The digital inputs can be used for sensing of multiple dry contact digital inputs in applications, such as equipment status monitoring or alarm point monitoring.
As counter inputs, digital inputs are commonly used in energy metering applications.
The DI digital inputs are designed to read two different types of inputs:
Digital
Counter
The external connection of a digital input is shown in the following figure.
K is the monitored external switch.
V S = 24 V
R PU = 10 kohm
A counter input uses the same hardware configuration as the digital input that is shown in the figure above.
Channels, IP-IO-DI10
|
10, DI1 to DI10
|
Channels, IP-IO-UIO10
|
0
|
Channels, IP-IO-UIO5DOFA4
|
0
|
Range
|
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
|
Absolute maximum ratings
|
-0.5 to +24 VDC
|
| Digital inputs | |
Range
|
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
|
Minimum pulse width
|
150 ms
|
| Counter inputs | |
Range
|
Dry contact switch closure or open collector/open drain, 24 VDC, typical wetting current 2.4 mA
|
Minimum pulse width
|
20 ms
|
Maximum frequency
|
25 Hz
|