High Power Relay Outputs

arrow1_rotationOutputs arrow1_rotationSpecifications

The main application of the high power relay output is to power an electrical heating element directly.

The outputs can be configured as one of the following types:

  • Digital output

  • Digital pulsed output

  • Pulse width modulated output

Consider the expected number of operation cycles specified for the relay output (cycle life rating) when configuring the period for a pulse width modulated (PWM) output point.

Outputs

The DO high power relay outputs are Form A digital outputs, which means the outputs are normally open contacts with one common terminal (C) and one normally open terminal (NO). The terminals are isolated from signal ground.

 
action_zoom_plus_stroke Form A digital output internal configuration
Figure: Form A digital output internal configuration

Specifications

Channels, MP-C-15A
1, DO7
Channels, MP-C-18A
1, DO8
Channels, MP-C-18B
0
Channels, MP-C-24A
0
Channels, MP-C-36A
0
Channels, MP-C-24A-M
0
Channels, MP-C-36A-M
0
Contact rating
250 VAC/24 VDC, 12 A, Pilot Duty (B300)
Switch type
Form A Relay
  
Single Pole Single Throw
  
Normally Open
Isolation contact to system ground
5000 VAC
Cycle life (Resistive load)
At least 100,000 cycles
Minimum pulse width
100 ms