earth_america
user_standard 登录
action_search_stroke
earth_america
登录以评价并提供反馈 1 2 3 4 5 登录以评价
0
概念

概念


产品: RP-C
功能: 硬件
产品版本: 2023, 2024, 7.0
2023/5/25

Grounding and Power for Systems with RP-C 230 V Controller Models

This section provides grounding and power recommendations for system configurations with the RP-C controller models that support 230 VAC input power.

This applies to the following RP-C 230 V controller models:

  • RP-C-16A-F-230V and RP-C-16B-F-230V

危险 危险

HAZARD OF ELECTRIC SHOCK, EXPLOSION, OR ARC FLASH

Never connect the 24 VAC supply output terminals 4 and 5 to any other power supply output, regardless of polarity.

Failure to follow these instructions will result in death or serious injury.

注释:

The grounding and power recommendations for RP-C-16C-F-230V differ from the other RP-C 230 V controller models. 有关更多信息,请参阅 Grounding and Power for Systems with RP-C-16C-F-230V and External 24 VAC/VDC Power Supply .

Use the following recommendations to design a good working system:

  • Select any of terminals 4 or 5 to be used as G0 (Power Ground/Common).

    Any of terminals 4 or 5 becomes G0 as long as it is connected to RET in some way.

  • G0 (terminal 4 or 5) can be connected to RET. Avoid this if not necessary.

  • G0 and/or RET can be connected to protective earth ground (PE). Avoiding this connection is preferable, as it can cause circulating ground currents.

  • Do not connect RET to terminal 3 as the creepage distance must be at least 5.5 mm from mains voltage to RET.

    If the incoming PE becomes loose, the required creepage distance between terminal 2 (N) and SELV may be violated.

  • The fuse (circuit breaker) F11 must be rated 3 A or higher.

  • Signal Ground Rail (SGR) is not needed.

注释:

The polarity of the 24 VAC output terminals 4 and 5 is unknown. 有关更多信息,请参阅 24 VAC Output on RP-C 230 V Controller Models .

Use the recommendations in the following subsections for interconnecting several RP-C 230 V controller models. 有关更多信息,请参阅 RP-C Models .

For the RP-C-16A-F-230V controller model, the recommendations differ depending on the hardware version of the controller. This is because terminal 3 differs between different hardware versions of that controller model. 有关更多信息,请参阅 Differences Between RP-C Hardware Versions .

提示:

The hardware version is shown on the label on the side of the device. If the side of the device is not accessible, the text on the front can be used to identify the hardware version. For example, “SpaceLogic RP-C” is displayed on devices of hardware version 10 and later, while “SmartX IP Controller” is printed on devices of hardware version 9 and earlier.

Interconnecting RP-C 230 V controller models

When interconnecting several RP-C 230 V controller models:

  • Avoid interconnection of local grounds (G0/RET) for different RP-Cs by using non-shielded Ethernet network cables. Avoid shielded Ethernet network cables. Also, do not connect G0/RET from one RP-C with G0/RET of a different RP-C.

通知

EQUIPMENT DAMAGE

Do not connect signal ground (RET terminals, USB shield, Ethernet network shield, or antenna shield) between RP-C controllers.

Failure to follow these instructions can result in equipment damage.

It is important to know that several nodes are internally interconnected to the common signal ground. This is important to help avoid ground loops and incorrect supply of G0. The following nodes are all interconnected:

  • All RET terminals (20, 23, 26, and 29)

  • Antenna connector

  • USB connector shields

  • Ethernet network connector shields

  • RS-485 (Room bus and Sensor bus) ground reference

Terminal 3 (PE) is connected to RET through a positive temperature coefficient (PTC) thermistor.

 
action_zoom_plus_stroke System configuration with RP-C 230 V controller model (RP-C-16A-F-230V controller of hardware version 10 and later)
图: System configuration with RP-C 230 V controller model (RP-C-16A-F-230V controller of hardware version 10 and later)
Interconnecting RP-C-16A-F-230V controllers of hardware version 9 and earlier

When interconnecting several RP-C-16A-F-230V controllers of hardware version 9 and earlier:

  • Avoid interconnection of local grounds (G0/RET) for different RP-Cs by using non-shielded Ethernet network cables. Avoid shielded Ethernet network cables. Also, do not connect G0/RET from one RP-C with G0/RET of a different RP-C.

  • If the local grounds (G0/RET) of different RP-Cs are interconnected, every RP-C with local ground connection to another device must be grounded to PE.

    It is necessary to connect RET to PE because the RP-C is supplied from mains voltage and a small touch current (<0.2 mA) is generated by the RP-C's internal AC/DC converter. If several RP-Cs are interconnected, the sum of all touch currents can be high, making it dangerous to touch parts such as the antenna or other parts connected to the internal ground.

  • Do not use terminal 3 as convenience terminal. Connect RET directly to PE.

    The reason is that the creepage distance between terminals 2 (N) and 3 is too small if PE becomes disconnected from terminal 3.

警告 警告

HAZARD OF ELECTRIC SHOCK

Do not connect signal ground (RET terminals, USB shield, Ethernet network shield, or antenna shield) between RP-C controllers without connecting at least one of the RET terminals to protective earth ground.

Failure to follow these instructions can result in death, serious injury, or equipment damage.

It is important to know that several nodes are internally interconnected to the common signal ground. This is important for safety reasons and to help avoid ground loops and incorrect supply of G0. The following nodes are all interconnected:

  • All RET terminals (20, 23, 26, and 29)

  • Antenna connector

  • USB connector shields

  • Ethernet network connector shields

  • RS-485 (Room bus and Sensor bus) ground reference

 
action_zoom_plus_stroke System configuration with RP-C-16A-F-230V controller of hardware version 9 and earlier
图: System configuration with RP-C-16A-F-230V controller of hardware version 9 and earlier
  • I/O Wiring
  • Grounding and Power
  • RP-C Controllers
  • Grounding and Power for Systems with RP-C-16C-F-230V and External 24 VAC/VDC Power Supply
  • Grounding and Power for Systems with RP-C 24 V Controller Models with Half-wave Rectified and Non-isolated Built-in Power Supply
  • Grounding and Power for Systems with RP-C 24 V Controller Models with Full-wave Rectified and Isolated Built-in Power Supply
  • RP-C Models
  • Differences Between RP-C Hardware Versions
  • 24 VAC Output on RP-C 230 V Controller Models