earth_america
user_standard 登录
action_search_stroke
earth_america
登录以评价并提供反馈 1 2 3 4 5 登录以评价
0
概念

概念


产品: AS-B
功能: 硬件
产品版本: 2.0, 2.1, 3.0, 3.1, 3.2
2021/3/18

Screw Terminals for SmartX AS-B Servers with 36 I/O Points

SmartX AS-B servers with 36 I/O points use nine pluggable terminal blocks and one fixed terminal block.

Recommended screw tightening torque: 0.56 Nm (5 lbf.in)

 
action_zoom_plus_stroke Screw terminals and other connectors, SmartX AS-B server with 36 I/O points
图: Screw terminals and other connectors, SmartX AS-B server with 36 I/O points

The terminal blocks are used as follows:

  • One 3-position pluggable terminal block for the power input

  • One 2-position fixed terminal block for the two return (RET) terminals 4 and 5

  • One 4-position pluggable terminal block for the RS-485 communication

  • One 6-position pluggable terminal block for the six universal inputs/outputs of type Ub

  • One 6-position pluggable terminal block for the four triac outputs

  • One 8-position pluggable terminal block for the four relay outputs

  • Four 6-position pluggable terminal blocks for the 20 universal inputs/outputs of type Ua

    One of the terminal blocks also accomodates two terminals for universal inputs/outputs of type Ub.

表格: Screw Terminals, SmartX AS-B Server with 36 I/O Points

Terminal number

Designation

Usage

Power input

1

L/+

Line (L) lead when operating the device from 24 VAC, 50/60 Hz, 15 VA

Positive (+) lead when operating the device from 24-30 VDC, 10 W

2

N/–

Neutral (N) lead when operating the device from 24 VAC, 50/60 Hz, 15 VA

Negative (–) lead when operating the device from 24-30 VDC, 10 W

3

 
action_zoom_plus_stroke

Earth ground

Return terminals

4

RET

Internally connected to terminal 3 (earth ground)

5

RET

Internally connected to terminal 3 (earth ground)

RS-485

6

Bias +

5.0 VDC, RS-485 bias supply, current limited 40 mA

7

TX/RX +

RS-485 communication

8

TX/RX –

RS-485 communication

9

RET

Internally connected to terminal 3 (earth ground)

Universal inputs/outputs, type Ub

10

Ub1

Universal input/output, type Ub

11

Ub2

Universal input/output, type Ub

12

Ub3

Universal input/output, type Ub

13

Ub4

Universal input/output, type Ub

14

Ub5

Universal input/output, type Ub

15

Ub6

Universal input/output, type Ub

Triac outputs

16

DO5

Triac output

17

COM1

Common connection for DO5 and DO6

The COM terminal can be connected to 24 VAC for high-side switching or to ground for low-side switching.

18

DO6

Triac output

19

DO7

Triac output

20

COM2

Common connection for DO7 and DO8

The COM terminal can be connected to 24 VAC for high-side switching or to ground for low-side switching.

21

DO8

Triac output

Relay outputs

22

DO1

Relay output, type Form A

23

DO1

Relay output, type Form A

24

DO2

Relay output, type Form A

25

DO2

Relay output, type Form A

26

DO3

Relay output, type Form A

27

DO3

Relay output, type Form A

28

DO4

Relay output, type Form A

29

DO4

Relay output, type Form A

Universal inputs/outputs, type Ub

30

Ub7

Universal input/output, type Ub

31

Ub8

Universal input/output, type Ub

Universal inputs/outputs, type Ua

32

Ua1

Universal input/output, type Ua

33

Ua2

Universal input/output, type Ua

34

Ua3

Universal input/output, type Ua

35

Ua4

Universal input/output, type Ua

36

Ua5

Universal input/output, type Ua

37

Ua6

Universal input/output, type Ua

38

Ua7

Universal input/output, type Ua

39

Ua8

Universal input/output, type Ua

40

Ua9

Universal input/output, type Ua

41

Ua10

Universal input/output, type Ua

42

RET

Internally connected to terminal 3 (earth ground)

43

Ua11

Universal input/output, type Ua

44

Ua12

Universal input/output, type Ua

45

Ua13

Universal input/output, type Ua

46

Ua14

Universal input/output, type Ua

47

Ua15

Universal input/output, type Ua

48

RET

Internally connected to terminal 3 (earth ground)

49

Ua16

Universal input/output, type Ua

50

Ua17

Universal input/output, type Ua

51

Ua18

Universal input/output, type Ua

52

Ua19

Universal input/output, type Ua

53

Ua20

Universal input/output, type Ua

The screw terminals 6 to 9, intended for RS-485 communication, act as connectors to the SmartX AS-B server and are easily inserted/removed without disrupting the network. Doing so may help in isolating possible RS-485 communication problems.

  • SmartX AS-B Servers
  • SmartX AS-B Server Screw Terminals
  • Wiring