earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Products: Commission, MP-V
Functionalities: Engineering, BACnet/IP devices
Product version: 2022
12/17/2021

Flow Balancer Workflow

Use this workflow to perform flow balance on a single MP-V controller, using the Commission mobile application. Related information can be found in the section after the flowchart.

For more information, see Flow Balancing .

 
action_zoom_plus_stroke Flow Balance workflow
Figure: Flow Balance workflow
Log in and start the Commission mobile application

Start the Commission mobile application and log in as either a Technician or Flow Balancer.

For more information, see Downloading and Starting the eCommission SmartX Controllers Mobile Application .

Connect to an MP-V

Discover controllers on the site, and connect to a single MP-V.

For more information, see Device Connection .

Configure air balancing setpoints

You configure the MP-V controller setpoints to set up the parameters by which the controller is flow balanced. These setpoints include the maximum flow setpoint, selected by default, and the intermediate and minimum flow setpoints, which are optional.

For more information, see Configuring MP-V Controller Setpoints .

Calibrate velocity pressure offset

Once the setpoints are configured and before the flow balance is started, the damper is forced closed to obtain an average reading of the zero flow threshold before continuing to balance for each setpoint. You can either apply these changes, or ignore once the calculation is completed.

For more information, see VAV Objects Provided for the Commission Mobile Application .

For more information, see VAV Controller Automatic Velocity Pressure Offset Calibration .

Balance at setpoints

Using the Commission mobile application, you flow balance a VAV unit at each designated setpoint to achieve the desired air flow.

For more information, see Flow Balancing at Minimum, Intermediate, or Maximum Flow Setpoint .

Perform manual checkout

After flow balancing the MP-V controller, you can perform manual checkout on two components of the MP-V:

  • Manual checkouts of air flow

    After completing the automated flow balancing process, you can optionally verify and command the air flow values by performing manual checkout.

    For more information, see Performing Manual Checkout of Air Flow .

Generate a flow balance report

After completing flow balancing, you can use the Commission mobile application to create, append, view, or delete flow balance reports. For more information, see Managing Flow Balance Reports .

  • Flow Balancing
  • Downloading and Starting the eCommission SmartX Controllers Mobile Application
  • Copy Object Type Names
  • Configuring MP-V Controller Setpoints
  • Flow Balancing at Minimum, Intermediate, or Maximum Flow Setpoint
  • Manually Verifying the Direction of Damper Rotation
  • Performing Manual Checkout of Air Flow
  • Managing Flow Balance Reports
  • VAV Objects Provided for the Commission Mobile Application
  • VAV Controller Automatic Velocity Pressure Offset Calibration