IP-IO-UIO5DOFA4 Screw Terminals

IP-IO-UIO5DOFA4 has 9 I/O points and the IP-IO module is equipped with four pluggable terminal blocks and one fixed terminal block.

Recommended screw tightening torque: 0.56 Nm (5 lbf.in)

 
action_zoom_plus_stroke Screw terminals and other connectors, IP-IO-UIO5DOFA4
Figure : Screw terminals and other connectors, IP-IO-UIO5DOFA4

The terminal blocks are used as follows:

  • One 3-position pluggable terminal block for the power input

  • One 6-position pluggable terminal block for the three relay outputs

  • One 2-position fixed terminal block for the high power relay output

  • One 6-position plus one 2-position pluggable terminal blocks for the five universal inputs/outputs of type Ub

Table : Screw Terminals, IP-IO-UIO5DOFA4

Terminal number

Designation

Usage

Power input

1

24 VAC/DC

24 VAC, 50/60 Hz, 17 VA

Positive lead (+) when operating the device from 24-30 VDC, 9 W

2

 
action_zoom_plus_stroke
/ –

Earth ground lead of 24 VAC transformer connects to terminals 2 or 3.

Terminals 2 and 3 are internally connected.

Negative (–) lead when operating the device from 24-30 VDC, 9 W

3

 
action_zoom_plus_stroke

Terminal 3 is provided for convenience to connect to protective earth ground (optional).

Terminals 2 and 3 are internally connected.

Relay outputs

10

DO1

Relay output, type Form A

11

DO1

Relay output, type Form A

12

DO2

Relay output, type Form A

13

DO2

Relay output, type Form A

14

DO3

Relay output, type Form A

15

DO3

Relay output, type Form A

High power relay outputs

16

DO4

High power relay output, type Form A

17

DO4

High power relay output, type Form A

Universal inputs/outputs

18

Ub1

Universal input/output, type Ub

19

RET

Internally connected to all earth ground and RET terminals

20

Ub2

Universal input/output, type Ub

21

Ub3

Universal input/output, type Ub

22

RET

Internally connected to all earth ground and RET terminals

23

Ub4

Universal input/output, type Ub

24

Ub5

Universal input/output, type Ub

25

RET

Internally connected to all earth ground and RET terminals

  • IP-IO Modules