earth_america
user_standard Logga in
action_search_stroke
earth_america
Log on to rate and give feedback 1 2 3 4 5 Log on to rate
0
Specifikationer

Specifikationer


Produkter: CRS-HH-REL-10
Funktionaliteter: Maskinteknik, Maskinvara
Produktversion: 2022, 2023, 2024, 7.0
2025-07-29
Klicka för att visa en uppdaterad version som ännu inte har översatts

SpaceLogic CRS-HH-REL-10

arrow1_rotationInledning arrow1_rotationFunktioner arrow1_rotationSpecifikationer arrow1_rotationAnslutningar
 
action_zoom_plus_stroke CRS-HH-REL-10 – 10-kanals relämodul
Figur: CRS-HH-REL-10 – 10-kanals relämodul

Inledning

SpaceLogic™ CRS-HH-REL-10 relay module connects to the SpaceLogic RP-C Pro room controllers and enables the control of lights and blinds.

It supports high-voltage (120/240 VAC) blind motors. Other types of blind motors are supported by means of external relays. For more information, see the SpaceLogic and EasyLogic - Hardware Installation System Guide.

It is part of the EcoStruxure™ Connected Room Solutions for Hotels and can be combined with other modules from this product range.

It is designed for hotel guest room applications.

It is not recommended to be used with the SpaceLogic RP-C Advanced room controllers for hotel applications.

Funktioner

Relämodulen har följande funktioner:

  • Ström och kommunikation via rumsbussen

  • 10 reläutgångar för styrning av valfri funktion såsom exempelvis belysning och persienner/markiser i rummet

  • 12 digitala ingångar ger ökad flexibilitet för användning av enheter med statusindikering. De digitala ingångarna är av typen SELV (Safety Extra-Low Voltage).

  • Reläer för hög effekt, med hög kapacitet för ingångsström, som passar bra för installationer med exempelvis LED-lampor

  • Status-LED för enheten

  • Roterande brytare för adresskonfiguration

Lösningen för det uppkopplade rummet

Schneider Electrics koncept The Connected Room Solutions inkluderar en portfölj av produkter och applikationer för det smarta och uppkopplade rummet. Få de senaste trådlösa funktionerna med mobilapplikationen Commission för driftsättning och de öppna protokollen för gränssnitt mot industristandardiserade IoT-enheter.

Rumsbuss

For information on the maximum number of RP controller expansion modules that can be connected to the RP-C Pro controller room bus, and which restrictions apply to certain types of devices, see the Architectural Guidelines - EcoStruxure Building Management and the Connected Room Solutions for Hotels Supplementary Document Architecture Guidelines, which is a supplementary document to the Architectural Guidelines - EcoStruxure Building Management.

Maximum total length of the room bus is 72 m (236 ft).

Tabell: Artikelnummer

Produkt

Artikelnummer

CRS-HH-REL-10

Includes pluggable screw terminal blocks (10 x 2-pole, 2 x 9-pole connectors) for the I/O, delivered in a plastic bag with the device.

SXWHHREL10001
DIN-RAIL-CLIP, DIN-rail end clip
package of 25 pieces
SXWDINEND10001

Specifikationer

Electrical
DC input supply voltage
24 VDC
  
Powered by the RP-C through the room bus (RJ45)
Maximum power consumption
0.3 W
Environment
Ambient temperature, operating
0 to 50 °C (32 to 122 °F)
Ambient temperature, storage
-20 to +70 °C (-4 to +158 °F)
Humidity
20 to 90 % RH non-condensing
Pollution degree
2
Material
Plastic flame rating
UL94 V-0
Ingress protection rating
IP 20
Mechanical
Dimensions
198 W x 110 H x 64 D mm (7.8 W x 4.3 H x 2.5 D in.)
 
action_zoom_plus_stroke
Weight
0.476 kg (1.050 lb)
Installation
DIN rail or flat surface
Terminal blocks
Relay outputs: 10 x 2-pin screw terminal block
  
Digital inputs: 2 x 9-pin screw terminal block
Compatibility
EcoStruxure BMS server communication
EcoStruxure Building Operation
version 3.3.1 and later
Agency compliances
Emission
RCM; BS/EN 61000-6-3; BS/EN IEC 63044-5-2; FCC Part 15, Sub-part B, Class B
Immunity
BS/EN 61000-6-2; BS/EN IEC 63044-5-3
Safety standards
BS/EN 60730-1; BS/EN 60730-2-11; BS/EN IEC 63044-3; UL 916 C-UL US Listed
Fire performance in air-handling spaces a
UL 2043
Communication ports
Room bus
RS-485
  
Dual RJ45 ports for daisy-chain configurations
  
Use a Cat 5 (or higher) cable
  
Maximum total length of the room bus: 72 m (236 ft)
Room bus protection
Transient voltage suppressors on communication and power signals
Hardware
CPU type
ARM Cortex-M4 single-core
Frequency
80 MHz
SRAM (embedded)
320 KB
Flash memory (embedded)
512 KB
NOR flash memory
16 MB
Status indicator
LED (green and red) that shows the status of the device
Address switch
Rotary switch 0 to 9
Set button
Push-button switch
Reläutgångar
Outputs
10, DO1 to DO10
Relay output rating
24 to 277 VAC, 50/60 Hz, 30 VDC:
  
Resistive and incandescent: 10 A
  
Standard magnetic ballast: 5 A
  
LED driver: 5 A
  
1/2 HP, 240 VAC, 50/60 Hz
  
1/4 HP, 120 VAC, 50/60 Hz
Max strömmängd
Maximum 50 A total load for the 10 outputs
Max ingångsström
Maximum 165 A inrush current (<20 ms) per output
  
Maximum 800 A inrush current (<200 µs) per output
Digital inputs
Inputs
12, DI1 to DI12
Range
Dry contact, 0 to 5.0 VDC, 2.2 mA, SELV (Safety Extra-Low Voltage)

Anslutningar

Follow proper installation wiring diagrams and instructions. For more information on wiring, see the installation instructions in the SpaceLogic CRS-HH-REL-10 Expansion Module Installation Sheet, the SpaceLogic and EasyLogic - Hardware Installation System Guide, and the RP-C room bus restrictions specified for the Connected Room Solutions for Hotels in the Architecture Guidelines - Hotel Application, which is a supplementary document to the Architectural Guidelines - EcoStruxure Building Management.

 
action_zoom_plus_stroke CRS-HH-REL-10
Figur: CRS-HH-REL-10
  • SpaceLogic RP-C Advanced
  • Driftsättning
  • Wire Sizes and Lengths for the CRS-HH-REL-10 Relay Module