SpaceLogic* Wireless Adapter - Advanced is a USB-based wireless adapter that enables Zigbee TM wireless connectivity for your SpaceLogic BACnet/IP controller or automation server, extending its point count and bringing flexibility in your retrofit applications. The adapter can be used with BACnet/IP controllers such as the RP controllers as well as automation servers such as the AS-P and AS-B servers.
An automation server equipped with the adapter can communicate over the Zigbee wireless protocol with up to 164 wireless devices, depending on the type of Zigbee device and the radio bandwidth usage of the device. An RP controller equipped with the adapter can communicate with up to 30 wireless devices.
For information on the supported wireless devices, see section “Supported Wireless Devices”.
The adapter works seamlessly within EcoStruxure Building Management systems so that Zigbee objects become easily available to the user.
The adapter’s compact design allows it to plug in to RP controllers or automation servers in tight spaces and the optional mounting cradle, wall plate, and USB cable extension allow for the choice of a wall, ceiling, or exterior of the enclosure mount to maximize the transmission and reception of signals from distributed Zigbee devices.
In WorkStation, the firmware of the adapter will be automatically updated when you update the RP controller or automation server to which it is connected.
* Formerly known as SmartX.
The adapter has the following features:
Zigbee Certified Product (with RP controllers, AS-P and AS-B servers)
Zigbee 3.0
Compact design and easy to install
Multiple mounting options
Integrated 2.4 GHz antenna
Wireless communication distance:
Line-of-sight range: Up to 50 m (164 ft)
Configuration and firmware update through EcoStruxure Building Operation software
|
Product |
Part number |
|
SpaceLogic Wireless Adapter - Advanced
|
SXWZBAUSB10001
|
|
USB Adapter Cradle Kit Includes plastic mounting cradle and wall plate |
SXWUSBCRA10001
|
|
USB Extension Cable 1 m (3 ft) Includes USB extension cable of length 1 m (3 ft) |
SXWUSBCBL10001
|
|
Plenum Rated USB Extension Cable 3 m (10 ft) Includes plenum rated USB extension cable of length 3 m (10 ft) |
SXWUSBCBL10002
|
| Electrical | |
DC input supply voltage
|
5 VDC (USB)
a
|
| a) Connected to and powered by the USB 2.0 host port on the RP controller or automation server. | |
Maximum power consumption
|
0.3 W
|
| Wireless connectivity | |
Communication protocol
|
Zigbee 3.0
|
Frequency band
|
2.4 GHz (ISM band), compliant with IEEE Standard 802.15.4
|
Maximum output power
|
+10 dBm
|
Maximum communication distance
|
Line-of-sight: 50 m (164 ft)
|
Antenna
|
Integrated antenna
|
Maximum total number of hops allowed in the wireless network
|
5
|
| Wireless device limits for an RP controller | |
Maximum total number of wireless devices connected to the wireless network
|
Up to 30
a
|
| a) The maximum number depends on the type of Zigbee device and the radio bandwidth usage of the Zigbee device. | |
Maximum total number of SE8000 and VT8000 room controllers
|
4
|
Maximum total number of Zigbee end devices paired with an RP controller
|
20
|
Maximum total number of ASSA ABLOY VingCard electronic locks
|
1
|
| Wireless device limits for an automation server | |
Maximum total number of wireless devices connected to the wireless network
|
Up to 164
a
|
| a) The maximum number depends on the type of Zigbee device and the radio bandwidth usage of the Zigbee device. | |
Maximum total number of Zigbee routers and Zigbee end devices
|
64
|
Maximum total number of Zigbee Green Power devices
|
100
|
Maximum total number of Zigbee end devices paired with an automation server
|
20
|
| Environment | |
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
Ambient temperature, storage
|
-40 to +70 °C (-40 to +158 °F)
|
Humidity
|
Maximum 95 % RH non-condensing
|
| Material | |
Plastic flame rating
|
UL94 HB
|
Plenum rating
|
UL 2043
|
Ingress protection rating
