0
Specifications

Specifications


Products: (None)
Functionalities: Engineering, Hardware
Product version: 2023, 2024
12/16/2022

RP-C-EXT-ZB-0-10V

arrow1_rotationIntroduction arrow1_rotationFeatures arrow1_rotationSpecifications arrow1_rotationTerminals
 
action_zoom_plus_stroke RP-C-EXT-ZB-0-10V – Zigbee 0-10V module

RP-C-EXT-ZB-0-10V – Zigbee 0-10V module

Introduction

SpaceLogic* RP-C-EXT-ZB-0-10V Zigbee 0-10V module communicates with the SpaceLogic RP room controller over the Zigbee TM wireless protocol and provides I/O expansion for 0-10V lighting control.

The Zigbee 0-10V module enables dimming of different types of lights equipped with electrical ballasts for 220–240 VAC line voltage. The Zigbee 0-10V module can distribute power (220–240 VAC) from an external power supply to the lights.

Lighting can be controlled by the RP-C through motion detection and light intensity measurement provided by the Multi-sensor or by SpaceLogic Sensors connected to the RP-C.

* Formerly known as SmartX.

Features

The Zigbee 0-10V module has the following features:

  • Wireless communication with the RP-C room controller

  • 0-10V light output for control of 230 VAC powered lights (see output specification for limitations on inrush current)

  • Power consumption monitoring per module

  • Suitable for mounting in ceilings

  • Integrated 2.4 GHz antenna

  • Configuration through EcoStruxure Building Operation software

  • Status LED for the device

0-10V lighting control

The light output is connected to the power supply network through the Zigbee 0-10V module. For the 0-10 VDC control signal wires, you may use the standard installation equipment permitted for ELV (Extra-Low Voltage) installations. The 0-10 VDC control signal meets SELV (Safety Extra-Low Voltage) requirements.

The analog interface has the following features:

  • The lights connected to the output belong to the same group and are thus controlled simultaneously (same ON / OFF / Dimming setpoint).

  • Power to the ballasts is cut off when the lights are switched off.

Table: Part Numbers

Product

Part number

RP-C-EXT-ZB-0-10V
SXWREZB010110001

Specifications

AC input
Nominal voltage
230 VAC
Rated voltage range
220 to 240 VAC
Frequency
50/60 Hz
Maximum load current
5 A
Maximum power consumption
<1 W
Power input protection
MOV suppression and internal fuse
AC output
Rated voltage range
220 to 240 VAC (same as power supply)
Maximum load current
5 A
Maximum inrush current
30 A (<5 ms)
Wireless connectivity
Communication protocol
Zigbee 3.0
Frequency band
2.4 GHz (ISM band), compliant with IEEE Standard 802.15.4
Maximum output power
7 dBm
Effective indoor radio signal range
30 m (98 ft)
Antenna
Integrated antenna
Environment
Ambient temperature, operating
-20 °C to +50 °C (-4 °F to +122 °F)
Case temperature, maximum
75 °C (167 °F)
Ambient temperature, storage
-30 to +65 °C (-22 to +149 °F)
Humidity
Maximum 85 % RH non-condensing
Material
Plastic flame rating
UL94 V-0
Ingress protection rating
IP 20
Mechanical
Dimensions
155 W x 44 H x 30 D mm (6.1 W x 1.7 H x 1.2 D in.)
Weight
0.126 kg (0.278 lb)
Installation
Ceiling
  
Indoor use only
Output terminals
Fixed
  
Left side: 1 x 6-pin terminal block
  
Right side: 1 x 2-pin terminal block
Compatibility
EcoStruxure Building Operation
version 4.0.1 and later
Agency compliances
EMC
ETSI EN 301 489-1 V2.1.1 (2017); ETSI EN 301 489-17 V3.1.1 (2017); BS/EN 61000-3-2:2014; BS/EN 61000-3-3:2013; BS/EN 55015:2013; BS/EN 61547:2009
Radio
ETSI EN 300 328 V2.1.1 (2016)
Safety standards
BS/EN 62493:2015; BS/EN 62479:2010; BS/EN 61347-1:2015; BS/EN 61347-2-11:2001
Power consumption monitoring
BS/EN 61010-1:2010
Hardware
CPU type
ARM Cortex-M4 single-core
Frequency
40 MHz
SRAM (embedded)
64 KB
Flash memory (embedded)
512 KB
NOR flash memory
1 MB
Status indicator
LED (green and red) that shows the status of the device
Reset button
Push-button switch
Energy metering
Measurement accuracy
See table below.

Measurement range

Measurement accuracy

< 50 W

+/-2 W

>= 50 W

+/-2 %

0-10V light output
Outputs
1, terminals 0-10V AO and COM
Output voltage
0 to 10 VDC
Sink current
40 mA

Terminals

 
action_zoom_plus_stroke RP-C-EXT-ZB-0-10V

RP-C-EXT-ZB-0-10V

  • SpaceLogic RP-C Advanced
  • RP-C-EXT-ZB-DALI