earth_america
user_standard Iniciar sessão
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Conceito

Conceito


Produtos: RP-C
Funcionalidades: Hardware
Versão do produto: 3.0, 3.1, 3.2, 3.3
14-06-2022

Solid-state Relay (SSR) Outputs

arrow1_rotationOutputs arrow1_rotationEspecificações

The solid-state relay (SSR) outputs can be used in many applications to switch 24 VAC or 24 VDC on or off for external loads such as actuators, relays, or indicators. SSRs are silent and are not adversely affected by relay contact wear.

The outputs can be configured as one of the following types:

  • Digital output

  • Digital pulsed output

  • Pulse width modulated output

  • Tristate output

  • Tristate pulsed output

Outputs

The DO SSR outputs are Form A digital outputs, which means the outputs are normally open contacts with one common terminal and one normally open terminal. Each pair of SSR outputs share a common terminal but the outputs can be controlled independently.

 
action_zoom_plus_stroke SSR digital output internal configuration
Imagem: SSR digital output internal configuration

Especificações

Channels, RP-C-12A-F-24V
4, DO1 to DO4
Channels, RP-C-12B-F-24V
0
Channels, RP-C-12C-F-24V
4, DO1 to DO4
Channels, RP-C-16A-F-230V
4, DO1 to DO4
Output rating
Maximum 2 A load per output
  
Maximum 4 A total load for the 4 outputs
AC voltage range
Maximum 30 VAC
DC voltage range
Maximum 30 VDC
Commons
COM1 for DO1 and DO2 (on RP-C-12A, -12C, and -16A models)
  
COM2 for DO3 and DO4 (on RP-C-12A, -12C, and -16A models)
When the SSR outputs are used to switch AC, the common terminals can be connected to 0 to 30 VAC. When the SSR outputs are used to switch DC, the common terminals can be connected to -30 VDC to +30 VDC.
Common voltage range (AC)
0 to 30 VAC
Common voltage range (DC)
-30 to +30 VDC
Minimum pulse width
100 ms
Solid-state relay output protection
Transient voltage suppressor across each solid-state relay (SSR) output
  • RP-Cs
  • RP-C Onboard I/O