|
IP 20
|
| Mechanical | |
Dimensions, adapter
|
See drawing below
|
|
|
Dimensions, mounting cradle and wall plate
|
See drawing below
|
|
|
Weight
|
Adapter: 7.57 g (0.267 oz)
|
Cradle and nut: 21.35 g (0.753 oz)
|
|
Cradle, nut, and wall plate: 33.40 g (1.178 oz)
|
|
Installation
|
Connection to USB host port on RP controller or automation server
|
Indoor use only
|
|
Installation options
|
Enclosure exterior
|
Drop ceiling with mounting cradle (optional)
|
|
Wall with wall plate (optional)
|
|
Maximum USB 2.0 cable length
|
3 m (10 ft)
|
| Software requirements | |
EcoStruxure Building Operation software
|
version 3.2 and later
|
EcoStruxure Building Commission mobile application software
|
version 4.0 and later
|
RP-C controller firmware
|
version 3.02.xx or higher
|
AS-P server firmware
|
EcoStruxure Building Operation software version 3.2 and later
|
AS-B server firmware
|
EcoStruxure Building Operation software version 3.3 and later
|
| Agency compliances | |
EMC
|
EN 301 489-1 V2.2.3; EN 301 489-17 V3.2.2; BS/EN 55032:2015; BS/EN 55035:2017; FCC Part 15, Sub-part C, Class B; ICES-003, Class B
|
Radio
|
ETSI EN 300 328 V2.2.2
|
Safety standards
|
BS/EN 62368-1:2014; BS/EN 62311:2008; BS/EN 62479:2010
|
FCC ID
|
QOQ13
|
ISED certification number
|
IC: 5123A-13
|
| Hardware | |
CPU type
|
ARM Cortex-M4 with Floating Point Unit (FPU)
|
Frequency
|
38.4 MHz
|
SRAM (embedded)
|
64 KB
|
Flash memory (embedded)
|
512 KB
|
Connectors
|
USB 2.0, type-A connector
|
This section provides information on the wireless devices that are supported by the wireless network.
The import files for supported wireless devices can be found in the Schneider Electric BMS Applications web portal ( bms-applications.schneider-electric.com ).
In EcoStruxure Building Operation software version 4.0 and later, additional Zigbee 3.0 wireless devices can be supported using the Zigbee Wireless Device Support Service. For information on how support for Zigbee 3.0 devices can be added in the EcoStruxure Building Operation software through this service, see PA-00842.
The SE8000 and VT8000 controllers can be used for fan coil, roof top unit, heat pump, indoor air quality, and VAV control applications.
The SE8000 and VT8000 controllers without built-in wireless networking capability require the VCM8000V5045P Zigbee extended profile wireless communication adapter to be installed to enable Zigbee wireless connectivity.
The following conditions apply to the support of SE8000 and VT8000 controllers under an automation server Zigbee wireless network:
In EcoStruxure Building Operation software version 3.3, when you connect an SE8000 or VT8000 controller via Zigbee wireless network to the automation server, you are not able to connect Zigbee devices to the SE8000 or VT8000 controller. If you already have Zigbee devices connected to the SE8000 or VT8000 controllers in the Zigbee network, you must either re-connect them to the automation server or upgrade to EcoStruxure Building Operation software version 4.0.
When you connect SE8000 and VT8000 controllers via Zigbee wireless network to the automation server, you are not able to use multiple SE8000 or VT8000 controllers as sensors to control a single setpoint in a single zone.
The following conditions apply to the support of SE8000 and VT8000 controllers under an RP controller Zigbee wireless network:
In EcoStruxure Building Operation software version 3.3 and version 4.0, when you connect an SE8000 or VT8000 controller via Zigbee wireless network to the RP controller, you are not able to connect Zigbee devices to the SE8000 or VT8000 controller. If you already have Zigbee devices connected to the SE8000 or VT8000 controllers in the Zigbee network, you must re-connect them to the RP controller.
Support for SE8000 and VT8000 controllers under the RP controller Zigbee wireless network is limited to display and sensor functionality. Under the RP controller Zigbee network, they are not supported as HVAC controllers.
