You perform I/O checkout to verify that the wiring between the devices was done correctly and to verify that the physical inputs and outputs are working properly.
In the Commission mobile application, connect to the BACnet/IP controller.
Only one BACnet/IP controller at a time can be selected for I/O checkout.
On the tab bar, click Commission .
Click I/O Checkout .
On the I/O Resources page, click Onboard I/O .
On the Inputs and Outputs page, select up to five points for checkout.
Click Checkout .
On the Input/Output Checkout page, test each point:
For inputs, cause or simulate a change to the physical input device and then observe the value in the Commission mobile application to determine that the input is responding as expected.
For outputs, change the value and then select Force . Observe the physical output to determine that it is responding as expected.
When you are finished forcing values and verifying the responses, select Unforce to revert the values.
Select the Refresh button at any time to view the current value of the point.
In the Comment text box, type a comment that will be included in the I/O checkout report.
Change Checkout status to Complete . If the input or output did not check out correctly, change Checkout status to Failed .
Click Done to transfer the checkout data to the I/O checkout report.
Click the Back arrow to return to the Inputs and Outputs page and then repeat the process until all the I/O points are verified.
You have completed checkout of the inputs and outputs on the BACnet/IP controller, and identified any failed connections that must be corrected. Clicking the Done button generates an I/O Checkout report which is stored in the BACnet/IP controller within diagnostic files. Более подробную информацию см. Viewing an I/O Checkout Report .