viewing in charts, dashboards and for inclusion in reports. The Log Processor enables advanced calculations on one or multiple trend logs and point values.

Examples of advanced calculations:

  • Energy usage normalization

  • Virtual submeters and summaries

  • Calculation of Mean Kinetic Temperature

  • Unit conversions

  • Average, maximum, and mini m um over custom periods

The output of the Log Processor can be saved in the database, including the External Log Storage or calculated automatically on demand.

From EcoStruxure Building Operation version 5.0.3 and later, selected trend logs and the event log can be sent to AVEVA PI System directly without the need for intermediate storage or specialized PI System connectors.

Reporting

The EcoStruxure BMS servers provide built-in functionality for basic reporting that can deliver reports in any text format and XLSX, without any dependencies to other external software. Reports for XLSX can be enriched by using advanced functionality such as formulas, conditional formatting, charts and sparklines.

Reports can be generated on schedule, on an alarm event or other custom conditions, and you can get the output delivered via email or written to file.

Text and graphics-based programming tools

Unique to the industry, the EcoStruxure BMS servers have both Script and Function Block programming options. This flexibility helps assure that a suitable programming method can be selected for the application.

eMMC memory for data and backup

The automation server has a 4 GB eMMC memory, which is used, for example, for the application, historical data, and backup storage. Users can also manually back up or restore the automation server to a storage location on a PC or network. Through the Enterprise Server, users have the ability to perform scheduled backups of associated automation servers to network storage for even greater levels of protection.

IT friendly

The EcoStruxure BMS servers communicate using the networking standards. This makes installations easy, management simple, and transactions more secure.

支持的协议
  • IP 寻址

  • TCP 通信

  • DHCP,用于轻松地配置网络

  • DNS,用于简捷地查找地址

  • HTTP/HTTPS,用于通过防火墙接入互联网,实现远程监控

  • NTP(网络时间协议),用于整个系统的时间同步

  • SMTP/SMTPS 支持基于 SSL/TLS 的身份验证,可发送时间表或报警触发的电子邮件讯息

  • SNMP,用于网络监测和指定网络管理工具中的应用程序报警接收

  • WebSocket Secure (WSS) 和 TLS 1.3 加密(BACnet/SC 应用程序)

TLS support

Communication between clients and the EcoStruxure BMS servers , and between EcoStruxure BMS servers, can be encrypted using Transport Layer Security (TLS ). The servers are delivered with a default self-signed certificate. Commercial Certification Authority (CA) server certificates are supported to lower the risk of malicious information technology attacks. Use of encrypted communication can be enforced for both WorkStation and WebStation access.

Simple DIN-rail installation

Fasteners easily snap into a locked position for panel installation. The fastener has a quick-release feature for easy DIN-rail removal.

可拆卸接线端

AS-B 服务器采用可插拔接线端,易于在设备上安装和拆卸。接线端块随设备交付。

高效的端子管理

输入和输出端均清楚标明。EcoStruxure Building Operation WorkStation 可为 AS-B 服务器生成自定义成品标签。

Protection

Protection components on the universal inputs/outputs, digital inputs, and triac outputs helps protect against high-voltage short-duration transient events. Universal inputs/outputs configured as current inputs (Ub only) have protection against over current. Universal inputs/outputs configured as voltage outputs have current limits to help protect against permanent short-circuit to ground.

SpaceLogic 操作员显示器支持

SpaceLogic Operator Display is an easy HMI based on the BACnet B-OD profile. It can interface and interact with automation servers in a small BMS that require a simple HMI. It features a large 7-inch color touch screen and a preloaded application. It is easy to install and use and does not require any programming. Built for the equipment room, the panel-mounted SpaceLogic Operator Display offers an ingress protection rating of IP65, which makes it both dust-tight and protected from low-pressure water jets. For more information, see the SpaceLogic Operator Display Specification Sheet.

