The main application of the high power relay output is to power an electrical heating element directly.
The outputs can be configured as one of the following types:
Digital output
Digital pulsed output
Pulse width modulated output
Consider the expected number of operation cycles specified for the relay output (cycle life rating) when configuring the period for a pulse width modulated (PWM) output point.
The DO high power relay outputs are Form C digital outputs, which means the outputs are switching contacts with one common terminal (C), one normally-open terminal (NO), and one normally-closed terminal (NC). The terminals are isolated from other circuits of the device and from signal ground.
Channels, RP-C-12A-F-24V
|
0
|
Channels, RP-C-12B-F-24V
|
1, DO4
|
Channels, RP-C-12C-F-24V
|
1, DO8
|
Channels, RP-C-16B-F-24V
|
1, DO8
|
Channels, RP-C-16A-F-230V
|
1, DO8
|
Channels, RP-C-16B-F-230V
|
1, DO8
|
Channels, RP-C-16C-F-230V
|
0
|
Channels, RP-C-12A-M-24V
|
0
|
Channels, RP-C-12B-M-24V
|
1, DO4
|
Channels, RP-C-16A-M-24V
|
1, DO8
|
Contact rating
|
Pilot Duty (B300)
|
Minimum current: 100 mA (5 VDC)
|
|
Normally Open contact, resistive load: 250 VAC/24 VDC, 12 A (cos phi = 1)
|
|
Normally Closed contact, inductive load: 250 VAC/24 VDC, 3 A (cos phi = 0.4)
|
|
Switch type
|
Form C Relay
|
Single Pole Double Throw
|
|
Normally Open and Normally Closed
|
|
Isolation contact to system ground
|
5,000 VAC
|
Cycle life
|
At least 100,000 cycles
|
Minimum pulse width
|
100 ms
|