The KNX Modbus gateway (RP-C-EXT-KNX) is equipped with two 3-position pluggable screw terminal blocks for connection to the RP-C Modbus (RS-485) network and a 2-pole PCB connector for connection to the KNX bus.
You need to configure which RS-485 port (RJ45) on the RP-C controller to use for the Modbus network. You can configure to use either the RS-485 Com A port (default: Sensor bus) or RS-485 Com B port (default: Room bus). For more information, see RP-C Communication Ports .For more information, see Allocating Flexible Ports .
For the RP-C-12A-F-24V, RP-C-12B-F-24V, RP-C-12C-F-24V, and RP-C-16A-F-230V controller models, the rating for the RS-485 Com A port, the RJ45 pinout for the RS-485 Com B port, and the labeling of the two RS-485 ports differ between different hardware versions of the controllers. For more information, see Differences Between RP-C Hardware Versions .
    The upper and lower screw terminal blocks are used as follows:
Upper: Power input from the RP-C through the controller's RS-485 port
Lower: Communication with the RP-C over the controller's Modbus network
The RS-485 Power Adapter (SXWNISORS485P10001) can be used to convert an RP-C controller's RS-485 port RJ45 interface to screw terminals. The adapter has a screw terminal for 24 VDC to support power supply from the controller to a device on the RS-485 based network. For more information, see Convert a BACnet/IP Controller RS-485 Interface .
| 
 Terminal number  | 
 Designation  | 
 Usage  | 
 RP-C RS-485 Port RJ45 Pin  | 
| 
 Power input  | 
 
  | 
 
  | 
 
  | 
| 
 1  | 
 –  | 
 Ground connection for supply voltage from the RP-C.  | 
 5 a  | 
| 
 2  | 
 –  | 
 Ground connection for supply voltage. Not connected to the RP-C.  | 
 -  | 
| 
 3  | 
 +  | 
 Positive connection for supply voltage (24 VDC) from the RP-C.  | 
 4, 7  | 
| 
 Modbus  | 
 
  | 
 
  | 
 
  | 
| 
 4  | 
 –  | 
 Ground connection for Modbus communication with the RP-C.  | 
 8 a  | 
| 
 5  | 
 A  | 
 Data line A (RS485+) for Modbus communication with the RP-C.  | 
 3  | 
| 
 6  | 
 B  | 
 Data line B (RS485–) for Modbus communication with the RP-C.  | 
 6  | 
The KNX Modbus gateway uses a 4-conductor, 2-pole KNX connector for connection to the KNX bus.
| 
 Connector color  | 
 Designation  | 
 Usage  | 
| 
 Red  | 
 +  | 
 Positive connection to KNX bus  | 
| 
 Dark gray  | 
 –  | 
 Ground connection to KNX bus  |