BACnet/IP controller – RP-C is a room-purpose, fully programmable, IP based field controller. The RP-C models offer a flexible mix of I/O point types that suit a wide range of HVAC applications. The controller can either be used as a standalone BACnet/IP field controller or as part of an EcoStruxure BMS with an AS-P or AS-B server or an Enterprise Server as the parent server. The RP-C features a wireless chip that allows a mobile device running the eCommission SmartX Controllers mobile application to connect directly to the controller.
The RP-C allows for flexible control solutions due to the dual Ethernet ports, the interface to SpaceLogic Sensor devices, the interface for support of Connected Room Solution (CRS) devices, and the versatile mix of universal inputs/outputs, solid-state relay (SSR) outputs, relay outputs, and high power relay outputs.
When RP-Cs are part of an EcoStruxure BMS, you can take full advantage of the existing EcoStruxure Building Operation engineering tools.
The RP-C comes in four different models, which offer four different sets of I/O point types, named 12A, 12B, 12C, and 16A.
Para mais informações, consulte RP-C Models .
The RP-C-12A, -12B, -12C, and -16A models provide 12 or 16 I/O points, consisting of four different sets of I/O point types. The versatile mix of I/O point types match a wide variety of applications. The universal inputs/outputs are highly flexible and can be configured as either inputs or outputs.
Para mais informações, consulte RP-C Onboard I/O .
The RP-C-12A, -12B, and -12C models have a built-in power supply designed to accommodate a nominal operating voltage of 24 VAC at 50/60 Hz or 24 to 30 VDC input power. The RP-C-16A model's power supply is designed for a nominal operating voltage of 230 VAC at 50/60 Hz.
Para mais informações, consulte RP-C Built-in Power Supply .
BACnet/IP devices have three types of memory:
Flash memory: for boot loader, operating system, application software, and configuration storage
RAM: for runtime operation
FRAM non-volatile memory: for data retention in the case of power outage
Para mais informações, consulte BACnet/IP Controller Device Memory .
One of the cornerstones of the EcoStruxure BMS is support for open standards. As a result, the BACnet/IP controller complies with the BACnet open standard, one of the most popular standards for buildings.
Para mais informações, consulte BACnet/IP controller Supported Building Standards .
RP-C is a Bluetooth Low Energy (BLE) enabled product. You can use this wireless connectivity option for connecting a smartphone or tablet running the eCommission SmartX Controllers mobile application to the RP-C.
Para mais informações, consulte RP-C Wireless Connectivity .
The RP-C provides the following combination of communication ports:
Two Ethernet ports
Two USB ports
Two RS-485 ports
Para mais informações, consulte RP-C Communication Ports .
The RP-C sensor bus allows SpaceLogic Sensor devices to be connected to the controller.
Para mais informações, consulte RP-C Sensor Bus .
The RP-C room bus allows RP controller expansion modules and multi-sensors to be connected to the controller for motion detection, luminosity measurements, communication with remote control (RP-C-RC-BLE), and control of electric lights and window blinds.
Para mais informações, consulte RP-C Room Bus .
The RP-C Modbus network allows standard Modbus devices and the KNX Modbus gateway (RP-C-EXT-KNX) to be connected to the controller.
Para mais informações, consulte RP-C Modbus .
The RP-C has fixed screw terminals for the power input, SSR outputs, relay outputs, high power relay outputs, and universal inputs/outputs.
Para mais informações, consulte RP-C Screw Terminals .
There is one LED on the front panel of the RP-C.
Para mais informações, consulte RP-C LEDs .
You can reset and restart the RP controllers in different ways depending on how long you press the reset button. The resets and restarts can affect the retention of values after restart based on the retain levels configured for the variables.
Para mais informações, consulte RP Controller Reset Modes .
The RP-C can be installed on a DIN rail or flat surface.
Para mais informações, consulte RP-C Device Installation .
The RP-C-16A model has a 24 VAC (19 VA) Class 2 output that can be used to power external loads such as actuators, relays, or indicators. The external loads can be controlled using the controller's solid-state relay (SSR) or relay outputs.
Para mais informações, consulte 24 VAC Output on the RP-C-16A Controller .
The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, BACnet/IP devices, and RP controller expansion modules, and Operator Display.
Para mais informações, consulte Wiring .
Using WorkStation, you can update the firmware of multiple BACnet/IP devices and their attached SpaceLogic Sensor devices, RP controller expansion modules, and multi-sensors at the same time with minimum downtime. In particular, the universal upgrade package simplifies the update process and requires minimal user involvement and coordination.
SpaceLogic Sensor devices, RP controller expansion modules, and multi-sensors are supported by the RP controller.
Para mais informações, consulte BACnet/IP Device Firmware Management .
This section provides information on regulatory compliance and approvals for the RP-C controllers.
Para mais informações, consulte RP-C Regulatory Compliance and Approvals .
