earth_america
user_standard Log on
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concept

Concept


Products: RP-C
Functionalities: Hardware
Product version: 2022, 2023, 2024, 7.0
3/11/2022

Wire Sizes and Lengths for the RP Controller Expansion Zigbee Modules

This section provides recommendations on wire sizes and lengths for the RP controller expansion Zigbee DALI and 0-10V modules.

The recommendations are for guidance only. Other wire sizes and lengths may be used, depending on wiring rules and when appropriate.

Table: Wire Sizes and Lengths for the RP Controller Expansion Zigbee DALI and 0-10V Modules

Terminals

Minimum Cross-sectional Area

Maximum Cross-sectional Area

Maximum Cable Length

Power input

L (in)

0.75 mm² (18 AWG)

1.5 mm² (15 AWG)

According to local wiring rules

N (in)

0.75 mm² (18 AWG)

1.5 mm² (15 AWG)

According to local wiring rules

 
action_zoom_plus_stroke

0.75 mm² (18 AWG)

1.5 mm² (15 AWG)

According to local wiring rules

Power output

L (out)

0.75 mm² (18 AWG)

1.5 mm² (15 AWG)

According to local wiring rules

N (out)

0.75 mm² (18 AWG)

1.5 mm² (15 AWG)

According to local wiring rules

 
action_zoom_plus_stroke

0.75 mm² (18 AWG)

1.5 mm² (15 AWG)

According to local wiring rules

DALI light output

DA+

0.75 mm² (18 AWG)

1.5 mm² (15 AWG)

For more information, see Wire Sizes and Lengths for the DALI Bus of the Zigbee DALI Module .

DA-

0.75 mm² (18 AWG)

1.5 mm² (15 AWG)

For more information, see Wire Sizes and Lengths for the DALI Bus of the Zigbee DALI Module .

0-10V light output

0-10V AO

0.75 mm² (18 AWG)

1.5 mm² (15 AWG)

100 m

COM

0.75 mm² (18 AWG)

1.5 mm² (15 AWG)

100 m

  • I/O Wiring
  • Wire Sizes and Lengths
  • Wire Sizes and Lengths for the DALI Bus of the Zigbee DALI Module
  • RP-C-EXT-ZB-DALI
  • RP-C-EXT-ZB-0-10V
  • Zigbee DALI Module Screw Terminals
  • Zigbee 0-10V Module Screw Terminals
  • Wiring