earth_america
user_standard Connexion
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Produits : RP-C
Fonctionnalités : Matériel
Version produit : 3.1
23/03/2020

RP-Cs

SmartX IP Controller – RP-C is a room-purpose, fully programmable, IP based field controller. The RP-C models offer a flexible mix of I/O point types that suit a wide range of HVAC applications. The controller can either be used as a standalone BACnet/IP field controller or as part of an EcoStruxure BMS with a SmartX AS-P or AS-B server or an Enterprise Server as the parent server. The RP-C features a wireless chip that allows a mobile device running the eCommission SmartX Controllers mobile application to connect directly to the controller.

The RP-C allows for flexible control solutions due to the dual Ethernet ports, the interface to SmartX Sensors, the interface for support of Connected Room Solution (CRS) devices, and the versatile mix of universal inputs/outputs, solid-state relay (SSR) outputs, relay outputs, and high power relay outputs.

When RP-Cs are part of an EcoStruxure BMS, you can take full advantage of the existing EcoStruxure Building Operation engineering tools.

 
action_zoom_plus_stroke RP-C
Figure : RP-C

RP-C Models

The RP-C comes in four different models, which offer four different sets of I/O point types, named 12A, 12B, 12C, and 16A.

Pour plus d'informations, voir RP-C Models .

RP-C Onboard I/O

The RP-C-12A, -12B, -12C, and -16A models provide 12 or 16 I/O points, consisting of four different sets of I/O point types. The versatile mix of I/O point types match a wide variety of applications. The universal inputs/outputs are highly flexible and can be configured as either inputs or outputs.

Pour plus d'informations, voir RP-C Onboard I/O .

RP-C Built-in Power Supply

The RP-C-12A, -12B, and -12C models have a built-in power supply designed to accommodate a nominal operating voltage of 24 VAC at 50/60 Hz or 24 to 30 VDC input power. The RP-C-16A model's power supply is designed for a nominal operating voltage of 230 VAC at 50/60 Hz.

Pour plus d'informations, voir RP-C Built-in Power Supply .

SmartX IP Controller Device Memory

SmartX IP Controller devices have three types of memory:

  • Flash memory: for boot loader, operating system, application software, and configuration storage

  • RAM: for runtime operation

  • FRAM non-volatile memory: for data retention in the case of power outage

Pour plus d'informations, voir SmartX IP Controller Device Memory .

SmartX IP Controller Supported Building Standards

One of the cornerstones of the EcoStruxure BMS is support for open standards. As a result, the SmartX IP controller complies with the BACnet open standard, one of the most popular standards for buildings.

Pour plus d'informations, voir SmartX IP Controller Supported Building Standards .

RP-C Wireless Connectivity

RP-C is a Bluetooth Low Energy (BLE) enabled product. You can use this wireless connectivity option for connecting a smartphone or tablet running the eCommission SmartX Controllers mobile application to the RP-C.

Pour plus d'informations, voir RP-C Wireless Connectivity .

RP-C Communication Ports

The RP-C contains a combination of Ethernet, USB, SmartX Sensor, and Connected Room Solution communication ports.

Pour plus d'informations, voir RP-C Communication Ports .

SmartX IP Controller Sensor Bus

The SmartX IP controller provides a sensor bus, which allows SmartX Sensors to be connected to the controller.

Pour plus d'informations, voir SmartX IP Controller Sensor Bus .

RP-C Room Bus

The RP-C provides a room bus, which allows RP Series expansion modules and multi-sensors to be connected to the controller for motion detection, luminosity measurements, and control of electric lights and window blinds.

Pour plus d'informations, voir RP-C Room Bus .

RP-C Screw Terminals

The RP-C has fixed screw terminals for the power input, SSR outputs, relay outputs, high power relay outputs, and universal inputs/outputs.

Pour plus d'informations, voir RP-C Screw Terminals .

RP-C LEDs

There is one LED on the front panel of the RP-C.

Pour plus d'informations, voir RP-C LEDs .

RP Series Controller Reset Modes

You can reset and restart the RP Series controllers in different ways depending on how long you press the reset button. The resets and restarts can affect the retention of values after restart based on the retain levels configured for the variables.

Pour plus d'informations, voir RP Series Controller Reset Modes .

RP-C Device Installation

The RP-C can be installed on a DIN rail or flat surface.

Pour plus d'informations, voir RP-C Device Installation .

24 VAC Output on RP-C-16A Model

The RP-C-16A model has a 24 VAC (19 VA) output that can be used to power external loads such as actuators, relays, or indicators. The external loads can be controlled using the controller's solid-state relay (SSR) or relay outputs.

Pour plus d'informations, voir 24 VAC Output on the RP-C-16A Controller .

Wiring

The wiring recommendations provide guidance regarding wiring of the I/O modules, SmartX servers, SmartX IP Controller devices, and RP Series expansion modules and multi-sensors.

Pour plus d'informations, voir Wiring .

SmartX IP Controller Device Firmware Management

Using WorkStation, you can update the firmware of multiple SmartX IP Controller devices and their attached SmartX Sensors, RP Series expansion modules, and multi-sensors at the same time with minimum downtime. In particular, the universal upgrade package simplifies the update process and requires minimal user involvement and coordination.

