earth_america
user_standard Zaloguj się
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Pojęcie

Pojęcie


Produkty: MP-V
Funkcje: Sprzęt
Wersja produktu: 2.0, 2.1, 3.0, 3.1, 3.2, 3.3, 2022, 2023, 2024, 7.0
2023-04-19

Analog Outputs

arrow1_rotationOutputs arrow1_rotationDane techniczne

The analog outputs are capable of supporting analog voltage or current point types. Therefore, analog outputs support a wide range of devices, such as actuators.

Niebezpieczeństwo Niebezpieczeństwo

HAZARD OF ELECTRIC SHOCK, EXPLOSION, OR ARC FLASH

Connect only devices with safe extra low voltage equipment (SELV/PELV) inputs/outputs to the controller universal inputs and analog outputs.

Failure to follow these instructions will result in death or serious injury.

The controller universal inputs and analog outputs are SELV/PELV. Connect only devices with safe extra low voltage equipment (SELV/PELV) inputs/outputs to the controller universal inputs and analog outputs. Connecting devices that are not SELV/PELV poses an electrical hazard that will result in death or serious injury.

Outputs

Voltage outputs

The analog outputs can be configured as voltage outputs.

 
action_zoom_plus_stroke Voltage output internal configuration and connection of external resistive load
Rysunek: Voltage output internal configuration and connection of external resistive load

R OUT is approximately equal to 10 ohm.

V OUT range is 0 to 10 VDC.

R LOAD minimum is 5 kohm.

Current outputs

The analog outputs can also be configured as current outputs.

 
action_zoom_plus_stroke Current output internal configuration and connection of external resistive load
Rysunek: Current output internal configuration and connection of external resistive load

I OUT range is 0 to 20 mA.

R LOAD maximum is 650 ohm.

Dane techniczne

Channels, MP-V-7A
1, VO1/CO1
Channels, MP-V-9A
2, VO1/CO1 and VO2/CO2
Analog output protection
Transient voltage suppressor on each output
Voltage outputs
Range
0 to 10 VDC
Accuracy
+/-60 mV
Resolution
10 mV
Minimum load resistance
5 kohm to ground
Load range
0 to +2 mA
Terminals
Voltage Output (VO), Return (RET)
Current outputs
Range
0 to 20 mA
Accuracy
+/-0.2 mA
Resolution
21 µA
Load range
0 to 650 ohm
Terminals
Current Output (CO), Return (RET)
  • MP-V Controllers
  • MP-V Onboard I/O