earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
How to

How to


Products: Commission, IP-IO , MP-C, MP-V, RP-C
Functionalities: Engineering, BACnet/IP devices
Product version: 2023, 2024, 7.0
4/3/2024

Discovering, Associating, and Winking DALI Outputs

Before you can do an I/O checkout on a DALI module, you must first perform a DALI discovery and associate the discovered physical output with logical outputs in the RP controller configuration. You then wink DALI outputs in order to identify the light or control device location when associating the physical output with the logical output.

Show More
action_close

The RP-C-EXT-DALI-M-PD light module connects to the RP-C room controllers and provides I/O expansion for lighting control with DALI (Digital Addressable Lighting Interface).

The DALI light module enables control of lights equipped with electronic ballasts, LED drivers, and other control gear with DALI interface as well as connection of DALI input devices such as sensors and push-buttons.

The power distribution capability means that the DALI light module can supply the connected control gear with AC mains voltage (230 VAC) from the module's power input.

The DALI light module is a DALI-2 certified control device (application controller) with multi-master capability. DALI-2 compliance means benefits such as improved interoperability and easier installation and maintenance. The DALI light module can be used with DALI version-1 products because DALI-2 is designed to be backward compatible with DALI version-1. The multi-master capability of the DALI light module allows the module to function as a DALI master in a DALI network and can thus work together with DALI-2 sensors and push-buttons.

The DALI light module is part of the RP controller expansion modules for connected room solution and can be combined with other modules from this product range.

 
action_zoom_plus_stroke RP-C-EXT-DALI-M-PD – DALI light module with power distribution capability
Figure: RP-C-EXT-DALI-M-PD – DALI light module with power distribution capability

DALI Inputs/Outputs with Power Distribution

The DALI light modules have four DALI inputs/outputs, which are designed for control and power supply of DALI light control gear such as lights with electronic ballasts, LED drivers, and other control gear with DALI interface as well as connection of DALI input devices such as sensors and push-buttons. Outputs not used for DALI lighting control can instead be configured and used for relay control of non-DALI lights on/off.

For more information, see DALI Inputs/Outputs with Power Distribution .

RP Controller Expansion Module Digital Inputs

The RP controller expansion modules have digital inputs that can be used for sensing of dry contacts:

  • The light modules, blind modules, and the RP-C-EXT-REL-4 relay module have four digital inputs, which can be used in applications such as interfacing with light switches and window contacts.

  • The CRS-HH-REL-10 relay module has 12 digital inputs suitable for dry contact monitoring of switches and push buttons used for lighting control, window and door positions, and other functions in the hotel room.

For more information, see RP Controller Expansion Module Digital Inputs .

RP Controller Expansion Module Built-in Power Supply

The RP controller expansion light modules with power distribution capability, low-voltage blind modules, and SMI blind modules have a built-in power supply that can accommodate a nominal input voltage of 230 VAC at 50/60 Hz. Light modules without power distribution capability can accommodate a nominal input voltage of 100 to 277 VAC at 50/60 Hz.

For more information, see RP Controller Expansion Module Built-in Power Supply .

RP Controller Expansion Module Energy Metering

RP controller expansion modules with power distribution capability support energy metering, which means that the module can measure the electrical energy consumption and power demand for the equipment connected to and supplied by the module.

For more information, see RP Controller Expansion Module Energy Metering .

RP Controller Expansion Module Memory

RP controller expansion modules have two types of memory, flash memory and RAM.

For more information, see RP Controller Expansion Module Memory .

DALI Light Module Supported Building Standards

The DALI light module complies to version 2 of the IEC 62386 standard (DALI-2).

For more information, see DALI Light Module Supported Building Standards .

RP Controller Expansion Module Communication Ports

The RP controller expansion modules have two room bus ports (RJ45 receptacles), which enable connection to the RP-C controller and other expansion modules on the room bus through a daisy-chain configuration.

For more information, see RP-C Room Bus .

RP Controller Expansion Module Address Switch

Each RP controller expansion module has a rotary switch, which is used to give the device a unique address on the room bus.

For more information, see RP-C Room Bus .

RP-C Room Bus

The RP controller room bus allows RP controller expansion modules to be connected to the controller for people counting, motion detection, luminosity and sound pressure level measurements, Bluetooth Low Energy based applications, and control of electric lights and window blinds.

For more information, see RP-C Room Bus .

RP Controller Expansion Module Pluggable Connectors

The RP controller expansion modules have PCB mounted connectors for the power input, outputs, and digital inputs. The PCB mounted connectors mate with pluggable connectors:

  • The light modules, blind modules, and the RP-C-EXT-REL-4 relay module have mechanically keyed and color-coded connectors, which allows the matching external connectors to be plugged in on site quickly and easily.

  • The CRS-HH-REL-10 relay module has PCB header connectors for pluggable screw terminal blocks, which are easy to install and remove from the device.

For more information, see RP Controller Expansion Module Pluggable Connectors .

RP Controller Expansion Module LEDs

There is one or more LEDs on the front panel of the RP controller expansion modules.

For more information, see RP Controller Expansion Module LEDs .

RP Controller Expansion Module Set Button

All RP controller expansion modules have a Set button on the front. The Set button is reserved for future use.

For more information, see RP Controller Expansion Module Set Button .

RP Controller Expansion Module Device Installation

The RP controller expansion module can be installed on a DIN rail or other flat surface inside a cabinet. The device is recommended to be installed in a cabinet, unless local regulations allow an exception.

For more information, see RP Controller Expansion Module Device Installation .

Wiring

The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, BACnet/IP devices, RP controller expansion modules, and Operator Display.

For more information, see Wiring .

RP Controller Expansion Module Maintenance Modes

The RP controller expansion modules support different modes that can be used for maintenance purposes.

