earth_america
user_standard Accedi
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Concetto

Concetto


Prodotti: RP-C, RP-C-EXT-KNX
Funzionalità: Hardware
Versione del prodotto: 3.2, 3.3, 2022, 2023, 2024, 7.0
13/02/2024

Wire Sizes and Lengths for the KNX Modbus Gateway

This section provides recommendations on wire sizes and lengths for the KNX Modbus gateway (RP-C-EXT-KNX).

The recommendations are for guidance only. Other wire sizes and lengths may be used, depending on wiring rules and when appropriate.

The recommended wire sizes in the following table apply to the multiconductor cable connecting the RS-485 Power Adapter to the KNX Modbus gateway screw terminals. The wire sizes do not apply to the Cat 5 UTP cable connecting to the RP controller. Per maggior informazioni, consulta Convert a BACnet/IP Controller RS-485 Interface .

Tabella: Wire Sizes and Lengths for the KNX Modbus Gatway

Terminals

Minimum Cross-sectional Area

Maximum Cross-sectional Area

Maximum Cable Length

Power input terminals a

0.34 mm² (22 AWG)

2 mm² (14 AWG)

72 m (236 ft) b

Modbus terminals c

0.34 mm² (22 AWG)

2 mm² (14 AWG)

72 m (236 ft) b

  1. Upper 3-position screw terminal block.
  2. Maximum total length, that is, Cat 5 UTP cable plus multiconductor cable.
  3. Lower 3-position screw terminal block.

The KNX bus cable should be a KNX certified cable, which typically has a diameter of 0.8 mm (20 AWG), and comply with the length limits defined in the KNX standard, that is, a total length of 1,000 m (3,280 ft). For more information, see the KNX standard and manufacturer's guidelines for shorter maximum lengths between different types of devices.

Per maggior informazioni, consulta KNX Modbus Gateway Screw Terminals and Connector .

  • I/O Wiring
  • Wire Sizes and Lengths
  • KNX Modbus Gateway Screw Terminals and Connector
  • Wiring
  • Convert a BACnet/IP Controller RS-485 Interface