When you connect SE8000 and VT8000 controllers via Zigbee wireless network to the RP controller, you are not able to use multiple SE8000 or VT8000 controllers as sensors to control a single setpoint in a single zone.
|
Product |
Part number |
|
Low-Voltage Fan Coil Room & Zone Controller, RH sensor & control |
SE8350U0Bxx a |
|
Low-Voltage Fan Coil Room & Zone Controller, RH sensor & control, PIR motion sensor |
SE8350U5Bxx a |
|
Low-Voltage Fan Coil Room & Zone Controller, ZigBee Embedded, RH sensor, PIR motion sensor |
SE8350U5BxxP a |
|
Roof Top Unit, Heat Pump & Indoor Air Quality Controller, RH sensor & control |
SE8650U0Bxx a |
|
Roof Top Unit, Heat Pump & Indoor Air Quality Controller, RH sensor & control, PIR motion sensor |
SE8650U5Bxx a |
|
Roof Top Unit, Heat Pump & Indoor Air Quality Controller, ZigBee Embedded, RH sensor & control, PIR motion sensor |
SE8650U5BxxP a |
|
Line-Voltage Fan Coil Room Controller, RH sensor & control |
SER8350A0Bxx a |
|
Line-Voltage Fan Coil Room Controller, RH sensor & control, PIR motion sensor |
SER8350A5Bxx a |
|
Line-Voltage Fan Coil Room Controller, ZigBee Embedded, RH sensor & control, PIR motion sensor |
SER8350A5BxxP a |
|
Variable Air Volume Controller, PD/PI, RH sensor & control |
SEZ8250U0Bxx a |
|
Variable Air Volume Controller, PD/PI, RH sensor & control, PIR motion sensor |
SEZ8250U5Bxx a |
|
Variable Air Volume Controller, PD/PI, Embedded ZigBee Pro, RH sensor & control, PIR motion sensor |
SEZ8250U5BxxP a |
|
Low-Voltage Fan Coil Room Controller, White Case, White Fascia |
VT8350U5x00B b |
|
Low-Voltage Fan Coil Room Controller, Embedded ZigBee Pro, RH sensor & control, PIR motion sensor, White Case, White Fascia |
VT8350U5500BP |
|
Roof Top Unit, Heat Pump & Indoor Air Quality Controller, White Case, White Fascia |
VT8650U5x00B b |
|
Roof Top Unit, Heat Pump & Indoor Air Quality Controller, Embedded ZigBee Pro, RH sensor & control, PIR Motion Sensor, White Case, White Fascia |
VT8650U5500BP |
|
Fan Coil Room Controller, White Case, White Fascia |
VTR8350A5x00B b |
|
Fan Coil Room Controller, Embedded ZigBee Pro, RH sensor & control, PIR Motion Sensor, White Case, White Fascia |
VTR8350A5500BP |
|
Variable Air Volume Controller, PD/PI, White Case, White Fascia |
VZ8250U5x00B b |
|
Variable Air Volume Controller, PD/PI, Embedded ZigBee Pro, RH sensor & control, PIR motion sensor, White Case, White Fascia |
VZ8250U5500BP |
The wireless sensors can be used for indoor air quality, motion and occupancy, window and door status, and water leakage monitoring.
|
Product |
Part number |
|
CO2 with Temperature and Humidity Sensor |
SED-CO2-G-5045 |
|
Temperature and Humidity Sensor |
SED-TRH-G-5045 |
|
Window/Door Contact Sensor |
SED-WDC-G-5045 |
|
Motion with Temperature and Humidity Sensor |
SED-MTH-G-5045 |
|
Water Leak Sensor |
SED-WLS-G-5045 |
The RP controller expansion Zigbee modules can be used for lighting control applications.
|
Product |
Part number |
|
RP-C-EXT-ZB-0-10V, Zigbee 0-10V module (230 VAC) |
SXWREZB010110001 |
|
RP-C-EXT-ZB-DALI, Zigbee DALI module (230 VAC) |
SXWREZBDALI110001 |
The TH900 Series thermostats can be used for packaged terminal air conditioner (PTAC), fan coil, heat pump, and gas and oil furnace control applications. The TH900 Series thermostats are only supported for the automation servers.