AC input | |||||||||||
RP-C-12A, -12B, and -12C models | |||||||||||
Nominal voltage
|
24 VAC
|
||||||||||
Operating voltage range
|
+/-15 %
|
||||||||||
Frequency
|
50/60 Hz
|
||||||||||
Maximum power consumption
|
23 VA
|
||||||||||
Power input protection
|
MOV suppression and internal fuse
|
||||||||||
RP-C-16A model | |||||||||||
Nominal voltage
|
230 VAC
|
||||||||||
Operating voltage range
|
+/-10 %
|
||||||||||
Frequency
|
50/60 Hz
|
||||||||||
Maximum power consumption
|
65 VA
|
||||||||||
Power consumption without load
|
5 VA
|
||||||||||
Power input protection
|
MOV suppression and internal fuse
|
||||||||||
Separate PTC thermistor used as a resettable fuse for 24 VAC Out only
|
|||||||||||
Overvoltage category
|
III
|
||||||||||
Pollution degree
|
2
|
||||||||||
DC input | |||||||||||
RP-C-12A, -12B, and -12C models | |||||||||||
Nominal voltage
|
24 to 30 VDC
|
||||||||||
Operating voltage range
|
23 to 33 VDC
|
||||||||||
Maximum power consumption
|
14 W
|
||||||||||
Power input protection
|
MOV suppression and internal fuse
|
||||||||||
AC output | |||||||||||
RP-C-16A model | |||||||||||
Type
|
Isolated Class 2 output
|
||||||||||
Nominal voltage
|
24 VAC
|
||||||||||
Frequency
|
Same frequency as the power supply (50/60 Hz)
|
||||||||||
Output power rating
|
19 VA
|
||||||||||
Environment | |||||||||||
RP-C-12A, -12B, and -12C models | |||||||||||
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F) at normal operation
|
||||||||||
-40 to +60 °C (-40 to +140 °F) for rooftop applications, horizontal installation only
|
|||||||||||
Ambient temperature, storage
|
-20 to +70 °C (-4 to +158 °F)
|
||||||||||
Maximum humidity
|
95 % RH non-condensing
|
||||||||||
RP-C-16A model | |||||||||||
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
||||||||||
Ambient temperature, storage
|
-20 to +70 °C (-4 to +158 °F)
|
||||||||||
Maximum humidity
|
95 % RH non-condensing
|
||||||||||
Material | |||||||||||
Plastic flame rating
|
UL94-5VB
|
||||||||||
Ingress protection rating
|
IP 20
|
||||||||||
Mechanical | |||||||||||
Dimensions
|
180 W x 110 H x 64 D mm (7.1 W x 4.3 H x 2.5 D in.)
|
||||||||||
|
|||||||||||
Weight, RP-C-12A model
|
0.370 kg (0.816 lb)
|
||||||||||
Weight, RP-C-12B and -12C models
|
0.390 kg (0.860 lb)
|
||||||||||
Weight, RP-C-16A model
|
0.720 kg (1.587 lb)
|
||||||||||
Weight, optional covers
|
0.070 kg (0.154 lb)
|
||||||||||
Installation
|
DIN rail or flat surface
|
||||||||||
Terminal blocks
|
Fixed
|
||||||||||
Optional covers | |||||||||||
Dimensions
|
181 W x 164 H x 64 D mm (7.1 W x 6.5 H x 2.5 D in.)
|
||||||||||
|
|||||||||||
Real-time clock | |||||||||||
Accuracy, at 25 °C (77 °F)
|
+/-1 minute per month
|
||||||||||
Backup time, at 25 °C (77 °F)
|
7 days minimum
|
||||||||||
Communication ports | |||||||||||
Ethernet
|
Dual 10/100BASE-TX (RJ45)
|
||||||||||
USB
|
1 USB 2.0 device port (mini-B)
|
||||||||||
1 USB 2.0 host port (type-A), 5 VDC, 2.5 W
|
|||||||||||
RS-485 port “Sensor Bus” (Com A)
|
24 VDC, 2 W, RS-485 (RJ45)
|
||||||||||
Transient voltage suppressors on communication and power signals
|
|||||||||||
RS-485 port “Room Bus” (Com B)
|
24 VDC, 3 W, RS-485 (RJ45)
|
||||||||||
Transient voltage suppressors on communication and power signals
|
|||||||||||
Communications | |||||||||||
BACnet
|
BACnet/IP, port configurable, default 47808
|
||||||||||
BTL B-AAC (BACnet Advanced Application Controller)
a
|
|||||||||||
a) See the BTL Product Catalog for up-to-date details on BTL listed firmware revisions on BACnet International's home page. | |||||||||||
Wireless connectivity | |||||||||||
Bluetooth Low Energy | |||||||||||
Communication protocol
|
Bluetooth
®
5.0 Low Energy compliant
|
||||||||||
Frequency
|
2.402 to 2.480 GHz
|
||||||||||
Maximum output power
|
10 dBm
|
||||||||||
Maximum communication distance
|
Line-of-sight: 100 m (328 ft)
|
||||||||||
Antenna
|
Integrated antenna
|
||||||||||
RF connector for optional external antenna
|
SMA connector
|
||||||||||
External antenna (optional)
|
Restricted to the approved antenna type listed below (used in certification)
|
||||||||||
|
|||||||||||
CPU | |||||||||||
Frequency
|
500 MHz
|
||||||||||
Type
|
ARM Cortex-A7 single-core
|
||||||||||
Internal SRAM
|
6 MB
|
||||||||||
NOR flash memory
|
32 MB
|
||||||||||
Memory backup
|
128 kB, FRAM, non-volatile
|
The RP-C internal configuration with regards to the signal ground is shown in the following figures.