earth_america
user_standard Connexion
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Produits : RP-C
Fonctionnalités : Matériel
Version produit : 3.0, 3.1
31/07/2020

24 VAC Output on the RP-C-16A Controller

The RP-C-16A model has a 24 VAC (19 VA) output that can be used to power external loads such as actuators, relays, or indicators. The external loads can be controlled using the controller's solid-state relay (SSR) or relay outputs.

The RP-C-16A controller uses an internal transformer to convert 230 VAC from the power input (terminals 1 and 2) to 24 VAC (terminals 4 and 5). The transformer provides galvanic isolation between the 24 VAC output and the 230 VAC power input as well as the controller electronics.

 
action_zoom_plus_stroke 24 VAC isolated output
Figure : 24 VAC isolated output

The following wiring example shows how an actuator can be connected to the controller's 24 VAC output and one of the SSR outputs. The example also shows how the 24 VAC output terminals 4 and 5 are connected to terminals G0 and G on a transmitter, for which the terminal M is connected to one of the RET terminals of the controller's Universal Inputs/Outputs. G0 and M of the transmitter may be interconnected internally or by a separate wire, which can introduce disturbances. Sometimes there is only one common ground connection G0/M, and this node must be connected to one of the 24 VAC output terminals and to a RET terminal. In the example below, the transmitter can be replaced by a voltage controlled actuator.

 
action_zoom_plus_stroke 24 VAC output, wiring example
Figure : 24 VAC output, wiring example

The polarity of the 24 VAC output terminals 4 and 5 is unknown, which means that the phase of the output relative to the input of the transformer is also unknown. For example, if you interconnect terminals 4 of two different controllers, a phase difference can result in a voltage difference of 0 VAC to 48 VAC between terminals 5 of the controllers. The primary side of the transformer has a PTC thermistor, which acts as a resettable fuse and turns off the voltage to the transformer in case of over current on the secondary side. However, the PTC thermistor does not provide any protection for external equipment from being exposed to 48 VAC.

Déclaration

EQUIPMENT DAMAGE

Never connect the controller’s 24 VAC output in parallel with another controller.

Failure to follow these instructions can result in equipment damage.

  • Hardware Overview
  • RP-Cs