MP-C-24A has 24 I/O points and the controller is equipped with seven pluggable terminal blocks.
Recommended screw tightening torque: 0.56 Nm (5 lbf.in)
The terminal blocks are used as follows:
One 3-position pluggable terminal block for the power input
One 6-position pluggable terminal block for the four universal inputs/outputs of type Uc
One 8-position pluggable terminal block for the four relay outputs
Four 6-position pluggable terminal blocks for the 16 universal inputs/outputs of type Ub
|
Terminal number |
Designation |
Usage |
|
Power input |
|
|
|
1 |
24 VAC/DC |
24 VAC, 50/60 Hz, 28 VA Positive lead (+) when operating the device from 24-30 VDC, 15 W |
|
2 |
|
Earth ground lead of 24 VAC transformer connects to terminals 2 or 3. Terminals 2 and 3 are internally connected. Negative (–) lead when operating the device from 24-30 VDC, 15 W |
|
3 |
|
Terminal 3 is provided for convenience to connect to protective earth ground (optional). Terminals 2 and 3 are internally connected. |
|
Universal inputs/outputs |
|
|
|
4 |
Uc1 |
Universal input/output, type Uc |
|
5 |
RET |
Internally connected to all earth ground and RET terminals |
|
6 |
Uc2 |
Universal input/output, type Uc |
|
7 |
Uc3 |
Universal input/output, type Uc |
|
8 |
RET |
Internally connected to all earth ground and RET terminals |
|
9 |
Uc4 |
Universal input/output, type Uc |
|
Relay outputs |
|
|
|
16 |
DO1 |
Relay output, type Form A |
|
17 |
DO1 |
Relay output, type Form A |
|
18 |
DO2 |
Relay output, type Form A |
|
19 |
DO2 |
Relay output, type Form A |
|
20 |
DO3 |
Relay output, type Form A |
|
21 |
DO3 |
Relay output, type Form A |
|
22 |
DO4 |
Relay output, type Form A |
|
23 |
DO4 |
Relay output, type Form A |
|
Universal inputs/outputs |
|
|
|
32 |
Ub1 |
Universal input/output, type Ub |
|
33 |
RET |
Internally connected to all earth ground and RET terminals |
|
34 |
Ub2 |
Universal input/output, type Ub |
|
35 |
Ub3 |
Universal input/output, type Ub |
|
36 |
RET |
Internally connected to all earth ground and RET terminals |
|
37 |
Ub4 |
Universal input/output, type Ub |
|
38 |
Ub5 |
Universal input/output, type Ub |
|
39 |
RET |
Internally connected to all earth ground and RET terminals |
|
40 |
Ub6 |
Universal input/output, type Ub |
|
41 |
Ub7 |
Universal input/output, type Ub |
|
42 |
RET |
Internally connected to all earth ground and RET terminals |
|
43 |
Ub8 |
Universal input/output, type Ub |
|
44 |
Ub9 |
Universal input/output, type Ub |
|
45 |
RET |
Internally connected to all earth ground and RET terminals |
|
46 |
Ub10 |
Universal input/output, type Ub |
|
47 |
Ub11 |
Universal input/output, type Ub |
|
48 |
RET |
Internally connected to all earth ground and RET terminals |
|
49 |
Ub12 |
Universal input/output, type Ub |
|
50 |
Ub13 |
Universal input/output, type Ub |
|
51 |
RET |
Internally connected to all earth ground and RET terminals |
|
52 |
Ub14 |
Universal input/output, type Ub |
|
53 |
Ub15 |
Universal input/output, type Ub |
|
54 |
RET |
Internally connected to all earth ground and RET terminals |
|
55 |
Ub16 |
Universal input/output, type Ub |