The RP-C-12A model has 12 I/O points and the controller is equipped with 23 fixed screw terminals.
Recommended screw tightening torque: 0.56 to 0.79 Nm (5 to 7 lbf.in)
The 23 screw terminals are used as follows:
Three screw terminals for the power input
Two screw terminals for the return (RET) terminals 4 and 5
Six screw terminals for the four solid-state relay (SSR) outputs
12 screw terminals for the eight universal inputs/outputs of type Ub
|
Terminal number |
Designation |
Usage |
|
Power input |
|
|
|
1 |
|
24 VAC, 50/60 Hz, 23 VA Positive lead (+) when operating the device from 24-30 VDC, 14 W |
|
2 |
|
Earth ground lead of 24 VAC transformer connects to terminal 2. Terminals 2 and 3 are internally connected. Negative (–) lead when operating the device from 24-30 VDC, 14 W |
|
3 |
RET
|
Terminal 3 is provided for convenience to connect to protective earth ground (optional). Terminals 2 and 3 are internally connected. |
|
Return terminals |
|
|
|
4 |
RET |
Internally connected to all earth ground and RET terminals |
|
5 |
RET |
Internally connected to all earth ground and RET terminals |
|
Solid-state relay (SSR) outputs |
|
|
|
6 |
DO1 |
SSR output |
|
7 |
COM1 |
Common connection for DO1 and DO2 The COM terminal can be connected to 0 to 24 VAC or -30 VDC to +30 VDC. |
|
8 |
DO2 |
SSR output |
|
9 |
DO3 |
SSR output |
|
10 |
COM2 |
Common connection for DO3 and DO4 The COM terminal can be connected to 0 to 24 VAC or -30 VDC to +30 VDC. |
|
11 |
DO4 |
SSR output |
|
Universal inputs/outputs |
|
|
|
19 |
Ub1 |
Universal input/output, type Ub |
|
20 |
RET |
Internally connected to all earth ground and RET terminals |
|
21 |
Ub2 |
Universal input/output, type Ub |
|
22 |
Ub3 |
Universal input/output, type Ub |
|
23 |
RET |
Internally connected to all earth ground and RET terminals |
|
24 |
Ub4 |
Universal input/output, type Ub |
|
25 |
Ub5 |
Universal input/output, type Ub |
|
26 |
RET |
Internally connected to all earth ground and RET terminals |
|
27 |
Ub6 |
Universal input/output, type Ub |
|
28 |
Ub7 |
Universal input/output, type Ub |
|
29 |
RET |
Internally connected to all earth ground and RET terminals |
|
30 |
Ub8 |
Universal input/output, type Ub |