The RP-C-EXT-ZB-DALI Zigbee DALI module communicates with the RP-C room controller over the Zigbee TM wireless protocol and provides I/O expansion for lighting control with DALI (Digital Addressable Lighting Interface).
The Zigbee DALI module enables control of different types of lights equipped with DALI electrical ballasts for 220–240 VAC line voltage. The Zigbee DALI module can distribute power (220–240 VAC) from an external power supply to the lights (DALI control gear).
The Zigbee DALI module supports LED lamp control gear (LED drivers) of Device Type 6 (DT6) and fluorescent lamp control gear of Device Type 0 (DT0).
The Zigbee DALI module supports broadcast addressing of the DALI devices. Using the DALI broadcast command, all lights connected to the output are controlled simultaneously for switching on/off and dimming.
The Zigbee DALI module provides one DALI channel (DALI bus). Up to 20 DALI control gear devices can be connected to the Zigbee DALI module.
The Zigbee DALI module has one DALI light output for control of lights with electronic ballasts, LED drivers, and other control gear with DALI interface and one power output for power distribution to the control gear.
有关更多信息,请参阅 Zigbee DALI Light Output and Power Output .
The RP controller expansion Zigbee modules have power distribution capability, which means that the module distributes the AC mains voltage (220–240 VAC) from the Power Input terminals to the light control gear connected to the Power Output terminals.
有关更多信息,请参阅 Zigbee Modules Power Distribution .
RP controller expansion Zigbee modules can measure and monitor the power consumption for the loads connected to the module.
有关更多信息,请参阅 Zigbee Modules Power Consumption Monitoring .
RP controller expansion Zigbee modules have two types of memory, flash memory and RAM.
有关更多信息,请参阅 Zigbee Modules Memory .
The RP controller expansion Zigbee modules are Zigbee Certified Products. The Zigbee modules' wireless connectivity option is used for connecting to and communicating with the RP controller.
有关更多信息,请参阅 Zigbee Modules Wireless Connectivity .
The RP controller expansion Zigbee modules have fixed screw terminals for the power input, power output, and light output.
有关更多信息,请参阅 Zigbee Modules Screw Terminals .
There is one LED on the front panel of the RP controller expansion Zigbee modules.
有关更多信息,请参阅 Zigbee Modules LED .
The RP controller expansion Zigbee modules have a Reset button on the front.
有关更多信息,请参阅 Zigbee Modules Reset Button .
The RP controller expansion Zigbee modules are designed to be installed on a flat surface on a ceiling.
有关更多信息,请参阅 Zigbee Modules Device Installation .
The wiring recommendations provide guidance regarding wiring of the Central IO modules, automation servers, BACnet/IP devices, RP controller expansion modules, and Operator Display.
有关更多信息,请参阅 Wiring .
Using WorkStation, you can update the firmware of multiple BACnet/IP devices and their attached SpaceLogic Sensor devices and RP controller expansion modules at the same time with minimum downtime. In particular, the universal upgrade package simplifies the update process and requires minimal user involvement and coordination.
SpaceLogic Sensor devices and RP controller expansion modules are supported by the RP controller.
有关更多信息,请参阅 BACnet/IP Device Firmware Management .
This section provides information on regulatory compliance and approvals for the RP controller expansion Zigbee modules.
有关更多信息,请参阅 Zigbee Modules Regulatory Compliance and Approvals .
AC input | ||||||||||
Nominal voltage
|
230 VAC
|
|||||||||
Rated voltage range
|
220 to 240 VAC
|
|||||||||
Frequency
|
50/60 Hz
|
|||||||||
Maximum load current
|
5 A
|
|||||||||
Maximum power consumption
|
<1 W
|
|||||||||
Power input protection
|
MOV suppression and internal fuse
|
|||||||||
AC output | ||||||||||
Rated voltage range
|
220 to 240 VAC (same as power supply)
|
|||||||||
Maximum load current
|
5 A
|
|||||||||
Maximum inrush current
|
30 A (<5 ms)
|
|||||||||
Wireless connectivity | ||||||||||
Communication protocol
|
Zigbee 3.0
|
|||||||||
Frequency band
|
2.4 GHz (ISM band), compliant with IEEE Standard 802.15.4
|
|||||||||
Maximum output power
|
7 dBm
|
|||||||||
Effective indoor radio signal range
|
30 m (98 ft)
|
|||||||||
Antenna
|
Integrated antenna
|
|||||||||
Environment | ||||||||||
Ambient temperature, operating
|
-20 °C to +50 °C (-4 °F to +122 °F)
|
|||||||||
Case temperature, maximum
|
75 °C (167 °F)
|
|||||||||
Ambient temperature, storage
|
-30 to +65 °C (-22 to +149 °F)
|
|||||||||
Humidity
|
Maximum 85 % RH non-condensing
|
|||||||||
Material | ||||||||||
Plastic flame rating
|
UL94 V-0
|
|||||||||
Ingress protection rating
|
IP 20
|
|||||||||
Mechanical | ||||||||||
Dimensions
|
155 W x 44 H x 30 D mm (6.1 W x 1.7 H x 1.2 D in.)
|
|||||||||
Weight
|
0.126 kg (0.278 lb)
|
|||||||||
Installation
|
Ceiling
|
|||||||||
Indoor use only
|
||||||||||
Output terminals
|
Fixed
|
|||||||||
Left side: 1 x 6-pin terminal block
|
||||||||||
Right side: 1 x 2-pin terminal block
|
||||||||||
Hardware | ||||||||||
Main microcontroller | ||||||||||
CPU type
|
ARM Cortex-M4 single-core
|
|||||||||
Frequency
|
40 MHz
|
|||||||||
SRAM (embedded)
|
64 KB
|
|||||||||
Flash memory (embedded)
|
512 KB
|
|||||||||
Memory | ||||||||||
NOR flash memory
|
1 MB
|
|||||||||
DALI microcontroller | ||||||||||
CPU type
|
ARM Cortex-M0 single-core
|
|||||||||
Frequency
|
32 MHz
|
|||||||||
SRAM (embedded)
|
16 KB
|
|||||||||
Flash memory (embedded)
|
32 KB
|
|||||||||
Additional hardware | ||||||||||
Status indicator
|
LED (green and red) that shows the status of the device
|
|||||||||
Reset button
|
Push-button switch
|
|||||||||
Energy metering | ||||||||||
Measurement accuracy
|
See table below.
|
|||||||||
|
||||||||||
DALI light output | ||||||||||
Outputs
|
1 (1 DALI channel), terminals DA+ and DA-
|
|||||||||
DALI bus voltage
|
17 VDC
|
|||||||||
Maximum supply current
|
250 mA
|
|||||||||
Guaranteed supply current
|
90 mA
|
|||||||||
Maximum cable length
|
See chapter Wiring.
|
|||||||||
DALI devices | ||||||||||
Supported control gear
|
See table below.
|
|||||||||
|