|
Product |
Part number |
|
TH903 Thermostat, LCD/Buttons, Zigbee, Occupancy Sensor, Auxiliary Input, White |
TH903-ZP-W |
|
TH903 Thermostat, LCD/Buttons, Zigbee, Occupancy Sensor, Modbus, Auxiliary Input, White |
TH903-ZPM-W |
|
TH907 Thermostat, Touchscreen, Zigbee, Occupancy Sensor, Auxiliary Input, White |
TH907-ZP-W |
|
TH907 Thermostat, Touchscreen, Zigbee, Occupancy Sensor, Modbus, Auxiliary Input, White |
TH907-ZPM-W |
|
TH907 Thermostat, Touchscreen, Zigbee, Occupancy Sensor, Auxiliary Input, Black |
TH907-ZP-B a |
|
TH907 Thermostat, Touchscreen, Zigbee, Occupancy Sensor, Modbus, Auxiliary Input, Black |
TH907-ZPM-B a |
The PowerTag energy sensors can be used for energy metering and monitoring, load monitoring and power availability for products and installations rated up to 2000 A.
PowerTag firmware version 004.000.424 or later is required for support in the EcoStruxure Building Operation software.
|
Product |
Part number |
|
PowerTag Energy M63 1P+Wire |
A9MEM1520 |
|
PowerTag Energy M63 1P+N TOP |
A9MEM1521 |
|
PowerTag Energy M63 1P+N BOTTOM |
A9MEM1522 |
|
PowerTag Energy M63 3P |
A9MEM1540 |
|
PowerTag Energy M63 3P+N TOP |
A9MEM1541 |
|
PowerTag Energy M63 3P+N BOTTOM |
A9MEM1542 |
|
PowerTag Energy M63 3P 230V LL |
A9MEM1543 |
|
PowerTag Energy P63 1P+N TOP |
A9MEM1561 |
|
PowerTag Energy P63 1P+N BOTTOM |
A9MEM1562 |
|
Powertag Energy P63 1P+N BOTTOM RCBO 18mm |
A9MEM1563 |
|
PowerTag Energy P63 3P+N TOP |
A9MEM1571 |
|
PowerTag Energy P63 3P+N BOTTOM |
A9MEM1572 |
|
PowerTag Energy F63 1P+N |
A9MEM1560 |
|
PowerTag Energy F63 1P+N 110V LL |
A9MEM1564 |
|
PowerTag Energy F63 3P+N |
A9MEM1570 |
|
PowerTag Energy F63 3P |
A9MEM1573 |
|
Powertag Energy F63 3P+N 127V/220V |
A9MEM1574 |
|
PowerTag Energy F160 3P/3P+N |
A9MEM1580 |
|
PowerTag Energy M250 3P |
LV434020 |
|
PowerTag Energy M250 3P+N |
LV434021 |
|
PowerTag Energy M630 3P |
LV434022 |
|
PowerTag Energy M630 3P+N |
LV434023 |
|
PowerTag Energy R200 3P/3P+N |
A9MEM1590 |
|
PowerTag Energy R600 3P/3P+N |
A9MEM1591 |
|
PowerTag Energy R1000 3P/3P+N |
A9MEM1592 |
|
PowerTag Energy R2000 3P/3P+N |
A9MEM1593 |
The Easergy wireless sensors can be used for environmental condition monitoring for enclosures and continuous thermal monitoring of critical power connections of indoor installations.
|
Product |
Part number |
|
Easergy CL110 Wireless Environmental Sensor |
EMS59443 a |
|
Easergy TH110 Wireless Thermal Sensor |
EMS59440 b |
The Wiser micro module switches and dimmers can be used for lighting control applications.
|
Product |
Part number |
|
Wiser 1 Gang Micro Module Switch |
CCT5011-0001_AS |
|
Wiser Micro Module Light Switch |
CCT5011-0002 |
|
Wiser 1 Gang Micro Module Dimmer |
CCT5010-0001_AS |
|
Wiser Micro Module Dimmer |
CCT5010-0002 |
The ASSA ABLOY electronic locks can be used for hotel applications with electronic door locks.
|
Product |
Part number |
|
Electronic Locks - VingCard Allure |
See the ASSA ABLOY web site |
|
Electronic Locks - VingCard Essence |
See the ASSA ABLOY web site |
|
Electronic Locks - VingCard Signature |
See the ASSA ABLOY web site |
|
Electronic Locks - VingCard Classic |
See the ASSA ABLOY web site |
|
Electronic Locks - VingCard Flex |
See the ASSA ABLOY web site |