For more information, see RP Controller Expansion Module Maintenance Modes .

BACnet/IP Device Firmware Management

Using WorkStation, you can update the firmware of multiple BACnet/IP devices and their attached SpaceLogic Sensor devices and RP controller expansion modules at the same time with minimum downtime. In particular, the universal upgrade package simplifies the update process and requires minimal user involvement and coordination.

Tip:

SpaceLogic Sensor devices and RP controller expansion modules are supported by the RP controller.

For more information, see BACnet/IP Device Firmware Management .

RP Controller Expansion Module Regulatory Compliance and Approvals

This section provides information on regulatory compliance and approvals for the RP controller expansion modules.

For more information, see RP Controller Expansion Light, Blind, and Relay Modules Regulatory Compliance and Approvals .

Specifications

Electrical
Nominal voltage
230 VAC
Operating voltage range
+/-10 %
Frequency
50/60 Hz
Maximum current consumption
10 A
Room bus power consumption
0.3 W (24 VDC)
Protection
Maximum 16 A external fuse (circuit breaker) is needed
Overvoltage category
III
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Humidity
20 to 90 % RH non-condensing
Pollution degree
2
Material
Plastic flame rating
UL94 V-0
Ingress protection rating
IP 20
Mechanical
Dimensions
198 W x 110 H x 64 D mm (7.8 W x 4.3 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight
0.433 kg (0.955 lb)
Recommended installation
DIN rail or flat surface in a cabinet a
Connectors
Power input: 1 x 3-pin Wieland GST15i3 connector
  
DALI inputs/outputs: 4 x 5-pin Wieland GST15i5 connector
  
Digital inputs: 4 x 2-pin Wieland GST15i2 connector
Communication ports
Room bus
RS-485
  
Dual RJ45 ports for daisy-chain configurations
  
Use a Cat 5 (or higher) cable
  
Maximum total length of the room bus: 72 m (236 ft)
Room bus protection
Transient voltage suppressors on communication and power signals
Hardware
Main microcontroller
CPU type
ARM Cortex-M4 single-core
Frequency
80 MHz
SRAM (embedded)
320 KB
Flash memory (embedded)
1024 KB
Memory
NOR flash memory
16 MB
DALI microcontroller
CPU type
ARM Cortex-M0 single-core
Frequency
32 MHz
SRAM (embedded)
8 KB
Flash memory (embedded)
64 KB
Additional hardware
Status indicator
LED (green and red) that shows the status of the device
Light status indicator
One status LED (green) for each DALI input/output
Address switch
Rotary switch 0 to 9
Set button
Push-button switch
Energy metering
Energy consumption measurement
The energy consumption is measured in Wh, shared by the four outputs.
Accuracy class (according to IEC 61557-12)
Active energy measurement: Class 1
Typical measurement accuracy at room temperature
20 to 100 W: 5%
  
100 to 3000 W: 1%
DALI inputs/outputs
Inputs/outputs
4, Light 1 to Light 4
The four inputs/outputs share one DALI channel.
Input/output terminals
N, PE, L, DA+, and DA-
DALI bus voltage
18 VDC
Maximum supply current
250 mA
Guaranteed supply current
64 mA
Maximum cable length
See chapter Wiring.
Power distribution
230 VAC (same voltage as power supply)
  
Maximum 5 A load per output
  
Maximum 10 A total load for the 4 outputs
  
Maximum 165 A inrush current (<20 ms) per output
  
Maximum 800 A inrush current (<200 µs) per output
Digital inputs
Inputs
4, DI1 to DI4
Range
Dry contact, 0 to 5.0 VDC, 2.2 mA, SELV (Safety Extra-Low Voltage)

Internal Configuration

The RP-C-EXT-DALI-M-PD internal configuration with regards to the signal ground is shown in the following figure.

 
action_zoom_plus_stroke RP-C-EXT-DALI-M-PD internal configuration
Figure: RP-C-EXT-DALI-M-PD internal configuration

To discover, associate, and wink DALI outputs
  1. In the Commission mobile application, click I/O Checkout .

  2. On the I/O Resources page, click Room Bus Modules .

  3. On the Room Bus Modules page, select the DALI module from the two module types that display: DALI power and DALI.

  4. Click Discover/Associate .

  5. Select a discover command as follows before clicking Discover .

    Note:

    Clicking Discover assigns addresses to all of the lights or control devices connected to the bus.

    • Click Discover new lights to discover only the new lights that have been installed on the DALI bus since the last discovery.

    • Click Discover new control devices to discover only the new control devices that have been installed on the DALI bus since the last discovery.

    • Click Discover all lights and control devices to discover all of the physical lights and control devices on the bus.

      Enter the word REDISCOVER to confirm that you really want to do this when the information dialog displays. Ensure also that you re-enter all physical light and control device associations.

    • Click Discover all lights to discover all of the physical lights on the bus.

      Enter the word REDISCOVER to confirm that you really want to do this when the information dialog displays. Ensure that you re-enter all physical light associations.

    • Click Discover all control devices to discover all of the physical control devices on the bus.

      Enter the word REDISCOVER to confirm that you really want to do this when the information dialog displays. Ensure that you re-enter all physical control device associations.

  6. In the Associate page, click the light bulb button

     
    action_zoom_plus_stroke
    to wink the light or control device in order to determine its location in the room.

  7. Click the Associate with box and select the name of the logical output that should be associated with the physical light or control device at the current address.

    Note:

    When the discovered lights are part of a DALI channel drop, the drop-down box is disabled since they cannot be changed. The name of the DALI channel group is displayed, however, so you can still wink the lights that are part of the DALI channel group.

  • Performing a Room Bus Module I/O Checkout
  • RP-C-EXT-DALI-M-PD