Productos RP-C, RP-C-EXT-0-10V-4-PD, RP-C-EXT-BL-2-LV-PD, RP-C-EXT-BL-4-HV-PD, RP-C-EXT-DALI-M-PD, RP-C-EXT-MS-BLE
Funcionalidades: Hardware
Versión del producto: 3.1, 3.2
19/12/2019

Configuring an RP Series Expansion Module or Multi-sensor into Online Maintenance Mode

You configure an RP Series expansion module or multi-sensor into online maintenance mode to read diagnostics from the device and to upgrade the device with new firmware.

Mostrar más
action_close

The RP Series expansion modules and multi-sensors support different modes that can be used for maintenance purposes.

The following maintenance modes are supported:

  • Offline maintenance mode

  • Online maintenance mode

The Status LED on the RP Series expansion modules and multi-sensors indicates when the device is in maintenance mode, provided that the LED is configured in show status mode (default mode). Para obtener más información, consulte RP Series Expansion Module LEDs .Para obtener más información, consulte RP Series Expansion Multi-sensor LED .

Offline maintenance mode

The device enters maintenance mode and goes offline when you configure the room bus address 0 for the device using its rotary switch.

Online maintenance mode

In online maintenance mode, the device will be online but without running any software other than what makes it possible to read diagnostics from the device and to upgrade the device.

Para obtener más información, consulte Configuring an RP Series Expansion Module or Multi-sensor into Online Maintenance Mode .

To configure an RP Series expansion module or multi-sensor into online maintenance mode
  1. Power off the RP Series expansion module or multi-sensor by disconnecting the device from the RP-C room bus.

    Para obtener más información, consulte RP-C Room Bus .

  2. Configure the room bus address 0 for the device, by turning the rotary switch on the device.

  3. Power on the RP Series expansion module or multi-sensor by connecting the device to the RP-C room bus.

    Para obtener más información, consulte Connecting RP Series Expansion Modules and Multi-sensors to RP-C .

  4. Configure a unique room bus address in the range of 1 to 6 for the device.

    Para obtener más información, consulte Configuring the Room Bus Address for an RP Series Expansion Module .

    Para obtener más información, consulte Configuring the Room Bus Address for an RP Series Expansion Multi-sensor .

You can now read diagnostic log files from the device and upgrade the device with new firmware.

  • RP Series Expansion Module and Multi-sensor Maintenance Modes
  • Connecting RP Series Expansion Modules and Multi-sensors to RP-C
  • RP-C Room Bus
  • RP Series Expansion Module Room Bus Addressing
  • Configuring the Room Bus Address for an RP Series Expansion Module
  • Configuring the Room Bus Address for an RP Series Expansion Multi-sensor
  • RP Series Expansion Module Diagnostics
  • Retrieving RP Series Expansion Module Diagnostics