earth_america
user_standard Iniciar sessão
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Conceito

Conceito


Produtos: RP-C, RP-C-EXT-KNX
Funcionalidades: Hardware
Versão do produto: 3.2, 3.3
26-02-2023

RP-C Modbus

The RP controller Modbus RTU (RS-485) subnetwork allows standard Modbus devices and the KNX Modbus gateway (RP-C-EXT-KNX) to be connected to the controller.

For the KNX Modbus gateway, the RP-C controller provides both 24 VDC power supply and communications through the Modbus network connection.

For standard Modbus devices, a separate power supply unit (PSU) is needed to power the Modbus devices on the network.

The Modbus RTU protocol is used for the communication. The RP-C controller acts the Modbus master and the connected devices act as slaves.

The Modbus communication parameters can be freely configured regardless of which RS-485 port on the RP-C controller that is used for the Modbus network. Para mais informações, consulte RP-C Communication Ports .

The maximum total length of the Modbus (RS-485) network is 72 m (236 ft). The Modbus network uses a Cat 5 (or higher) unshielded, straight-through wired cable with eight conductors (four twisted pairs) and RJ45 connectors. The wire size (cross-sectional area) should be 22 to 26 AWG (0.34 to 0.14 mm²). When the RP-C controller is installed in a space that handles conditioned air or return air, the Modbus network cables and IP network cables frequently must be plenum-rated to meet applicable building codes. Para mais informações, consulte Wiring .

Nota

LOSS OF COMMUNICATION

  • Ensure that the total length of the Modbus network does not exceed 72 m (236 ft).

  • Use a Cat 5 or higher unshielded twisted pair cable with eight conductors (four twisted pairs), a cross-sectional area of 22 to 26 AWG (0.34 to 0.14 mm 2 ), and a rating that meets the requirements of the target environment.

Failure to follow these instructions can result in loss of communication.

You need to configure which RS-485 (RJ45) port on the RP-C controller to use for the Modbus network. You can configure to use either the Sensor Bus port (RS-485 Com A) or Room Bus port (RS-485 Com B). Para mais informações, consulte RP-C Communication Ports .

 
action_zoom_plus_stroke Location of the Sensor Bus port (RS-485 Com A) and Room Bus port (RS-485 Com B) on the RP-C controllers
Imagem: Location of the Sensor Bus port (RS-485 Com A) and Room Bus port (RS-485 Com B) on the RP-C controllers

The maximum number of Modbus devices that can be connected to an RP-C controller depends on the type of Modbus device and the number of Modbus registers.

The maximum number of Modbus registers that can be connected to and managed by an RP-C controller depends on the communication capacity of the controller's Modbus network.

The RP-C Modbus network supports up to 10 connected Modbus devices with the following restrictions:

  • Maximum of one KNX Modbus gateway (RP-C-EXT-KNX)

  • Maximum of 250 Modbus registers per network

The RP controller Modbus network does not support 64-bit Modbus registers.

 
action_zoom_plus_stroke Examples with one KNX Modbus gateway and several standard Modbus devices connected to an RP-C controller in a daisy-chain configuration
Imagem: Examples with one KNX Modbus gateway and several standard Modbus devices connected to an RP-C controller in a daisy-chain configuration

The KNX Modbus gateway has the default Modbus address 1. The address can be configured through the ETS. Para mais informações, consulte Configuring the Modbus Device Settings in the KNX Modbus Gateway .

  • Hardware Overview
  • RP-Cs
  • Wiring
  • RP-C Communication Ports
  • RP-C
  • KNX Modbus Gateway RP-C-EXT-KNX
  • RP-C-EXT-KNX
  • Configuring the Modbus Device Settings in the KNX Modbus Gateway
  • ETS Database for the KNX Modbus Gateway