earth_america
user_standard Connexion
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Produits : MP-C
Fonctionnalités : Matériel
Version produit : 3.3
05/10/2023

MP-C Controllers

The MP-C controller is a multi-purpose, fully programmable, IP based field controller. The MP-C models offer a flexible mix of I/O point types that suits a wide range of HVAC applications. MP-C is a native SpaceLogic device, which can either be used as a standalone BACnet/IP field controller or as part of an EcoStruxure BMS with a AS-P or AS-B server, or an Enterprise Server, as the parent server.

MP-C allows for flexible control solutions due to the dual Ethernet ports, the interface to SpaceLogic Sensor devices, and the versatile mix of universal inputs/outputs, triac outputs, relay outputs, and high power relay outputs.

When MP-Cs are part of an EcoStruxure BMS, you can take full advantage of the existing EcoStruxure Building Operation engineering tools.

The MP-C can be installed on a DIN rail or other flat surface inside a cabinet.

All MP-C models can be equipped with MP-C Display, which is an optional add-on module for output override. The MP-C Display can also be used to view and locally configure inputs and outputs.

 
action_zoom_plus_stroke MP-C
Figure : MP-C

MP-C Models

The MP-C comes in five models with different I/O point count and different I/O point mix.

Pour plus d'informations, voir MP-C Models .

MP-C Onboard I/O

The MP-C models offer a versatile mix of I/O point types that match a wide variety of applications. Most of the I/O points are universal inputs/outputs, which are highly flexible and can be configured as either inputs or outputs.

Pour plus d'informations, voir MP-C Onboard I/O .

Output Override Function (Optional)

The output override function allows you to manually override outputs. This function can be used for testing, commissioning, and maintenance of equipment.

Pour plus d'informations, voir Output Override Function .

MP-C Built-in Power Supply

The MP-C has a built-in power supply designed to accommodate 24 VAC at 50/60 Hz or 24 to 30 VDC input power.

Pour plus d'informations, voir MP-C Built-in Power Supply .

BACnet/IP Device Memory

BACnet/IP devices have three types of memory:

  • Flash memory: for boot loader, operating system, application software, and configuration storage

  • RAM: for runtime operation

  • FRAM non-volatile memory: for data retention in the case of power outage

Pour plus d'informations, voir BACnet/IP Controller Device Memory .

BACnet/IP Controller Supported Building Standards

One of the cornerstones of the EcoStruxure BMS is support for open standards. As a result, the BACnet/IP controller complies with the BACnet open standard, one of the most popular standards for buildings.

Pour plus d'informations, voir BACnet/IP controller Supported Building Standards .

MP Controller Communication Ports

The MP controller contains a combination of Ethernet, USB, and SpaceLogic Sensor communication ports.

Pour plus d'informations, voir MP Controller Communication Ports .

BACnet/IP Controller Sensor Bus

The BACnet/IP controller provides a sensor bus, which allows SpaceLogic Sensor devices to be connected to the controller.

Pour plus d'informations, voir MP Controller Sensor Bus .

MP-C Screw Terminals

The MP-C is delivered with terminal blocks installed on the device. The MP-C uses pluggable terminal blocks, which are easy to install and remove from the device.

Pour plus d'informations, voir MP-C Screw Terminals .

MP Controller LEDs

There are five LEDs on the front panel of the MP controller.

Pour plus d'informations, voir MP Controller LEDs .

MP Controller Reset Modes

You can reset and restart the MP controllers in different ways depending on how long you press the reset button. The resets and restarts can affect the retention of values after restart based on the retain levels configured for the variables.

Pour plus d'informations, voir MP Controller Reset Modes .

MP-C Device Installation

The MP-C can be installed on a DIN rail or other flat surface inside a cabinet. The device is recommended to be installed in a cabinet, unless local regulations allow an exception.

Pour plus d'informations, voir MP-C Device Installation .

Wiring

The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, BACnet/IP devices, RP controller expansion modules, and Operator Display.

Pour plus d'informations, voir Wiring .

BACnet/IP Device Firmware Management

Using WorkStation, you can update the firmware of multiple BACnet/IP devices and their attached SpaceLogic Sensor devices at the same time with minimum downtime. In particular, the universal upgrade package simplifies the update process and requires minimal user involvement and coordination.