规格

AC input
Nominal voltage
24 VAC
Operating voltage range
+/- 20 %
Frequency
50/60 Hz
Maximum current
0.5 A rms
Recommended transformer rating
≥15 VA
DC input
Nominal voltage
24 to 30 VDC
Operating voltage range
21 to 33 VDC
Maximum power consumption
10 W
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94-5VB
Enclosure
PC/ABS
Ingress protection rating
IP 20
Mechanical
Dimensions
198 W x 110 H x 64 D mm (7.8 W x 4.3 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight, including terminal blocks
0.504 kg (1.111 lb) a
Weight, excluding terminal blocks
0.420 kg (0.926 lb) a
Compatibility
AS-B-24, AS-B-24H, AS-B-36, and AS-B-36H
EcoStruxure BMS server communication
EcoStruxure Building Operation
version 1.8.1 and later
AS-B-24-P, AS-B-24H-P, AS-B-36-P, and AS-B-36H-P
EcoStruxure BMS server communication
EcoStruxure Building Operation
version 4.0.1 and later
Agency compliances
Emission
RCM; BS/EN 61000-6-3; BS/EN IEC 63044-5-2; FCC Part 15, Sub-part B, Class B
Immunity
BS/EN 61000-6-2; BS/EN IEC 63044-5-3
Safety standards
BS/EN 60730-1; BS/EN 60730-2-11; BS/EN IEC 63044-3; UL 916 C-UL US Listed
Product
BS/EN IEC 63044-1
Real-time clock
Accuracy in runtime mode
NTP server
Accuracy in backup mode, at 25 °C (77 °F)
+/-52 seconds per month
Backup time, at 25 °C (77 °F)
10 days
Communication ports
Ethernet
Dual 10/100BASE-TX (RJ45)
USB
1 USB 2.0 device port (mini-B)
  
1 USB 2.0 host port (type-A), 5 VDC, 2.5 W
RS-485
2-wire port, bias 5.0 VDC
Communications
BACnet
BACnet/IP, port configurable, default 47808
  
BACnet/SC, port configurable, no default port
BACnet profile
BACnet Building Controller (B-BC), BACnet Secure Connect Hub (B-SCHUB), AMEV AS-B
BACnet certification
BTL Certification (BTL Listing a , WSPCert)
OPC UA Client
Profile group UACore 1.03
Core Client Facet, Base Client Behaviour Facet a , AddressSpace Lookup Client Facet, Attribute Read Client Facet a , Attribute Write Client Facet a , DataChange Subscriber Client Facet a , Method Client Facet, UA-TCP UA-SC UA-Binary, SecurityPolicy – Basic256, SecurityPolicy – Basic256Sha256, User Token – Anonymous Facet, User Token – User Name Password Client Facet, DataAccess Client Facet, Base Event Processing Client Facet, and Historical Access Client Facet.
Modbus
Modbus TCP, client and server
  
Serial, RS-485, client and server
TCP
Binary, port fixed, 4444
HTTP
Non-binary, port configurable, default 80
HTTPS
Encrypted supporting TLS 1.3, 1.2, 1.1 a , and 1.0 a , port configurable default 443
WSS a
Encrypted supporting TLS 1.3, port configurable
SMTP
Email sending, port configurable, default 25
SMTPS
Email sending, port configurable, default 587
SNMP
version 3
  