Déclaration

SmartX Sensors, RP Series expansion modules, and multi-sensors are supported by the SmartX IP Controller - RP Series.

Pour plus d'informations, voir SmartX IP Controller Device Firmware Management .

RP-C Regulatory Compliance and Approvals

This section provides information on regulatory compliance and approvals for the RP-C controllers.

Pour plus d'informations, voir RP-C Regulatory Compliance and Approvals .

Spécifications

AC input
RP-C-12A, -12B, and -12C models
Nominal voltage
24 VAC
Operating voltage range
+/-15 %
Frequency
50/60 Hz
Maximum power consumption
23 VA
Power input protection
MOV suppression and internal fuse
RP-C-16A model
Nominal voltage
230 VAC
Operating voltage range
+/-10 %
Frequency
50/60 Hz
Maximum power consumption
65 VA
Power consumption without load
5 VA
Power input protection
MOV suppression and internal fuse
  
Separate PTC thermistor used as a resettable fuse for 24 VAC Out only
Overvoltage category
III
Pollution degree
2
DC input
RP-C-12A, -12B, and -12C models
Nominal voltage
24 to 30 VDC
Operating voltage range
23 to 33 VDC
Maximum power consumption
14 W
Power input protection
MOV suppression and internal fuse
AC output
RP-C-16A model
Type
Isolated output
Nominal voltage
24 VAC
Frequency
Same frequency as the power supply (50/60 Hz)
Output power rating
19 VA
Environment
RP-C-12A, -12B, and -12C models
Ambient temperature, operating
0 to 50 °C (32 to 122 °F) at normal operation
  
-40 to +60 °C (-40 to +140 °F) for rooftop applications, horizontal installation only
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
RP-C-16A model
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Maximum humidity
95 % RH non-condensing
Material
Plastic flame rating
UL94-5VB
Ingress protection rating
IP 20
Mechanical
Dimensions
180 W x 110 H x 64 D mm (7.1 W x 4.3 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight, RP-C-12A model
0.370 kg (0.816 lb)
Weight, RP-C-12B and -12C models
0.390 kg (0.860 lb)
Weight, RP-C-16A model
0.720 kg (1.587 lb)
Weight, optional covers
0.070 kg (0.154 lb)
Installation
DIN rail or flat surface
Terminal blocks
Fixed
Optional covers
Dimensions
181 W x 164 H x 64 D mm (7.1 W x 6.5 H x 2.5 D in.)
 
action_zoom_plus_stroke
Real-time clock
Accuracy, at 25 °C (77 °F)
+/-1 minute per month
Backup time, at 25 °C (77 °F)
7 days minimum
Communication ports
Ethernet
Dual 10/100BASE-TX (RJ45)
USB
1 USB 2.0 device port (mini-B)
  
1 USB 2.0 host port (type-A), 5 VDC, 2.5 W
Sensor bus
24 VDC, 2 W, RS-485 (RJ45)
Sensor bus protection
Transient voltage suppressors on communication and power signals
Room bus
24 VDC, 3 W, RS-485 (RJ45)
Room bus protection
Transient voltage suppressors on communication and power signals
Communications
BACnet
BACnet/IP, port configurable, default 47808
  
BTL B-AAC (BACnet Advanced Application Controller) a
a) See the BTL Product Catalog for up-to-date details on BTL listed firmware revisions on BACnet International's home page.
Wireless connectivity
Bluetooth Low Energy
Communication protocol
Bluetooth ® 5.0 Low Energy compliant
Frequency
2.402 to 2.480 GHz
Maximum output power
10 dBm
Maximum communication distance
Line-of-sight: 100 m (328 ft)
Antenna
Integrated antenna
RF connector for optional external antenna
SMA connector
External antenna (optional)
Restricted to the approved antenna type listed below (used in certification)

Manufacturer

Model (Part number)

Gain

Type

Impedance

Linx Technologies

ANT-2.4-WRT-MON-SMA

0.8 dBi

Monopole

50 ohm

CPU
Frequency
500 MHz
Type
ARM Cortex-A7 single-core
Internal SRAM
6 MB
NOR flash memory
32 MB
Memory backup
128 kB, FRAM, non-volatile

Internal Configuration

The RP-C internal configuration with regards to the signal ground is shown in the following figures.

 
action_zoom_plus_stroke RP-C-12A, -12B, and -12C models, internal configuration
Figure : RP-C-12A, -12B, and -12C models, internal configuration
 
action_zoom_plus_stroke RP-C-16A model, internal configuration
Figure : RP-C-16A model, internal configuration
  • Hardware Overview
  • RP-C Models
  • RP-C Onboard I/O
  • RP-C Built-in Power Supply
  • SmartX IP Controller Device Memory
  • SmartX IP Controller Supported Building Standards
  • RP-C Wireless Connectivity
  • RP-C Communication Ports
  • SmartX IP Controller Sensor Bus
  • RP-C Room Bus
  • RP-C Screw Terminals
  • RP-C LEDs
  • RP Series Controller Reset Modes
  • RP-C Device Installation
  • 24 VAC Output on the RP-C-16A Controller
  • Wiring
  • SmartX IP Controller Device Firmware Management
  • RP-C Regulatory Compliance and Approvals