Concept

Concept


Produits : RP-C
Fonctionnalités : Matériel
Version produit : 2023, 2024, 7.0
17/12/2022

Zigbee DALI Light Output and Power Output

arrow1_rotationSpécifications

The Zigbee DALI module has one DALI light output for control of lights with electronic ballasts, LED drivers, and other control gear with DALI interface and one power output for power distribution to the control gear.

The Zigbee DALI module supports:

  • DALI lighting control

  • Power distribution (220–240 VAC)

 
action_zoom_plus_stroke Zigbee DALI module, DALI light output and power distribution
Figure : Zigbee DALI module, DALI light output and power distribution
DALI lighting control

The DALI light output equals one logical DALI channel.

The DALI light output has two screw terminals for DALI lighting control:

  • DA+

  • DA-

These two screw terminals are where the wires from the DALI bus are connected. The DALI bus is a 2-wire bus, which is used for bi-directional communication. Pour plus d'informations, voir Wire Sizes and Lengths .

The Zigbee DALI module monitors and controls all control gear devices on the DALI bus. A broadcast address is used when communicating with the control gear devices on the bus. For example, a broadcast command can be used to change all LED drivers in a room from Off to On.

Up to 20 DALI control gear devices to can be connected to the Zigbee DALI module. The maximum number of control gear devices per module is also determined by the module's power distribution limitations. For more information, see section “Specifications”.

Power distribution

The power distribution capability means that the module distributes the AC mains voltage (220–240 VAC) from the Power Input to the control gear connected to the Power Output. Pour plus d'informations, voir Zigbee Modules Power Distribution .

The Power Output has three screw terminals for power distribution:

  •  
    action_zoom_plus_stroke
    – Protective earth ground

  • N (out) – Neutral

  • L (out) – Line

The module uses a relay to control the power distribution, by connecting or disconnecting the AC mains voltage to the Power Output's L (out) terminal. In the figure above, the relay is named K1.

The module's AC mains voltage side and low-voltage side (SELV side) are galvanically separated by means of isolation circuitry.

The module has energy metering circuitry to measure the energy consumption for the total load connected to the module. Pour plus d'informations, voir Zigbee Modules Power Consumption Monitoring .

Spécifications

DALI light output
Outputs
1 (1 DALI channel), terminals DA+ and DA-
DALI bus voltage
17 VDC
Maximum supply current
250 mA
Guaranteed supply current
90 mA
Maximum cable length
See chapter Wiring.
Power input
Nominal voltage
230 VAC
Rated voltage range
220 to 240 VAC
Frequency
50/60 Hz
Maximum load current
5 A
Maximum power consumption
<1 W
Power input protection
MOV suppression and internal fuse
Power output
Rated voltage range
220 to 240 VAC (same as power supply)
Maximum load current
5 A
Maximum inrush current
30 A (<5 ms)
  • RP Controller Expansion Zigbee Modules
  • RP-C-EXT-ZB-DALI
  • Zigbee Modules Power Distribution
  • Zigbee Modules Power Consumption Monitoring
  • Wire Sizes and Lengths