earth_america
user_standard Iniciar sesión
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concepto

Concepto


Productos MP-C, MP-V, RP-C, RP-V
Funcionalidades: Ingeniería, Dispositivos SmartX IP Controller
Versión del producto: 2024
26/08/2024

Commission Mobile Application Overview

arrow1_rotationDevice Connection arrow1_rotationBluetooth Adapter arrow1_rotationDevice Configuration arrow1_rotationConfiguration Menu arrow1_rotationI/O Checkout arrow1_rotationFlow Balancing arrow1_rotationDevice Restart

The Commission mobile application allows you to use a mobile device to perform commissioning, flow balance, and checkout operations on SpaceLogic BACnet/IP devices. BACnet/IP devices include BACnet/IP controllers (MP and RP), and IP-IO modules. The Commission mobile application is available for Android and iOS (Apple) phones and tablets, as well as devices using Microsoft Windows. The Commission mobile application can connect to a single BACnet/IP device or to a network of BACnet/IP devices on the local network.

Device Connection

The Commission mobile application supports device connection through BACnet Wi-Fi and wireless Bluetooth connection.

Para obtener más información, consulte Conexión del dispositivo .

Bluetooth Adapter

The SpaceLogic Bluetooth Adapter allows you to establish a Bluetooth connection to SpaceLogic and EasyLogic controllers that contain an extra COM port. You plug the Bluetooth adapter into the corresponding SpaceLogic Sensor to connect to the controller.

Para obtener más información, consulte Adaptador Bluetooth SpaceLogic .

Device Configuration

You configure the device settings of a BACnet/IP device so that it can communicate on the network. For example, in the Commission Mobile Application, you can configure the BACnet/IP controller so that it can communicate on the IP network, or configure it as an MS/TP device to enable it to communicate on an MS/TP network.

Para obtener más información, consulte Configuración del dispositivo Controlador BACnet/IP .

Configuration Menu

Configuration Menus are a group of pre-engineered objects and values that make device commissioning faster and easier. Configuration Menus are exported and downloaded from image files. Download a Configuration Menu to a BACnet/IP controller to commission the controller.

Para obtener más información, consulte Menú de configuración .

I/O Checkout

After you have wired the physical inputs and outputs of the controller, you perform I/O checkout to verify that the wiring was done correctly and that the physical inputs and outputs are working properly.

Para obtener más información, consulte Vista general de la comprobación de E/S .

Flow Balancing

The Flow Balance function of the Commission mobile application is used to air balance terminal boxes controlled by VAV controllers. This function automates most of the air balance procedure but it also allows you to manually check out the flow balance by driving the damper to a specified position, a flow setpoint, or a flow value.

Para obtener más información, consulte Equilibrado de flujo .

Device Restart

Use the Device Restart function of the Commission mobile application to perform a restart of the BACnet/IP controller. There are four different ways to restart the BACnet/IP controller.

Para obtener más información, consulte Reinicio del dispositivo .

  • Conexión del dispositivo
  • Adaptador Bluetooth SpaceLogic
  • Configuración del dispositivo Controlador BACnet/IP
  • Menú de configuración
  • Vista general de la comprobación de E/S
  • Equilibrado de flujo
  • Reinicio del dispositivo