Using the eCommission SmartX Controllers mobile application, you flow balance a VAV unit at each designated setpoint to achieve the desired air flow.
One, two, or three flow setpoints can be selected for flow balancing. The maximum flow setpoint is selected by default. In addition, you can also select the intermediate flow setpoint or the minimum flow setpoint, or both. The VAV unit is automatically flow balanced at the chosen setpoints, in sequence, using the same process at each setpoint.
In the Air Balancing Setpoints view, the Intermediate flow and Minimum flow setpoint check boxes are cleared by default. However, it is recommended that you include either or both these setpoints for flow balancing, in addition to the Maximum flow setpoint. Doing so allows you to achieve greater flow accuracy across the operating flow range of the VAV unit.
When the flow balance process begins, the eCommission application automatically checks for correct damper rotation. If a message is displayed, saying that the direction of rotation is not correct, choose to either allow the application to automatically correct the direction of rotation or dismiss the message.
In the Balance at Maximum Flow view, select the information icon
During flow balancing at maximum flow, the MP-V controller's actuator rotates the damper, which is driven until a stable flow is produced at the flow setpoint.
Monitor Box measured flow until its value reaches the setpoint and remains within tolerance for 10 seconds, signifying that the flow has stabilized.
In the Air Balancing Setpoints view, the Flow tolerance value defines how close the measured box flow must be to the associated setpoint before the eCommission application automatically advances, so that the flow balancer can measure and record diffuser flow values.
On the terminal box being balanced, position a flow hood at one of the outlet diffusers and then record the flow. Repeat this for any additional outlet diffusers on the terminal box.
Select the grayed portion of the window to open the Balance at Maximum view.
In the Diffuser 1 flow box, type the measured flow value recorded in the previous step.
In the Diffuser 2 flow box, type the next measured flow value.
Continue typing measured flow values for any additional outlet diffusers.
Hood measured flow is calculated by the sum of the Diffuser values. For example, if you have two diffusers, the hood measured flow will be the sum of Diffuser1 and Diffuser2 measurements. The Hood Measured Flow should be similar to the Box Measured Flow value.
In the Comment field, enter a comment to add to the Air Balancing Report.
Select Next . After completing flow balance at the maximum flow setpoint, the eCommission application automatically proceeds to flow balancing at the intermediate and minimum flow setpoints, if selected.
The VAV unit is flow balanced at the selected setpoints. Now you are ready to perform manual checkout.