earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
How to

How to


Products: SpaceLogic Sensors
Functionalities: Hardware, LCD
Product version: 3.3, 2022, 2023, 2024, 7.0
7/23/2021

Changing the Temperature Setpoint

In the SpaceLogic Sensor LCD Temperature Sensor model, you change the temperature setpoint to increase living space comfort by using the available buttons. You enable the temperature setpoint by configuring the Display object Allow setpoint changes , followed by the Setpoint hig h limi t and Setpoint low limit properties. In this way, you can use the desired setpoint to control applications through the Setpoint property.

Show More
action_close

You use the SpaceLogic Sensor Display property tabs in WorkStation to view and configure the UI features of the various sensor models within your control application.

Property Tabs

The Display Basic tab properties includes the same General Information you find on all EcoStruxure Building Operation objects. Beyond that, it also provides a Setpoint , a Fan speed , an Occupancy override , an HVAC mode , a Heating cooling status , and 4 Custom value text fields. In addition, there are several properties that allow you to control the temperature display. For example, the Temperature display mode allows you to configure the temperature value displayed on the SpaceLogic Sensor display in its passive display state with the following settings:

  • Live Temperature : Displays the space temperature measured by the SpaceLogic sensors internal temperature sensor

  • Temperature setpoint : Displays the current setpoint temperature value

  • Custom temperature : Displays the value of the Custom temperature property

The Custom temperature property then allows you to display any value in the temperature range, either by referencing another temperature source (for example, an external temperature sensor) or by setting it manually in the Custom temperature field (warm start retained only).

Advanced Tab

The Display Advanced property tab includes considerably more configuration information. For example, you turn on the Allow menu page property to display all submenus including the Functions menu and any of its submenus. Should you wish, you can enable the temperature setpoint feature by setting the Display object Allow setpoint changes property to On and configuring the Setpoint high limit and Setpoint low limit properties. If colored wall back lighting feedback is required for the room occupant, you can turn on the Enable wall back lighting property.

Note:

Allow setpoint changes, Setpoint high limit, and Setpoint low limit are the types of properties you may wish to drive dynamically based on time of day. For example, using a schedule, you may only allow setpoint changes during the day and not at night. You may also only change the high and low limits for the setpoint based on whether you are in the heating or cooling season.

You can also enable lighting and blind control functions using the Display object Allow light control and Allow blind control properties. Within the light function, you can toggle on and off or set a percentage to control the intensity of the lights using the Lighting mode property. Similarly, you can you can toggle on and off or set a percentage to control the blind louver sub-function using the Blind control mode property.

Button and Scene Configuration Tab

The Display Button and Scene Configuration property tab allows you to select from the available functions or scenes to program the buttons on the SpaceLogic Sensor display models. You can also select the buttons you wish to display for configured scenes and triggers for each of the scene buttons.

For more information, see Configuring SpaceLogic Sensor Display Properties .

Property Mapping

While the Display property tabs allow you to configure varied SpaceLogic Sensor models with different UI features, not all of the properties apply to each model. Be sure to consider this when configuring the application and binding it to your control programs. The table that follows shows the properties applicable to each unit.

Table: SpaceLogic Sensor and Display Object Property Mapping

Display property

Touchscreen Display

LCD Temperature Sensor

3-Button Cover

Setpoint

Yes

Yes

Yes

Fan speed

Yes

Yes

No

Occupancy override

Yes

Yes

Yes

HVAC mode

Yes

Yes

No

Selected scene

Yes

Yes

No

Light level

Yes

Yes

No

Blind position

Yes

Yes

No

Blind slat angle

Yes

Yes

No

Temperature display mode

Yes

Yes

No

Custom temperature

Yes

Yes

No

Heating cooling status

Yes

Yes

No

Show time

Yes

No

No

Time format

Yes

No

No

Show CO2

Yes

Yes

No

Show humidity

Yes

Yes

No

Temperature units

Yes

Yes

No

Allowed fan speeds

Yes

Yes

No

Enable wall back lighting

No

No

Yes

Lighting mode

Yes

Yes

No

Blind control mode

Yes

Yes

No

Blind angle mode

Yes

Yes

No

Allowed HVAC modes

Yes

Yes

No

Allow setpoint changes

Yes

Yes

Yes

Setpoint high limit

Yes

Yes

Yes

Setpoint low limit

Yes

Yes

Yes

Allow fan speed changes

Yes

Yes

No

Allow occupancy overrides

Yes

Yes

No

Allow HVAC mode changes

Yes

Yes

No

Allow menu pages

Yes

No

No

Allow sensors information pages

Yes

No

No

Allow device information page

Yes

No

No

Allow parent information page

Yes

No

No

Allow custom information page

Yes

No

No

Allow temperature unit changes

Yes

Yes

No

Allow light control

Yes

Yes

No

Allow blind control

Yes

Yes

No

Display backlight

Yes

No

No

Button (1-12) function

Yes

Yes

No

Scene button (1-8) button

Yes

Yes

No

Scene button (1-8) trigger

Yes

Yes

No

SpaceLogic Living Space Sensor / Eco mode

Yes

Yes

Yes

To change the temperature setpoint
  1. In the SpaceLogic Sensor LCD Temperature Sensor, in the default temperature menu, press the

     
    action_zoom_plus_stroke
    button.

    The icon blinks to indicate that you are actively editing the temperature setpoint.

     
    action_zoom_plus_stroke
  2. In editing mode, press the

     
    action_zoom_plus_stroke
    or
     
    action_zoom_plus_stroke
    buttons to reach the desired temperature setpoint.

    Tip:

    The setpoint may differ from the actual temperature reading.

    The icon continues to blink while you are in editing mode.

  3. Wait for six seconds for the setpoint to return to temperature.

    The icon returns to a normal, solid grey and the numbers now denote temperature rather than setpoint.

     
    action_zoom_plus_stroke
  • SpaceLogic Display Properties
  • SpaceLogic Sensor LCD Temperature Sensor Model
  • Configuring SpaceLogic Sensor Display Properties