The main application of the high power relay output is to power an electrical heating element directly.
The outputs can be configured as one of the following types:
Digital output
Digital pulsed output
Pulse width modulated output
Consider the expected number of operation cycles specified for the relay output (cycle life rating) when configuring the period for a pulse width modulated (PWM) output point.
The DO high power relay outputs are Form A digital outputs, which means the outputs are normally open contacts with one common terminal (C) and one normally open terminal (NO). The terminals are isolated from signal ground.
Channels, IP-IO-DI10
|
0
|
Channels, IP-IO-UIO10
|
0
|
Channels, IP-IO-UIO5DOFA4
|
1, DO4
|
Contact rating
|
250 VAC/24 VDC, 12 A, Pilot Duty (B300)
|
Switch type
|
Form A Relay
|
Single Pole Single Throw
|
|
Normally Open
|
|
Isolation contact to system ground
|
5000 VAC
|
Cycle life (Resistive load)
|
At least 100,000 cycles
|
Minimum pulse width
|
100 ms
|