earth_america
user_standard Iniciar sessão
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Conceito

Conceito


Produtos: RP-C
Funcionalidades: Hardware
Versão do produto: 3.3
16-07-2021

RP-Cs

arrow1_rotationRP-C Models arrow1_rotationRP-C Onboard I/O arrow1_rotationRP-C Built-in Power Supply arrow1_rotationBACnet/IP Controller Device Memory arrow1_rotationBACnet/IP Controller Supported Building Standards arrow1_rotationRP-C Wireless Connectivity arrow1_rotationRP-C Communication Ports arrow1_rotationRP-C Sensor Bus arrow1_rotationRP-C Room Bus arrow1_rotationRP-C Modbus arrow1_rotationRP-C Screw Terminals arrow1_rotationRP-C LEDs arrow1_rotationRP Controller Reset Modes arrow1_rotationRP-C Device Installation arrow1_rotation24 VAC Output on RP-C-16A Model arrow1_rotationWiring arrow1_rotationBACnet/IP Controller Device Firmware Management arrow1_rotationRP-C Regulatory Compliance and Approvals arrow1_rotationEspecificações arrow1_rotationInternal Configuration

BACnet/IP controller – RP-C is a room-purpose, fully programmable, IP based field controller. The RP-C models offer a flexible mix of I/O point types that suit a wide range of HVAC applications. The controller can either be used as a standalone BACnet/IP field controller or as part of an EcoStruxure BMS with an AS-P or AS-B server or an Enterprise Server as the parent server. The RP-C features a wireless chip that allows a mobile device running the eCommission SmartX Controllers mobile application to connect directly to the controller.

The RP-C allows for flexible control solutions due to the dual Ethernet ports, the interface to SpaceLogic Sensor devices, the interface for support of Connected Room Solution (CRS) devices, and the versatile mix of universal inputs/outputs, solid-state relay (SSR) outputs, relay outputs, and high power relay outputs.

When RP-Cs are part of an EcoStruxure BMS, you can take full advantage of the existing EcoStruxure Building Operation engineering tools.

 
action_zoom_plus_stroke RP-C
Imagem: RP-C

RP-C Models

The RP-C comes in four different models, which offer four different sets of I/O point types, named 12A, 12B, 12C, and 16A.

Para mais informações, consulte RP-C Models .

RP-C Onboard I/O

The RP-C-12A, -12B, -12C, and -16A models provide 12 or 16 I/O points, consisting of four different sets of I/O point types. The versatile mix of I/O point types match a wide variety of applications. The universal inputs/outputs are highly flexible and can be configured as either inputs or outputs.

Para mais informações, consulte RP-C Onboard I/O .

RP-C Built-in Power Supply

The RP-C-12A, -12B, and -12C models have a built-in power supply designed to accommodate a nominal operating voltage of 24 VAC at 50/60 Hz or 24 to 30 VDC input power. The RP-C-16A model's power supply is designed for a nominal operating voltage of 230 VAC at 50/60 Hz.

Para mais informações, consulte RP-C Built-in Power Supply .

BACnet/IP Controller Device Memory

BACnet/IP devices have three types of memory:

  • Flash memory: for boot loader, operating system, application software, and configuration storage

  • RAM: for runtime operation

  • FRAM non-volatile memory: for data retention in the case of power outage

Para mais informações, consulte BACnet/IP Controller Device Memory .

BACnet/IP Controller Supported Building Standards

One of the cornerstones of the EcoStruxure BMS is support for open standards. As a result, the BACnet/IP controller complies with the BACnet open standard, one of the most popular standards for buildings.

Para mais informações, consulte BACnet/IP controller Supported Building Standards .

RP-C Wireless Connectivity

RP-C is a Bluetooth Low Energy (BLE) enabled product. You can use this wireless connectivity option for connecting a smartphone or tablet running the eCommission SmartX Controllers mobile application to the RP-C.

Para mais informações, consulte RP-C Wireless Connectivity .

RP-C Communication Ports

The RP-C provides the following combination of communication ports:

  • Two Ethernet ports

  • Two USB ports

  • Two RS-485 ports

Para mais informações, consulte RP-C Communication Ports .

RP-C Sensor Bus

The RP-C sensor bus allows SpaceLogic Sensor devices to be connected to the controller.

Para mais informações, consulte RP-C Sensor Bus .

RP-C Room Bus

The RP-C room bus allows RP controller expansion modules and multi-sensors to be connected to the controller for motion detection, luminosity measurements, communication with remote control (RP-C-RC-BLE), and control of electric lights and window blinds.

Para mais informações, consulte RP-C Room Bus .

RP-C Modbus

The RP-C Modbus network allows standard Modbus devices and the KNX Modbus gateway (RP-C-EXT-KNX) to be connected to the controller.

Para mais informações, consulte RP-C Modbus .

RP-C Screw Terminals

The RP-C has fixed screw terminals for the power input, SSR outputs, relay outputs, high power relay outputs, and universal inputs/outputs.

Para mais informações, consulte RP-C Screw Terminals .

RP-C LEDs

There is one LED on the front panel of the RP-C.

Para mais informações, consulte RP-C LEDs .

RP Controller Reset Modes

You can reset and restart the RP controllers in different ways depending on how long you press the reset button. The resets and restarts can affect the retention of values after restart based on the retain levels configured for the variables.

Para mais informações, consulte RP Controller Reset Modes .

RP-C Device Installation

The RP-C can be installed on a DIN rail or flat surface.

Para mais informações, consulte RP-C Device Installation .

24 VAC Output on RP-C-16A Model

The RP-C-16A model has a 24 VAC (19 VA) Class 2 output that can be used to power external loads such as actuators, relays, or indicators. The external loads can be controlled using the controller's solid-state relay (SSR) or relay outputs.