Déclaration

SpaceLogic Sensor devices are supported by the BACnet/IP controllers - MP and RP controllers.

Pour plus d'informations, voir BACnet/IP Device Firmware Management .

Spécifications

AC input
Nominal voltage
24 VAC
Operating voltage range
+/- 20 %
Frequency
50/60 Hz
Maximum power consumption (MP-C-15A, -18A, -18B)
22 VA
Maximum power consumption (MP-C-24A)
28 VA
Maximum power consumption (MP-C-36A)
33 VA
Power input protection
MOV suppression and internal fuse
DC input
Nominal voltage
24 to 30 VDC
Operating voltage range
21 to 33 VDC
Maximum power consumption (MP-C-15A, -18A, -18B)
12 W
Maximum power consumption (MP-C-24A)
15 W
Maximum power consumption (MP-C-36A)
18 W
Power input protection
MOV suppression and internal fuse
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F) at normal operation a
  
-40 to +60 °C (-40 to +140 °F) for rooftop applications, horizontal installation only a
Ambient temperature, storage
-40 to +70 °C (-40 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94-5V
Ingress protection rating
IP 20
Mechanical
Dimensions (MP-C-15A, -18A, -18B)
153 W x 110 H x 64 D mm (6.0 W x 4.3 H x 2.5 D in.)
 
action_zoom_plus_stroke
Dimensions (MP-C-24A, -36A)
234 W x 110 H x 64 D mm (9.2 W x 4.3 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight, MP-C-15A
Including terminal blocks
0.358 kg (0.789 lb)
Weight, MP-C-18A
Including terminal blocks
0.371 kg (0.818 lb)
Weight, MP-C-18B
Including terminal blocks
0.361 kg (0.796 lb)
Weight, MP-C-24A
Including terminal blocks
0.495 kg (1.091 lb)
Weight, MP-C-36A
Including terminal blocks
0.547 kg (1.206 lb)
Recommended installation
DIN rail or flat surface in a cabinet a
Terminal blocks
Removable
Real-time clock
Accuracy, at 25 °C (77 °F)
+/-1 minute per month
Backup time, at 25 °C (77 °F)
7 days minimum
Communication ports
Ethernet
Dual 10/100BASE-TX (RJ45)
USB
1 USB 2.0 device port (mini-B)
  
1 USB 2.0 host port (type-A), 5 VDC, 2.5 W
Sensor bus
24 VDC, 2 W, RS-485 (RJ45)
Sensor bus protection
Transient voltage suppressors on communication and power signals
Communications
BACnet
BACnet/IP, port configurable, default 47808
  
BTL B-AAC (BACnet Advanced Application Controller) a
CPU
Frequency
500 MHz
Type
ARM Cortex-A7 dual-core
DDR3 SDRAM
128 MB
NOR flash memory
32 MB
Memory backup
128 kB, FRAM, non-volatile
MP-C Display (Optional)
Removable
No
Display size
36 W x 17 H mm (1.4 W x 0.7 H in.)
Display resolution
128 x 64 pixels
Display type
FSTN monochrome LCD, white color transflective backlight
Power consumption
max. 0.15 W (45 mA at 3.3 V)
Ambient temperature, operating
-30 to +60 °C (-22 to +140 °F)
Ambient temperature, storage
-40 to +70 °C (-40 to +158 °F)
Maximum humidity
95 % RH non-condensing
Weight
0.035 kg (0.077 lb)

Internal Configuration

The MP-C internal configuration with regards to the signal ground is shown in the following figure.

 
action_zoom_plus_stroke MP-C internal configuration
Figure : MP-C internal configuration
  • Hardware Overview
  • MP-C Models
  • MP-C Onboard I/O
  • Output Override Function
  • MP-C Built-in Power Supply
  • BACnet/IP Controller Device Memory
  • BACnet/IP controller Supported Building Standards
  • MP Controller Communication Ports
  • MP Controller Sensor Bus
  • MP-C Screw Terminals
  • MP Controller LEDs
  • MP Controller Reset Modes
  • MP-C Device Installation
  • Wiring
  • BACnet/IP Device Firmware Management