earth_america
user_standard Iniciar sesión
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concepto

Concepto


Productos RP-C
Funcionalidades: Hardware
Versión del producto: 2023, 2024, 7.0
17/12/2022

Zigbee 0-10V Light Output and Power Output

arrow1_rotationEspecificaciones

The Zigbee 0-10V module has one 0-10V analog output for control (dimming) of lights with electronic ballasts, LED drivers, and other 0-10V compatible control gear and one power output for power distribution to the control gear.

The Zigbee 0-10V module supports:

  • 0-10V lighting control

  • Power distribution (220–240 VAC)

 
action_zoom_plus_stroke Zigbee 0-10V module, 0-10V light output and power distribution
Figura: Zigbee 0-10V module, 0-10V light output and power distribution
0-10V lighting control

The 0-10V light output has two screw terminals for 0-10V lighting control:

  • 0-10V AO (Analog Output)

  • COM (Common)

The control signal is a DC voltage that varies between 0 V and 10 V. The Zigbee 0-10V module supports the current sinking standard.

The maximum number of control gear devices per module and per output is determined by the module's power distribution limitations. For more information, see section “Specifications”.

Power distribution

The power distribution capability means that the module distributes the AC mains voltage (220–240 VAC) from the Power Input to the control gear connected to the Power Output. Para obtener más información, consulte Zigbee Modules Power Distribution .

The Power Output has three screw terminals for power distribution:

  •  
    action_zoom_plus_stroke
    – Protective earth ground

  • N (out) – Neutral

  • L (out) – Line

The module uses a relay to control the power distribution, by connecting or disconnecting the AC mains voltage to the Power Output's L (out) terminal. In the figure above, the relay is named K1.

The module's AC mains voltage side and low-voltage side (SELV side) are galvanically separated by means of isolation circuitry.

The module has energy metering circuitry to measure the energy consumption for the total load connected to the module. Para obtener más información, consulte Zigbee Modules Power Consumption Monitoring .

Especificaciones

0-10V light output
Outputs
1, terminals 0-10V AO and COM
Output voltage
0 to 10 VDC
Sink current
40 mA
Power input
Nominal voltage
230 VAC
Rated voltage range
220 to 240 VAC
Frequency
50/60 Hz
Maximum load current
5 A
Maximum power consumption
<1 W
Power input protection
MOV suppression and internal fuse
Power output
Rated voltage range
220 to 240 VAC (same as power supply)
Maximum load current
5 A
Maximum inrush current
30 A (<5 ms)
  • RP Controller Expansion Zigbee Modules
  • RP-C-EXT-ZB-0-10V
  • Zigbee Modules Power Distribution
  • Zigbee Modules Power Consumption Monitoring
  • Wire Sizes and Lengths