The RP-C-EXT-MS-BLE multi-sensor connects to the RP controllers and is used for infrared motion detection and luminosity measurements. The multi-sensor supports Bluetooth Low Energy based applications such as beaconing and remote control communication.
The multi-sensor is connected to the RP controller using an RJ45 type quick connector.
The multi-sensor's three flexible mounting brackets (springs) enable quick and easy installation on a suspended ceiling tile. The multi-sensor also comes with a mounting ring, which allows the sensor to be installed on a ceiling with drywall anchors and a 76 mm (3 in.) clearance hole or to a 102 mm (4 in.) junction/gang box.
The multi-sensor is a Bluetooth Low Energy (BLE) device. The multi-sensor support for Bluetooth beacon enables nearby mobile devices with a specific app installed to interact when in close proximity to the broadcasting multi-sensor. The Bluetooth beacon can be used for services such as indoor positioning of the mobile device. The service and mobile app need to be provided by a third party. The Bluetooth connection can also be used for communication with the RP-C-RC-BLE remote control, which makes it possible to control the lighting, blinds, and air conditioning in a zone of an office building.
The multi-sensor is part of the RP controller expansion modules product range. The multi-sensor can be combined with the RP controller expansion modules for lighting and blind control to provide a connected room solution.
The RP controller expansion sensor modules support motion detection through a passive infrared sensor.
For more information, see Motion Detection .
The RP controller expansion sensor modules support luminosity measurements through an ambient light sensor.
For more information, see Luminosity Measurement .
RP controller expansion modules have two types of memory, flash memory and RAM.
For more information, see RP Controller Expansion Module Memory .
The RP controller expansion sensor modules, such as the Multi-sensor and Insight-Sensor, are Bluetooth Low Energy (BLE) devices, which support applications such as beaconing and remote control communication.
For more information, see RP Controller Expansion Sensor Module Wireless Connectivity .
The RP controller expansion modules have two room bus ports (RJ45 receptacles), which enable connection to the RP controller and other expansion modules on the room bus through a daisy-chain configuration.
For more information, see RP-C Room Bus .
For more information, see RP-V Room Bus .
Each RP controller expansion module has a rotary switch, which is used to give the device a unique address on the room bus.
For more information, see RP-C Room Bus .
For more information, see RP-V Room Bus .
The RP controller room bus allows RP controller expansion modules to be connected to the controller for people counting, motion detection, luminosity and sound pressure level measurements, Bluetooth Low Energy based applications, and control of electric lights and window blinds.
For more information, see RP-C Room Bus .
For more information, see RP-V Room Bus .
There is one LED on the RP controller expansion sensor modules. The LED is integrated with the Set button.
For more information, see RP Controller Expansion Sensor Module LED .
The RP controller expansion sensor modules have a Set button on the front. The Set button is reserved for future use.
For more information, see RP Controller Expansion Sensor Module Set Button .
The RP controller expansion multi-sensor can be installed on a dropped (suspended) ceiling, a drywall ceiling, or a junction (gang) box.
For more information, see RP Controller Expansion Multi-sensor Device Installation .
The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, BACnet/IP devices, RP controller expansion modules, and Operator Display.
For more information, see Wiring .
The RP controller expansion modules support different modes that can be used for maintenance purposes.
For more information, see RP Controller Expansion Module Maintenance Modes .
Using WorkStation, you can update the firmware of multiple BACnet/IP devices and their attached SpaceLogic Sensor devices and RP controller expansion modules at the same time with minimum downtime. In particular, the universal upgrade package simplifies the update process and requires minimal user involvement and coordination.
SpaceLogic Sensor devices and RP controller expansion modules are supported by the RP controller.
For more information, see BACnet/IP Device Firmware Management .
This section provides information on regulatory compliance and approvals for the RP controller expansion multi-sensor.
For more information, see RP Controller Expansion Multi-sensor Regulatory Compliance and Approvals .
| Electrical | |||||||||
DC input supply voltage
|
24 VDC
|
||||||||
Powered by the RP controller through the room bus (RJ45)
|
|||||||||
Maximum power consumption
|
0.3 W
|
||||||||
| Environment | |||||||||
Ambient temperature, operating
|
0 to 50 °C (32 to 122 °F)
|
||||||||
Ambient temperature, storage
|
-20 to +70 °C (-4 to +158 °F)
|
||||||||
Humidity
|
20 to 90 % RH non-condensing
|
||||||||
| Material | |||||||||
Plastic flame rating
|
UL94 V-0
|
||||||||
Ingress protection rating
|
IP 20
|
||||||||
Plenum rating
|
UL 2043
|
||||||||
Cover color
|
Signal white (RAL9003)
|
||||||||
| Mechanical | |||||||||
|
|||||||||
Overall external diameter
|
97.5 mm (3.84 in.)
|
||||||||
Diameter of mounting clearance hole
|
75.0 to 76.0 mm (2.95 to 3.00 in.)
|
||||||||
External washer thickness
|
12 mm (0.47 in.)
|
||||||||
Overall external thickness
|
19 mm (0.75 in.)
|
||||||||
Internal thickness
|
20 mm (0.79 in.)
|
||||||||
Overall internal depth
|
28 mm (1.10 in.)
|
||||||||
Weight, multi-sensor with mounting springs (3x)
|
0.083 kg (0.183 lb)
|
||||||||
Weight, multi-sensor with mounting ring
|
0.094 kg (0.207 lb)
|
||||||||
Installation
|
Plastic unit to be fitted flush in a suspended ceiling tile with a thickness of up to 45 mm (1.77 in.)
|
||||||||
| Communication ports | |||||||||
Room bus
|
RS-485
|
||||||||
Dual RJ45 ports for daisy-chain configurations
|
|||||||||
Use a Cat 5 (or higher) cable
|
|||||||||
Maximum total length of the room bus: 72 m (236 ft)
|
|||||||||
Room bus protection
|
Transient voltage suppressors on communication and power signals
|
||||||||
| Wireless connectivity | |||||||||
| Bluetooth Low Energy | |||||||||
Communication protocol
|
Bluetooth
®
5.1 Low Energy compliant
|
||||||||
Frequency
|
2.402 to 2.480 GHz
|
||||||||
Maximum communication distance
|
Line-of-sight: 50 m (164 ft)
|
||||||||
Maximum output power
|
3 dBm
|
||||||||
Antenna
|
Integrated antenna
|
||||||||
Beacon protocol
|
iBeacon
|
||||||||
| Hardware | |||||||||
CPU type
|
ARM Cortex-M4 single-core
|
||||||||
Frequency
|
38.4 MHz
|
||||||||
SRAM (embedded)
|
256 KB
|
||||||||
Flash memory (embedded)
|
1024 KB
|
||||||||
Flash memory (serial)
|
2 MB
|
||||||||
Status indicator
|
LED (green and red) that shows the status of the device
|
||||||||
Address switch
|
Rotary switch 0 to 9
|
||||||||
Set button
|
Push-button switch
|
||||||||
| Motion detection | |||||||||
Sensor
|
Quad-type passive infrared (PIR) sensor with Fresnel lens
|
||||||||
Detection range
|
See image and table below.
|
||||||||
|
|||||||||
|
|||||||||
| Luminosity measurements | |||||||||
Sensor
|
Ambient Light Sensor (ALS)
|
||||||||
|
|||||||||
Spectral response
|
Human eye
|
||||||||
Luminosity range
|
0 to 10,000 lux
|
||||||||
Field of view
|
30 degrees from vertical
|
||||||||
The RP-C-EXT-MS-BLE internal configuration with regards to the signal ground is shown in the following figure.