Network supervision using poll and trap
  
Application alarm distribution using trap
CPU
Frequency
333 MHz
Type
SPEAr320S, ARM926 core
DDR2 SDRAM
256 MB
eMMC memory
4 GB
Memory backup
Yes, battery-free, no maintenance
Display
Display resolution
128 x 64 pixels
Display size
36 W x 17 H mm (1.4 W x 0.7 H in.)
Display type
FSTN monochrome LCD, white color transflective backlight
Part numbers
SpaceLogic AS-B-24
SXWASB24X10001
SpaceLogic AS-B-24H
Includes display
SXWASB24H10001
SpaceLogic AS-B-24-P
Hardware only, software not included.
SXWASB24PX10001
SpaceLogic AS-B-24H-P
Hardware only, software not included. Includes display.
SXWASB24HP10001
SpaceLogic AS-B-36
SXWASB36X10001
SpaceLogic AS-B-36H
Includes display
SXWASB36H10001
SpaceLogic AS-B-36-P
Hardware only, software not included.
SXWASB36PX10001
SpaceLogic AS-B-36H-P
Hardware only, software not included. Includes display.
SXWASB36HP10001
Accessory part numbers
AS-B connector kit (includes terminal blocks)
SXWASBCON10001
AS-B installer kit
SXWASBINS10001
SpaceLogic Wireless Adapter - Advanced
SXWZBAUSB10001
Software bundles
AS-B-24-P, AS-B-24H-P, AS-B-36-P, and AS-B-36H-P
In the following description, a Connected Product is a communicating device directly connected to a BACnet, Modbus, or Zigbee network driven by the AS-B server. A device connected to an RP or MP controller or a non-communicating sensor, valve, or actuator is not a Connected Product.
AS-B Bundle – Standard
Supports up to 10 Connected Products.
SXWSWXBBU010SD
AS-B Bundle – Full
Supports up to 50 Connected Products.
SXWSWXBBU050FU
AS-B Bundle Upgrade – Standard to Full
Upgrade from 10 to 50 Connected Products
SXWSWXBBUPSDFU
AS-B Upgrade from software version 4.x or 5.x – Standard
Standard AS-B upgrade. Upgrades AS-B-24, AS-B-24-P, AS-B-24H, AS-B-24H-P, AS-B-36, AS-B-36-P, AS-B-36H, or AS-B-36H-P from EcoStruxure Building Operation software version 4.x or 5.x to 6.0, and to support up to 10 Connected Products.
SXWSWASBUP40SD
AS-B Upgrade from software version 4.x or 5.x – Full
Full AS-B upgrade. Upgrades AS-B-24, AS-B-24-P, AS-B-24H, AS-B-24H-P, AS-B-36, AS-B-36-P, AS-B-36H, or AS-B-36H-P from EcoStruxure Building Operation software version 4.x or 5.x to 6.0, and to support up to 50 Connected Products.
SXWSWASBUP40FU
AS-B-24, AS-B-24H, AS-B-36, and AS-B-36H
AS-B Upgrade – Standard
Standard AS-B upgrade. Upgrades AS-B-24, AS-B-24H, AS-B-36, or AS-B-36H from EcoStruxure Building Operation software version 3.x to 6.0, and to support up to 10 Connected Products.
SXWSWASBUP30SD
AS-B Upgrade – Full
Full AS-B upgrade. Upgrades AS-B-24, AS-B-24H, AS-B-36, or AS-B-36H from EcoStruxure Building Operation software version 3.x to 6.0, and to support up to 50 Connected Products.
SXWSWASBUP30FU
AS-B Upgrade from software version 4.x or 5.x – Standard
Standard AS-B upgrade. Upgrades AS-B-24, AS-B-24-P, AS-B-24H, AS-B-24H-P, AS-B-36, AS-B-36-P, AS-B-36H, or AS-B-36H-P from EcoStruxure Building Operation software version 4.x or 5.x to 6.0, and to support up to 10 Connected Products.
SXWSWASBUP40SD
AS-B Upgrade from software version 4.x or 5.x – Full
Full AS-B upgrade. Upgrades AS-B-24, AS-B-24-P, AS-B-24H, AS-B-24H-P, AS-B-36, AS-B-36-P, AS-B-36H, or AS-B-36H-P from EcoStruxure Building Operation software version 4.x or 5.x to 6.0, and to support up to 50 Connected Products.
SXWSWASBUP40FU
Add-on options
SW-EWS-1, EcoStruxure Web Services (run-time) option
Consume only for one automation server
SXWSWEWSXX0001
SW-EWS-2, EcoStruxure Web Services (run-time) option
Serve & Consume for one automation server
SXWSWEWSXX0002
SW-EWS-3, EcoStruxure Web Services (run-time) option
Serve & Consume, plus Historical trend log data for one automation server
SXWSWEWSXX0003
SW-GWS-1, Web Services (Generic Consume) option
For one automation server
SXWSWGWSXX0001
SW-SNMP-1, Alarm notifications via SNMP option
For one automation server
SXWSWSNMPX0001
Building Operation Personal Dashboards option, 1 per server required for users logging on to that server to have Personal Dashboard capabilities
For one automation server
SXWSWDASHX0001
SW-ASDBTS-1, TimescaleDB connection option
For one automation server (not required if the parent Enterprise Server has a license)
SXWSWASDBXS001
EcoStruxure Building Operation, Microsoft SQL Server connection option
For one automation server (not required if the parent Enterprise Server has a license)
SXWSWASDBMS001
EcoStruxure Building Operation, AVEVA PI System connection option
For one automation server (not required if the parent Enterprise Server has a license)
SXWSWASDBPI001
SW-ASMQTT-1, MQTT option
For one automation server (not required if the parent Enterprise Server has a license)
SXWSWMQTTXRW01
Building Operation Zoning option
For one automation server or Edge Server
SXWSWASSDZR001
SAML Authentication option
F or one SpaceLogic automation server
SXWSWASSAML001
Sustainability Pack option
For one automation server or Edge Server
SXWSWASXSUSPK1
OPC UA Client option
For one automation server or Edge Server
SXWSWASXOPCL01
Software requirements
External log storage PostgreSQL option
TimescaleDB 1.2 and later
  
