Powering Up an IP-IO Module

You perform the following steps to power up an IP-IO module.

显示更多
action_close

The IP-IO module device can be installed on a DIN rail or other flat surface inside a cabinet.

A DIN rail is a common and convenient technique for installing the IP-IO module along with other associated control and monitoring devices. The most efficient ventilation is achieved with the wall-mounted DIN rail oriented horizontally and with adequate space provided between the IP-IO module rail and adjacent rails or other panel-mounted devices.

The IP-IO module is typically installed horizontally (on a DIN rail going from left to right), with the device label text in the upright position reading left to right.

 
action_zoom_plus_stroke IP-IO module installed on a horizontal DIN rail
图: IP-IO module installed on a horizontal DIN rail

The restrictions on installing the device in other orientations differ depending on the operating conditions.

通知

CONTROLLER DEVICE DAMAGE

Follow the installation orientation restrictions that apply to the specific SmartX IP Controller device.

Failure to follow these instructions can result in equipment damage.

Under normal operating conditions of 0 to 50 °C (32 to 122 °F), the IP-IO module can be installed in the following orientations:

  • Horizontally (on a DIN rail going from left to right), with the device label text in the upright position reading left to right. See “a” in the following figure.

  • Vertically (on a DIN rail going from top to bottom), which means that the device is rotated +90 degrees or -90 degrees from the horizontal position. See “b” and “c” in the following figure.

Installing the IP-IO module rotated 180 degrees from the horizontal position with device label text up and down (“e” in the figure), face down from a ceiling (“d” in the figure), or face up on a horizontal surface (“f” in the figure) is not supported.

 
action_zoom_plus_stroke Installation orientation restrictions for the IP-IO module operated in normal conditions, 0 to 50 °C (32 to 122 °F)
图: Installation orientation restrictions for the IP-IO module operated in normal conditions, 0 to 50 °C (32 to 122 °F)

When the IP-IO module is used for rooftop applications, -40 to +60 °C (-40 to +140 °F), the device should be installed horizontally, with the device label text in the upright position reading left to right. See “a” in the following figure. Any other installation orientation (“b”, “c”, “d”, “e”, and “f” in the figure) may exceed the IP-IO module's thermal specifications, which can damage the module.

 
action_zoom_plus_stroke  Installation orientation restrictions for the IP-IO module operated at -40 to +60 °C (-40 to +140 °F)
图: Installation orientation restrictions for the IP-IO module operated at -40 to +60 °C (-40 to +140 °F)

The IP-IO module can be installed in a standard DIN enclosure.

When installing IP-IO modules in a cabinet, it is recommended to provide ample space between the DIN rails and modules for sufficient ventilation.

 
action_zoom_plus_stroke IP-IO modules installed on horizontal DIN rails in a cabinet
图: IP-IO modules installed on horizontal DIN rails in a cabinet

To help prevent the device from sliding down or sideways on the DIN rail, install an end clip for DIN 35 (part number SXWDINEND10001) tightly against the bottom or rightmost device on the rail. The end clip is easily removed if you bend the snap lock open with a screwdriver.

通知

Equipment damage

Use an end clip (part number SXWDINEND10001) when you install the device on a vertical DIN rail.

Failure to follow these instructions can result in equipment damage.

 
action_zoom_plus_stroke End clip for DIN 35 fixed across the DIN rail
图: End clip for DIN 35 fixed across the DIN rail

The IP-IO module is delivered with terminal blocks installed on the device.

The terminal blocks are removable. You can replace an IP-IO module in seconds because no terminal wiring is affected. The only exception is the high power relay output on the IP-IO-UIO5DOFA4 model, which uses a two-position fixed terminal block due to current requirements.

All IP-IO module models can be equipped with MP-C Display (part number SXWMPCDSP10001), which is an add-on module that enables manual override control of analog and digital outputs. The module consists of an LCD display and keys. The module is designed for permanent installation.

 
action_zoom_plus_stroke MP-C Display installed on an IP-IO module
图: MP-C Display installed on an IP-IO module

Do not try to remove the MP-C Display module as it may damage the enclosure and the module. Once installed, the MP-C Display module cannot be removed.

通知

CONTROLLER DEVICE DAMAGE

Do not try to remove the MP-C Display module.

Failure to follow these instructions can result in equipment damage.

显示更多
action_close

The IP-IO module has a built-in power supply designed to accommodate 24 VAC at 50/60 Hz or 24 to 30 VDC input power.

The built-in power supply is based on a half-wave rectified, non-isolated design, which is complemented with electronic protection components for transient protection, overload protection, and EMC compliance.

To power the IP-IO module, you can use a transformer or a DC power supply:

  • Class 2 (EN 60742) transformer supplying a nominal 24 VAC at 50/60 Hz

  • DC power supply supplying a nominal 24 to 30 VDC with the required output power

有关更多信息,请参阅 SmartX IP Controller - IP-IO Modules .

A separate, local 24 VAC step-down transformer is recommended to power each SmartX IP Controller device. The transformer with appropriate VA rating may also be used to power the locally connected I/O devices. The separate transformer helps to avoid problems with ground loops, 24 VAC induced EMI on LAN, low or distorted AC voltage level at the controller, and excess transformer load due to the half-wave power supply, which can result in intermittent equipment detected faults, loss of communications, or equipment damage.

通知

EQUIPMENT DAMAGE

Use a separate, local 24 VAC step-down transformer to power each SmartX IP Controller device.

Failure to follow these instructions can result in equipment damage.

通知

CONTROLLER DEVICE DAMAGE

Do not power the SmartX IP Controller device with a 24 VAC transformer that is used to power devices that contain non-isolated full-wave rectifier power supplies.

Failure to follow these instructions can result in equipment damage.

通知

EQUIPMENT DAMAGE

Use a separate, local 24 VAC step-down transformer to power each SmartX IP Controller device.

Failure to follow these instructions can result in equipment damage.

To power up an IP-IO module
  1. Check that all wiring is correct.

  2. Ensure that the 24 VAC at 50/60 Hz or 24-30 VDC power is supplied to terminals 1 and 2.

    通知

    The IP-IO module input power polarity and voltage level must be strictly observed. Failure to follow these instructions can result in equipment damage.

    通知

    Do not connect 230 VAC or 110 VAC to any terminal. Doing so will permanently damage the device.

     
    action_zoom_plus_stroke
  3. Ensure that the ground cable is connected to terminal number 3.

    通知

    Earth ground must be properly connected to avoid damage to the device and to ensure proper operation of the device.

  4. After powering up, check that the Status LED changes to a constant green light after about a minute.

  • IP-IO Module Device Installation
  • IP-IO Module Built-in Power Supply
  • Grounding and Power for Systems with IP-IO Modules
  • IP-IO Module Screw Terminals
  • IP-IO-DI10 Screw Terminals
  • IP-IO-UIO10 Screw Terminals
  • IP-IO-UIO5DOFA4 Screw Terminals
  • IP-IO Module LEDs
  • Status LEDs