earth_america
user_standard Zaloguj się
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Pojęcie

Pojęcie


Produkty: RP-C, RP-C-EXT-KNX
Funkcje: Sprzęt
Wersja produktu: 2022
2023-03-30

RP-C Modbus

The RP controller Modbus RTU (RS-485) subnetwork allows standard Modbus devices and the KNX Modbus gateway (RP-C-EXT-KNX) to be connected to the controller. An adapter is required for converting the controller RS-485 Com port with RJ45 interface to screw terminals.

The Modbus RTU protocol is used for the communication. The RP controller acts the Modbus client and the connected devices act as servers.

For standard Modbus devices, a separate power supply unit (PSU) is needed to power the Modbus devices on the network.

For the KNX Modbus gateway, the RP controller provides both 24 VDC power supply and communications through the Modbus network connection.

It is recommended to use the Non-isolated RS-485 Adapter (SXWNISORS48510001) to provide screw termination of the Modbus device wiring and help avoid miswiring. The adapter converts an RS-485 RJ45 interface to screw terminals. Więcej informacji zawiera Non-isolated RS-485 Adapter .

For the KNX Modbus gateway, the RS-485 Power Adapter (SXWNISORS485P10001) can preferably be used to convert the RP controller RS-485 interface from RJ45 port to screw terminals because this adapter supports 24 VDC power supply from the controller to the KNX Modbus gateway. Więcej informacji zawiera RS-485 Power Adapter .

The maximum total length of the Modbus (RS-485) network is 72 m (236 ft).

The Modbus (RS-485) network cable should be routed in a continuous daisy-chain bus configuration without cable stubs. Więcej informacji zawiera Cable Routing .

Cable selection is important to achieve good performance and reliability of the Modbus (RS-485) network. The cable must provide twisted pairs and be specified for RS-485 data communications. It is recommended to use a shielded, low-capacitance twisted pair cable with an impedance of 120 ohm and a wire size (cross-sectional area) of 22 to 24 AWG (0.33 to 0.20 mm²). Więcej informacji zawiera Cable Selection .

When the controller is installed in a space that handles conditioned air or return air, the Modbus network cables and IP network cables frequently must be plenum-rated to meet applicable building codes.

Uwaga

LOSS OF COMMUNICATION

  • Ensure that the total length of the Modbus network does not exceed 72 m (236 ft).

  • Use a shielded, low-capacitance twisted pair cable specified for RS-485 data communications, with an impedance of 120 ohm, a cross-sectional area of 22 to 24 AWG (0.33 to 0.20 mm2), and a rating that meets the requirements of the target environment.

Failure to follow these instructions can result in loss of communication.

You need to configure which RS-485 (RJ45) port on the RP-C controller to use for the Modbus network. You can configure to use either the RS-485 Com A or Com B port, which by default are configured for the sensor bus and room bus respectively. Więcej informacji zawiera RP-C Communication Ports . The Modbus communication parameters can be freely configured regardless of which RS-485 port on the RP-C controller that is used for the Modbus network.

 
action_zoom_plus_stroke Location of the RS-485 Com A and Com B ports on the RP-C controllers
Rysunek: Location of the RS-485 Com A and Com B ports on the RP-C controllers

The maximum number of Modbus devices that can be connected to an RP-C controller depends on the type of Modbus device and the number of Modbus registers.

The maximum number of Modbus registers that can be connected to and managed by an RP-C controller depends on the communication capacity of the controller's Modbus network.

The RP-C Modbus network supports up to 10 connected Modbus devices with the following restrictions:

  • Maximum of one KNX Modbus gateway (RP-C-EXT-KNX)

  • Maximum of 250 Modbus registers per network

The RP controller Modbus network does not support 64-bit Modbus registers.

 
action_zoom_plus_stroke Examples with one KNX Modbus gateway and several standard Modbus devices connected to an RP-C controller in a daisy-chain configuration
Rysunek: Examples with one KNX Modbus gateway and several standard Modbus devices connected to an RP-C controller in a daisy-chain configuration

The KNX Modbus gateway has the default Modbus address 1. The address can be configured through the ETS. Więcej informacji zawiera Configuring the Modbus Device Settings in the KNX Modbus Gateway .

  • Hardware Overview
  • RP-C Controllers
  • Non-isolated RS-485 Adapter
  • RS-485 Power Adapter
  • Wiring
  • RS-485 Communications
  • Cable Routing
  • Cable Selection
  • RP-C Communication Ports
  • SpaceLogic RP-C Advanced
  • KNX Modbus Gateway RP-C-EXT-KNX
  • RP-C-EXT-KNX
  • Configuring the Modbus Device Settings in the KNX Modbus Gateway
  • ETS Database for the KNX Modbus Gateway