For use of compression: TimescaleDB 2.11 and later
  
PostgreSQL version compatible with the TimescaleDB version
Quality assurance testing has been performed by Schneider Electric with TimescaleDB and PostgreSQL installed natively in Windows 10, Windows Server 2012, 2016, and 2019. Other deployment scenarios have not been tested by Schneider Electric.
External log storage Microsoft SQL option
Microsoft SQL Server 2016 SP1 and later
The following Microsoft SQL Server editions are supported: Enterprise, Standard, and Express.
External log storage AVEVA PI System option
PI Web API 2021 SP3 and database compatible with that version
Quality assurance testing has been performed by Schneider Electric with PI Web API 2021 SP3, and database compatible with that version, installed on Windows Server 2019. Other deployment scenarios have not been tested by Schneider Electric.
Universal inputs/outputs, Ua and Ub
Channels, AS-B servers with 24 I/O points
12 Ua, Ua1 to Ua12
  
4 Ub, Ub1 to Ub4
Channels, AS-B servers with 36 I/O points
20 Ua, Ua1 to Ua20,
  
8 Ub, Ub1 to Ub8
Absolute maximum ratings
-0.5 to +24 VDC
A/D converter resolution
16 bits
Digital inputs
Range
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
Minimum pulse width
120 ms
Counter inputs
Range
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
Minimum pulse width
20 ms
Maximum frequency
25 Hz
Supervised inputs
5 V circuit, 1 or 2 resistors
Monitored switch combinations
Series only, parallel only, and series and parallel
Resistor range
1 to 10 kohm
For a 2-resistor configuration, each resistor must have the same value +/- 5 %
Voltage inputs
Range
0 to 10 VDC
Accuracy
+/-(7 mV + 0.2 % of reading)
Resolution
0.5 mV
Impedance
100 kohm
Current inputs
Range
0 to 20 mA
Accuracy
+/-(0.01 mA + 0.4 % of reading)
Resolution
1 μA
Impedance
47 ohm
Resistive inputs
10 ohm to 10 kohm accuracy
+/-(7 + 4 x 10 -3 x R) ohm
R = Resistance in ohm
10 kohm to 60 kohm accuracy
+/-(4 x 10 -3 x R + 7 x 10 -8 x R 2 ) ohm
R = Resistance in ohm
Temperature inputs (thermistors)
Range
-50 to +150 °C (-58 to +302 °F)
Supported thermistors
Honeywell
20 kohm
Type I (Continuum)
10 kohm
Type II (I/NET)
10 kohm
Type III (Satchwell)
10 kohm
Type IV (FD)
10 kohm
Type V (FD w/ 11k shunt)
Linearized 10 kohm
Satchwell D?T
Linearized 10 kohm
Johnson Controls
2.2 kohm
Xenta
1.8 kohm
Balco
1 kohm
Measurement accuracy
20 kohm
-50 to -30 °C: +/-1.5 °C (-58 to -22 °F: +/-2.7 °F)
  
-30 to 0 °C: +/-0.5 °C (-22 to +32 °F: +/-0.9 °F)
  
0 to 100 °C: +/-0.2 °C (32 to 212 °F: +/-0.4 °F)
  
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F)
10 kohm, 2.2 kohm, and 1.8 kohm
-50 to -30 °C: +/-0.75 °C (-58 to -22 °F: +/-1.35 °F)
  
-30 to +100 °C: +/-0.2 °C (-22 to +212 °F: +/-0.4 °F)
  
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F)
Linearized 10 kohm
-50 to -30 °C: +/-2.0 °C (-58 to -22 °F: +/-3.6 °F)
  
-30 to 0 °C: +/-0.75 °C (-22 to +32 °F: +/-1.35 °F)
  
