You perform I/O checkout to verify that the wiring between the devices was done correctly and to verify that the physical inputs and outputs are working properly.
In the Device List , select a BACnet/IP controller.
Only one BACnet/IP controller at a time can be selected for I/O checkout.
Select Next .
From the Menu , select I/O Checkout .
In the Inputs and Outputs page, select the check box next to the point. You can select up to five objects at once.
Select Checkout .
For inputs , cause or simulate a change to the physical input device and then observe the value in the Commission mobile application to determine that the input is responding as expected.
For outputs , change the value and then select Force . Observe the physical output to determine that it is responding as expected.
When you are finished forcing values and verifying the responses, select Unforce to revert the values.
Select the Refresh button at any time to view the current value of the point.
In the Comment text box, type a comment that will be included in the I/O checkout report.
Change Checkout status to Complete . If the input or output did not check out correctly, change Checkout status to Failed .
Select Save to transfer the checkout data to the I/O checkout report.
Select Back to return to the Inputs and Outputs view and then repeat the process until all the I/O points are verified.
You have completed checkout of the inputs and outputs on the BACnet/IP controller, and identified any failed connections that must be corrected. Selecting the Save button generates an I/O Checkout report which is stored in the BACnet/IP controller within diagnostic files. Więcej informacji zawiera Viewing an I/O Checkout Report .