earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Products: RP-C, RP-C-EXT-DALI-M-PD
Functionalities: Hardware
Product version: 2022, 2023, 2024, 7.0, 7.1
12/17/2021

Wire Sizes and Lengths for the DALI Bus of the RP Controller Expansion DALI Light Modules

This section provides recommendations on wire sizes and lengths for the DALI bus of the RP controller expansion DALI light modules.

The DALI bus is connected to the DALI inputs/outputs, labeled Light 1 to Light 4, of the DALI light modules. The DALI inputs/outputs have two terminals, labeled DA+ and DA-, to which the two-wire bus is connected.

The recommendations are for guidance only. Other wire sizes and lengths may be used, depending on wiring rules and when appropriate.

Only copper wires should be used for the DALI bus.

Table: Wire Sizes and Lengths for the DALI Bus of the RP Controller Expansion DALI Light Modules

Minimum Cross-sectional Area

Cable Length

0.5 mm² (20 AWG)

Up to 100 m (328 ft)

0.75 mm² (18 AWG)

Up to 150 m (492 ft)

1.5 mm² (15 AWG)

Up to 300 m (984 ft)

  • I/O Wiring
  • Wire Sizes and Lengths
  • Wire Sizes and Lengths for the Digital Inputs of the RP Controller Expansion Modules
  • DALI Inputs/Outputs with Power Distribution
  • DALI Inputs/Outputs without Power Distribution