0 to 100 °C: +/-0.2 °C (32 to 212 °F: +/-0.4 °F)
  
100 to 150 °C: +/-0.5 °C (212 to 302 °F: +/-0.9 °F)
1 kohm
-50 to +150 °C: +/-1.0 °C (-58 to +302° F: +/-1.8 °F)
RTD temperature
Supported RTDs
Pt1000, Ni1000, LG-Ni1000, and JCI-Ni1000
Pt1000
Range
-50 to +150 °C (-58 to +302 °F)
Measurement accuracy
-50 to +70 °C: +/-0.5 °C (-58 to +158 °F: +/-0.9 °F)
  
70 to 150 °C: +/-0.7 °C (158 to 302 °F: +/-1.3 °F)
Ni1000
Range
-50 to +150 °C (-58 to +302 °F)
Measurement accuracy
+/-0.5 °C (+/-0.9 °F)
LG-Ni1000
Range
-50 to +150 °C (-58 to +302 °F)
Measurement accuracy
+/-0.5 °C (+/-0.9 °F)
JCI-Ni1000
Range
-50 to +150 °C (-58 to +302 °F)
Measurement accuracy
+/- 0.5 °C (+/- 0.9 °F)
RTD temperature wiring
Maximum wire resistance
20 ohm/wire (40 ohm total)
Maximum wire capacitance
60 nF
The wire resistance and capacitance typically corresponds to a 200 m wire.
RTD resistive
1,000 ohm
Range
500 to 2,200 ohm
  
Including wiring resistance
Measurement accuracy
+/-(0.2 + 1.5 x 10 -3 x R) ohm
R = resistance in ohm
Resolution
0.1 ohm
RTD resistive wiring
Maximum wire capacitance
60 nF
Voltage outputs
Range
0 to 10 VDC
Accuracy
+/-60 mV
Resolution
10 mV
Minimum load resistance
5 kohm
Load range
-1 to +2 mA
Digital inputs, DI
Channels, AS-B servers with 24 I/O points
4, DI1 to DI4
Channels, AS-B servers with 36 I/O points
0
Absolute maximum ratings
-0.5 to +24 VDC
Digital inputs
Range
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
Minimum pulse width
120 ms
Counter inputs
Range
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
Minimum pulse width
20 ms
Maximum frequency
25 Hz
Relay outputs, DO
Channels, AS-B servers with 24 I/O points
4, DO1 to DO4
Channels, AS-B servers with 36 I/O points
4, DO1 to DO4
Contact rating
250 VAC/30 VDC, 2 A, Pilot Duty (C300)
Switch type
Form A Relay
  
Single Pole Single Throw
  
Normally Open
Isolation contact to system ground
3000 VAC
Cycle life (Resistive load)
At least 100,000 cycles
Minimum pulse width
100 ms
Triac outputs, DO
Channels, AS-B servers with 24 I/O points
0
Channels, AS-B servers with 36 I/O points
4, DO5 to DO8
Output rating
Max. 0.8 A
Voltage
24 VAC +/-20 %
Commons
COM1 for DO5 and DO6
  
COM2 for DO7 and DO8
The common terminals COM1 and COM2 can be connected to 24 VAC or to ground.
Common voltage, high side output
24 VAC
Common voltage, low side output
0 VAC (ground)
Minimum pulse width
100 ms

端子

 
action_zoom_plus_stroke  AS-B 服务器型号,带 24 I/O 点
图: AS-B 服务器型号,带 24 I/O 点
 
action_zoom_plus_stroke  AS-B 服务器型号,带 36 I/O 点
图: AS-B 服务器型号,带 36 I/O 点

For protection from excess current that could be produced by field wiring, follow these instructions:

  • Connect RET terminal number 4 or 5 to a common chassis/signal ground rail in the control panel using a size 2.5 mm² (13 AWG) or larger wire. The wire must have a current rating greater than or equal to 16 A.

  • AS-B servers with 24 I/O points have more RET terminals for connection of I/O returns, so the common chassis/signal ground rail is optional and may not be needed.

  • Individual 24 VDC power sources to the field must be current limited to maximum 4 A for UL compliant installations, and maximum 6 A in other areas.

如需了解有关接线的更多信息,请参阅《SpaceLogic 硬件参考指南》。

  • Enterprise Server
  • WorkStation