0
Conceito

Conceito


Produtos: RP-C
Funcionalidades: Hardware
Versão do produto: 3.0, 3.1, 3.2, 3.3
18-03-2021

RP-C-12C Screw Terminals

The RP-C-12C model has 12 I/O points and the controller is equipped with 24 fixed screw terminals.

Perigo Perigo

HAZARD OF ELECTRIC SHOCK, EXPLOSION, OR ARC FLASH

Disconnect the power supply and other high voltage equipment before wiring.

Failure to follow these instructions will result in death or serious injury.

Recommended screw tightening torque: 0.56 to 0.79 Nm (5 to 7 lbf.in)

 
action_zoom_plus_stroke Screw terminals and other connectors, RP-C-12C model
Imagem: Screw terminals and other connectors, RP-C-12C model

The 24 screw terminals are used as follows:

  • Three screw terminals for the power input

  • Two screw terminals for the return (RET) terminals 4 and 5

  • Six screw terminals for the four solid-state relay (SSR) outputs

  • Four screw terminals for the three relay outputs

  • Three screw terminals for the high power relay output

  • Six screw terminals for the four universal inputs/outputs of type Ub

Tabela: Screw Terminals, RP-C-12C Model

Terminal number

Designation

Usage

Power input

1

 
action_zoom_plus_stroke
/+

24 VAC, 50/60 Hz, 23 VA

Positive lead (+) when operating the device from 24-30 VDC, 14 W

2

 
action_zoom_plus_stroke
/–

Earth ground lead of 24 VAC transformer connects to terminal 2.

Terminals 2 and 3 are internally connected.

Negative (–) lead when operating the device from 24-30 VDC, 14 W

3

RET

 
action_zoom_plus_stroke

Terminal 3 is provided for convenience to connect to protective earth ground (optional).

Terminals 2 and 3 are internally connected.

Return terminals

4

RET

Internally connected to all earth ground and RET terminals

5

RET

Internally connected to all earth ground and RET terminals

Solid-state relay (SSR) outputs

6

DO1

SSR output

7

COM1

Common connection for DO1 and DO2

The COM terminal can be connected to 0 to 24 VAC or -30 VDC to +30 VDC.

8

DO2

SSR output

9

DO3

SSR output

10

COM2

Common connection for DO3 and DO4

The COM terminal can be connected to 0 to 24 VAC or -30 VDC to +30 VDC.

11

DO4

SSR output

Relay outputs

12

COM3

Common connection for DO1, DO2, and DO3

13

DO1

Relay output, type Form A

14

DO2

Relay output, type Form A

15

DO3

Relay output, type Form A

High power relay outputs

16

NC

Normally Closed terminal. High power relay output, type Form C.

17

DO4

Common terminal. High power relay output, type Form C.

18

NO

Normally Open terminal. High power relay output, type Form C.

Universal inputs/outputs

19

Ub1

Universal input/output, type Ub

20

RET

Internally connected to all earth ground and RET terminals

21

Ub2

Universal input/output, type Ub

22

Ub3

Universal input/output, type Ub

23

RET

Internally connected to all earth ground and RET terminals

24

Ub4

Universal input/output, type Ub

  • RP-Cs