Para mais informações, consulte 24 VAC Output on the RP-C-16A Controller .

Wiring

The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, BACnet/IP devices, and RP controller expansion modules, and Operator Display.

Para mais informações, consulte Wiring .

BACnet/IP Controller Device Firmware Management

Using WorkStation, you can update the firmware of multiple BACnet/IP devices and their attached SpaceLogic Sensor devices, RP controller expansion modules, and multi-sensors at the same time with minimum downtime. In particular, the universal upgrade package simplifies the update process and requires minimal user involvement and coordination.

Nota

SpaceLogic Sensor devices, RP controller expansion modules, and multi-sensors are supported by the RP controller.

Para mais informações, consulte BACnet/IP Device Firmware Management .

RP-C Regulatory Compliance and Approvals

This section provides information on regulatory compliance and approvals for the RP-C controllers.

Para mais informações, consulte RP-C Regulatory Compliance and Approvals .

Especificações

AC input
RP-C-12A, -12B, and -12C models
Nominal voltage
24 VAC
Operating voltage range
+/-15 %
Frequency
50/60 Hz
Maximum power consumption
23 VA
Power input protection
MOV suppression and internal fuse
RP-C-16A model
Nominal voltage
230 VAC
Operating voltage range
+/-10 %
Frequency
50/60 Hz
Maximum power consumption
65 VA
Power consumption without load
5 VA
Power input protection
MOV suppression and internal fuse
  
Separate PTC thermistor used as a resettable fuse for 24 VAC Out only
Overvoltage category
III
Pollution degree
2
DC input
RP-C-12A, -12B, and -12C models
Nominal voltage
24 to 30 VDC
Operating voltage range
23 to 33 VDC
Maximum power consumption
14 W
Power input protection
MOV suppression and internal fuse
AC output
RP-C-16A model
Type
Isolated Class 2 output
Nominal voltage
24 VAC
Frequency
Same frequency as the power supply (50/60 Hz)
Output power rating
19 VA
Environment
RP-C-12A, -12B, and -12C models
Ambient temperature, operating
0 to 50 °C (32 to 122 °F) at normal operation
  
-40 to +60 °C (-40 to +140 °F) for rooftop applications, horizontal installation only
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
RP-C-16A model
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94-5VB
Ingress protection rating
IP 20
Mechanical
Dimensions
180 W x 110 H x 64 D mm (7.1 W x 4.3 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight, RP-C-12A model
0.370 kg (0.816 lb)
Weight, RP-C-12B and -12C models
0.390 kg (0.860 lb)
Weight, RP-C-16A model
0.720 kg (1.587 lb)
Weight, optional covers
0.070 kg (0.154 lb)
Installation
DIN rail or flat surface
Terminal blocks
Fixed
Optional covers
Dimensions
181 W x 164 H x 64 D mm (7.1 W x 6.5 H x 2.5 D in.)
 
action_zoom_plus_stroke
Real-time clock
Accuracy, at 25 °C (77 °F)
+/-1 minute per month
Backup time, at 25 °C (77 °F)
7 days minimum
Communication ports
Ethernet
Dual 10/100BASE-TX (RJ45)
USB
1 USB 2.0 device port (mini-B)
  
1 USB 2.0 host port (type-A), 5 VDC, 2.5 W
RS-485 port “Sensor Bus” (Com A)
24 VDC, 2 W, RS-485 (RJ45)
  
Transient voltage suppressors on communication and power signals
RS-485 port “Room Bus” (Com B)
24 VDC, 3 W, RS-485 (RJ45)
  
Transient voltage suppressors on communication and power signals
Communications
BACnet
BACnet/IP, port configurable, default 47808
  
BTL B-AAC (BACnet Advanced Application Controller) a
a) See the BTL Product Catalog for up-to-date details on BTL listed firmware revisions on BACnet International's home page.
Wireless connectivity
Bluetooth Low Energy
Communication protocol
Bluetooth ® 5.0 Low Energy compliant
Frequency
2.402 to 2.480 GHz
Maximum output power
10 dBm
Maximum communication distance
Line-of-sight: 100 m (328 ft)
Antenna
Integrated antenna
RF connector for optional external antenna
SMA connector
External antenna (optional)
Restricted to the approved antenna type listed below (used in certification)

Manufacturer

Model (Part number)

Gain

Type

Impedance

Linx Technologies

ANT-2.4-WRT-MON-SMA

0.8 dBi

Monopole

50 ohm

CPU
Frequency
500 MHz
Type
ARM Cortex-A7 single-core
Internal SRAM
6 MB
NOR flash memory
32 MB
Memory backup
128 kB, FRAM, non-volatile

Internal Configuration

The RP-C internal configuration with regards to the signal ground is shown in the following figures.

 
action_zoom_plus_stroke RP-C-12A, -12B, and -12C models, internal configuration
Imagem: RP-C-12A, -12B, and -12C models, internal configuration
 
action_zoom_plus_stroke RP-C-16A model, internal configuration
Imagem: RP-C-16A model, internal configuration
  • Hardware Overview
  • RP-C Models
  • RP-C Onboard I/O
  • RP-C Built-in Power Supply
  • BACnet/IP Controller Device Memory
  • BACnet/IP controller Supported Building Standards
  • RP-C Wireless Connectivity
  • RP-C Communication Ports
  • RP-C Sensor Bus
  • RP-C Room Bus
  • RP-C Modbus
  • RP-C Screw Terminals
  • RP-C LEDs
  • RP Controller Reset Modes
  • RP-C Device Installation
  • 24 VAC Output on the RP-C-16A Controller
  • Wiring
  • BACnet/IP Device Firmware Management
  • RP-C Regulatory Compliance and Approvals